Hi all,
Need a taking your time to explain :
1. What is the difference generator use in application on parallel and single ? is there any spesific generator to use exclusively for parallel ?
2. How to test winding on generator, beside megger test.
Appreciate for your explanation !
One system
Re: Between parallel generator and single
02/19/2011 9:45 PM
There is no such thing as a generator to be used exclusively in parallel.
However, there might be various limited and/or malfunctioning generators that can be used only in island (single) mode....
ξ
Re: Between Parallel Generator and Single
02/19/2011 11:31 PM
I heard an issue told about special generaator for parallel. That why I want you guys opinion. thanks
One system
02/20/2011 12:47 AM
Hmm? If it can work only in parallel, what happens until you get the other one(s) running??
02/20/2011 3:15 AM
........and do these other ones only run in parallel too? Curious minds want to know.
02/20/2011 3:38 AM
Oh, part 2: besides a Megger® test (phase to ground), a continuity test (phase to phase) would be useful.
02/21/2011 7:15 AM
You seem to be out of your field!
All generators can work single or in parallel. The differenceis that you need some special extra equipment to be able to use a generator in parallel with another source of electrical power....
On the winding issue: Too complicated for you. just check if the winding reads to ground or body of the alternator, using a megger: This is an insulation test only. If the reading is less than 2 or 3 mega Ohms, then you might have a problem...
02/21/2011 7:19 AM
The KVA ratings of the two generators to be paralled must be within 3:1 for proper loadsharing.
Apart from meggar( IR test) test, P.I.( Polarisation Index ) test; i.e. ratio of I.R. value of 600 secs to 60 secs, sholud be done either by motorised meggar or P.I. tester ; in general for solid insulation, P.I. value should be greater than 2.0. Comparison of % inductance and resistance values ( Phase to Phase and Phase to Neutral ) should be checked by Electric Motor Checker instrument; for healthy generator, the % varaiation should be within 5%.