Motors will run at 5/6 normal speed. If they are lightly loaded, this may not be a problem, but if they are fully loaded, they may overheat and/or burn out. (Wrong volts/Hz ratio.) Heaters and incandescent lights will probably be okay.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Purely resistive loads shouldn't care, everything else requires further research. For example if the load happens to be a unit heater then the Btu output of the resistive element won't change, but the since the fan will run at approximately 83% of its 60 Hz speed the volume of air will be reduced to (0.83) cubed or 48% of normal (60Hz) air flow. Will the heating element overheat and burnout or will the conditioned space get too cold, both due to reduced air flow? Those are just a few of the questions you will need to consider for each and every device attached to your generator.
__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Apart from power factor correction and busbar sizing, this is one of CR4's principal topics. Try the "search all of CR4" box on the right.