I am designing a farm bridge using W6x16 I-beams 24" oc for a 11 ft span. These have a yield strength of 50 ksi. The tops are fully braced. I was thinking of welding on a 2x2x1/4" angle brace at midspan on the bottom, but if the angle weren't 50 ksi as well, the welding would degrade the I-beam strength to 36 ksi. Correct?
Re: Farm Bridge
03/27/2011 1:51 PM
I don't think so.
How could welding on a brace weaken the original strength of the I beam?
The worst it could do is nothing, I would think.
Re: Farm Bridge
03/27/2011 2:06 PM
Well now, Grasshopper. welding does weaken the base metals. But only locally, which may not be significant. PWHT may not be necessary. Milo, and a few others, will be able to give an informed answer.
Re: Farm Bridge
03/27/2011 2:40 PM
I was trying my best not to sound like I knew what I was talking about. But it does seem to me like the strength of the I beam is derived primarily through the vertical center section of the beam, therefore I would think that welding on the flat bottom of the "I" would have little impact on the strength of the beam itself.
Please tell me it's true master.
Re: Farm Bridge
03/27/2011 11:42 PM
Wrong. If you look at moment of inertia stuff, the parts farthest from the neutral axis contribute most to the strength--the beam flanges in this case. They reach yield stress quicker than the stem.
I agree with the X bracing mentioned later by Old Salt.
Lehman57
Re: Farm Bridge
03/27/2011 3:22 PM
"I do not wish to fight you".
In this instance, I believe the weakening would be insignificant as you say.
My question to you is, what does "W6x16 I-beams 24" oc" mean?
Re: Farm Bridge
03/27/2011 3:41 PM
W6x16 is a wide flange I-beam 6.28 inches high by 4.03 wide, spaced at 24 inches, on center.
Sorry ba/ael.
Structural Steel W Flange Section Properties Moment of Inertia ...
Re: Farm Bridge
03/27/2011 4:10 PM
Wow. How far we can get off the mark! How do you get 6.28" x 4.03" from W6x16?
Is W6x16 a standard? That's why I hate standards; they don't make sense.
OK, talkin' sh*t now, maybe.
Re: Farm Bridge
03/27/2011 4:30 PM
in × lb/ft Area (in2) d (in) bf (in) tf (in) tw (in) Ixx (in4) Iyy (in4)
W6x16 4.74 6.28 4.03 0.405 0.26 32.1 4.43
Sorry, I can't get everything lined up here.
Good Answers: 114
Re: Farm Bridge
03/27/2011 5:46 PM
With wide flange sections, the inner rolls are set for a range of members, in this case, all nominally 6"x4". The different weights are achieved by moving the rolls further apart for the heavier end of the range.
Re: Farm Bridge
03/27/2011 4:17 PM
It happens.
It's a little risky telling someone that says they have "I" beams, they don't.
All's good over here, while I still was not able to snatch the pebble from your hand, at least I know I was right.
Re: Farm Bridge
03/29/2011 6:33 AM
Well, at least I wasn't the only one here that was a little off.
http://en.wikipedia.org/wiki/I-beam
Good Answers: 179
Re: Farm Bridge
03/29/2011 7:21 AM
Wiki is a bit off regarding their terminology, as usual, and shouldn't be solely relied on regarding technical terminology and definitions. This is what happens when professional writers (do I dare say "Liberal Arts" grads?) who don't do their research properly by not asking technical questions (or know enough to ask the correct technical questions....usually not, like the Network and local TV talking heads who really don't know "Jack Chit" about technical issues but rather specialize in "fluff" subjects. Uncle Walter where are you man, we need you back in charge of the network news program!?) of the experts in any given field.
Well here in the USA, Structural Engineers don't use the "I-Beam" terminology in their day-to-day work, but rather S-Beams and Wide Flange Beams.
If fact, I-Beams are really S-beams, where the inner faces of the flanges slope (or thicken) from the narrow flange tip to the web-flange interface/root.
Wide flange beams have constant thickness throughout.
Just tossing-in my 2 peanuts worth.....
Re: Farm Bridge
03/29/2011 7:27 AM
I just jump in some of these threads to get kicked around a little..................it keeps me humble.
Good Answers: 74
Re: Farm Bridge
03/27/2011 3:22 PM
flyinghigh,
  • W6x16 are not I-beams, they are wideflange (W) shapes. There is a 6" I-beam at 17.25#/'. It is designated S6x17.25.
  • Welding an A36 angle brace to the bottom does not change the beam's yield strength.
  • What is the purpose of the midspan brace on the bottom? It is not customary to brace the tension flange.
  • It is also a little unusual to space beams at 24" centers.
Bruce
Good Answers: 114
Re: Farm Bridge
03/27/2011 5:51 PM
I agree with ba/ael, on it being unusual to place the angle on the bottom flange. It is the weld metal that mixes with the steel of the member so if you use a "matching" weld rod it should make no difference.
Good Answers: 203
Re: Farm Bridge
03/27/2011 11:08 PM
I have been involved with constructing several bridges/structures such as you are planning. Steel beams were primary H/I's that were readily available for cheap. Wooden were primarily glulams. We always placed the braces from the top of each beam to the bottom of the adjacent beams. This formed sort of an "X" configuration between each adjacent set of beams. If the braces were placed along the bottoms of the beams as you propose there would be a tendencey of one beam causing the adjacent beams and others to follow its movement should it start to twist. With the "X' configuration of the braces each beam will resist the twisting of adjacent beams.
This is also how braces are installed between joists when building a house or structure. Each joist resists the twisting of its adjacent joist because of the "X" configuration of the braces. By only installing along the bottoms of the joists you would be at risk of parallel failure of all the joists.
Good Luck- old salt
Re: Farm Bridge
03/27/2011 11:48 PM
What are you trying to determine? The load capacity? I would think the capacity would be with the heaviest loaded wheel at center span with the whole load on one of the beams. Don't forget the dead load of deck, beams, etc.
Lehman57
Re: Farm Bridge
03/28/2011 12:41 AM
At a quick look, the beams you have are well up to the task - a rule of thumb is 0.5 inch depth per foot of span, which you have. There are standards that spell out all you need to know - BS153 (probably superseded by now) is one.
One never designs at yield for reasons of safety, and more importantly for reasons of elastic stability and fatigue.
At high load stresses, open sections like I beams will twist and fail "sideways". This is called torsional instability and is why bracing is placed between adjacent main beams, and for the same reason, timber noggins are inserted between rafters in roofs/floors. You seem to appreaciate this, but many don't.
The main reason for not welding to the tension side of a beam (lower flange ) is that it introduces a stress raiser that will encourage fatigue failure. You application is unlikely to have enough use to make this important but as good practice I would weld any stiffener/bracing to the web/s and not the flanges. This minimises the fatigue issue but still gives excellent torsional bracing.
A approximate way to calculate strength is to use a low stress figure like 12000 ksi (also implies safety factor of 4) and multiply this by the Z modulus (in3) for the beam.
This modulus (relates to section inertia) is approximately the area of one flange by the distance from its area centreline to that of the other flange. The web will add about another roughly 15% (from memory) to this initial figure.
Using rounded figures.
So for you that is about Z = 5.9*0.4*4 = 9.5 in3 (ignore adding 15%)
at 12000 ksi is 12000*9.5 /12= 9500 ft lbf
which on an 11 ft span implies a point load of 9500*2/(11/2) = 3500 lbf or if uniformally loaded about 7000 lbf per beam
the self weight of the beam at 180 lbm is not significant.
I can't advise on the need for a stiffener in the middle off the top of my head. I suspect that the answer is that it is not needed, but either do a proper check or just weld a bit of light 5 inch rhs or maybe even a couple of bits of 5 inch flat to between the webs, in the middle of the span.
Disclaimer - This is offerred for assistance and should not be relied upon.
Re: Farm Bridge
03/28/2011 10:53 AM
Thx to all who responded.
Good morning TrevorM,
Your note gives me comfort. The client has requested the design be based on a 60,000# GVW. This would equate to 30,000#/axle, or 15,000#/I-beam at mid-span. This would induce a moment of 247,500 in#, and a corresponding stress of 24,265 psi in the selected W6x16 Fy 50 ksi beam, providing a factor of safety of over 2:1. The AISC manual typically uses 0.66 Fy where I used 0.5 Fy. The section modulus of the beam is 10.2 in^3, exceeding the calculated required modulus of 9.9 in^3.
The manual emphasizes top bracing, but not bottom bracing. On top the I-beams will be placed steel plate, which I have called to be welded to both sides of the top flange at 1/4" x 2" fillet welds 48" oc.
Good Answers: 74
Re: Farm Bridge
03/28/2011 2:08 PM
flyinghigh alert!!!
"This would equate to 30,000#/axle, or 15,000#/I-beam at mid-span. This would induce a moment of 247,500 in#, and a corresponding stress of 24,265 psi in the selected W6x16 Fy 50 ksi beam"
M = PL/4 = 15*11/4 = 41.25'k = 495,000'#, but you should be using an impact factor of 1.25, so your design moment should be 618,750'#.
Beams at 2' centers does not appear to be a practical solution to the problem. You should consider other framing systems.
Bruce
Re: Farm Bridge
03/29/2011 10:08 AM
Good morning ba/ael,
Since the beam ends will be fixed, I used the corresponding formula.
Good Answers: 74
Re: Farm Bridge
03/29/2011 11:39 AM
flyinghigh,
What is going to fix the ends? A 28" x 16" x 30' long footing resting on soil? Give us a break! You should be considering the beams as simple spans.
In my humble opinion, you are going to find yourself in serious trouble if the design load ever gets on this bridge. I suggest you think it over.
Bruce
Re: Farm Bridge
03/28/2011 4:12 PM
What is the truck? Single or dual rear axle? If a single rear axle, your load distribution won't be 50/50; if a dual axle, the front axle still won't have 50% of the load. With dual back axles, is the moment worse with one of them at the center and the other toward an end; or is it worse with the centerline between the axles at the center of the bridge? You probably will have to calculate both ways.
Calculating for fire apparatus weight is an absolute; contact the local fire chief for their weights, then add some for future increases.
If the wheel(s) happen to be midway between the beams, the beams will be OK, but how about the deck?
Lehman57
Re: Farm Bridge
03/29/2011 10:13 AM
Good morning Lehman57,
The design deck's 1" steel plate thickness checked out ok.
Good Answers: 74
Re: Farm Bridge
03/29/2011 11:49 AM
A one inch steel deck? Wow! At 490 pounds per cubic foot, that will weigh 30*11*490/12 = 13,500# all by itself. An additional 2800# of beams brings the dead weight to 16,300# which will create a substantial bending moment without any wheel loads.
This design really needs to be re-considered.
Bruce
Re: Farm Bridge
03/28/2011 3:19 AM
After solidifying, the weld cools and tries to contract which creates local tensile stress.
As trevorM points out, it is good practice not to weld on the tension flange of a beam.
chris@ade.net.au
Good Answers: 179
Re: Farm Bridge
03/28/2011 7:27 AM
In this instance I would suggest that the plate be continuously (or nearly so) welded to the top flanges of each beam on both sides. It's very important to provide full lateral support of the top flanges (ie, compression flanges) to prevent twisting of the beams (torsional buckling) and keep the Allowable Bending Stress (Fb) in the upper limits and not a lower value. You're going to have to compute Fb in accordance with the AISC Steel Manual.
Also, provide lateral bracing in the form of X-Braces between the beams, as old salt suggested....I'd place these at the mid-span and at the quarter-span locations.
Welding of the angles to the beam flanges will have no overall effect on the Yield Stress of the beams, only a slight localized disturbance.
One thing we don't know is what the maximum anticipated vehicle axle load will be travelling across this farm bridge, therefore we can't even hazard a guesstimate what the design Bending Stress could be and compare it to Fb to see if the beams are structurally adequate.
Also of concern would be the design bearing stresses at the foundation abutment walls........which we also know nothing about. So, what exactly is supporting this bridge???? I'd be very worried about the beam bearing locations too! You'll need adequately designed beam bearing plates and properly designed anchor bolts.
That's just for starters IMO.
===signed,
CaptMoosie, PE / PhD
Civil, Structural & Environmental Engineer
Re: Farm Bridge
03/28/2011 11:03 AM
Good morning CaptMoosie,
Several of your ponderings I have addressed in my previous note. For the supports at each end of the mentioned I-beams, will be 28" horizontal x 16" v 3000 psi concrete footings, 30 ft long, with 5 ea #4 gr 60 continuous rebars, with 3" clearance. These were based on a soil strength of 1980 psf, and the associated dead and live loads.
Good Answers: 203
Re: Farm Bridge
03/28/2011 11:42 AM
As a firefighter, I feel obligated to ask a question concerning your design of this bridge. Can it safely and confortably withstand the load of a fully loaded pumper (up to 60,000#), tanker (up to 70-80,000#) or a ladder/platform truck (up to 70,000) should there be a fire and full size fire apparatus need to cross it?
Within the response areas that my dept. responds to there have been several incidents where structures have been lost (with the potential for lives to be lost) because only light weight equipment, brush trucks and mini-pumpers, could cross bridges. A year ago I was the Incident Commander for a barn fire which started to char the residence. Only because we carry compressed-air foam on our mini-pumper were we able to save the residence. We finally were able to pump out of the swimming pool to extinguish the main fire at the barn. Serveral out-buildings were also lost. The driveway was about a 1/4 of mile long with a lightweight bridge on it about 100 yards in from the rural road. No situation to try to hand lay about 1,500' of 5" LDH for a tanker task force from the road.
Good Luck- old salt
Re: Farm Bridge
03/28/2011 11:56 AM
You raise a good point. Altho it's been my experience its impossible to get the fire trucks to your place if its outside the city, I should at least post a sign showing the maximum bridge GVW is 60,000#.
Location: Lincoln City, Oregon, Central Oregon Coast, USA
Re: Farm Bridge
03/28/2011 1:30 PM
I have to add a brick to the load...good comment from Old Salt. I too am involved with firefighting, and we have several of "farm bridges' that area made from recycled flatbed train cars. While these are usually in decent shape, it's always a concern when we approach them with a fully loaded engine or tender. We have one that is constantly abused by loaded and unloaded tandum axle dump trucks that haul pit run up to and including some decent boulders used for riprap against sloughing hillsides. So far the only thing that seems to have suffered is the wood plank decking that most likely came with the original flatcar bed! Please do post the weight limit...you will put a few of us firefighters at ease as they approach the smoke! Take care!
..."life is too busy to let boredom drop anchor."
Re: Farm Bridge
03/28/2011 12:03 PM
I assume your farm bridge is one-lane just wide enough to allow a truck or tractor to pass. Since your loads will be concentrated along each side of the bridge, why not concentrate the strength there. Rather than using 5 beams on 24" centers (for 8 ft wide bridge), place 2 beams much closer together on either edge where the load is actually going to be applied by the tires.
If you have 5 beams on 24" centers, and cross with an 8 ft wide truck or tractor, the load one each side will be carried primarily by one beam. Placing 2 beams close together will cause the loaded to be shared.
You can leave one in the center to support the 3rd wheel of any 3-wheel implenents you might have to take across.
Re: Farm Bridge
03/28/2011 12:24 PM
The bridge is 30' wide.
Good Answers: 114
Re: Farm Bridge
03/29/2011 12:54 PM
This design is highly suspect, 1" plates over W6x16s is a mismatch. The foundation size stated cannot provide fixity.
Is there a constraint on depth that drives this design?
Re: Farm Bridge
03/30/2011 12:56 PM
Good morning passingtongreen,
I was originally given a GVW of 80,000#, and designed for W10x19, S = 18.8 in^3, 24"oc. The client then decided a GVW of 60,000# would be adequate, and requested the lowest possible beam height. The revised design was based on a W6x16, 10.2 in^3, 24" oc.
Next he requested a consideration of beams closer together, and a 1/2" steel plate. This iteration was based on W6x8.5, 5.08 in^3, 12" oc, with 1/2" plate.
Next he proposed a steel reinforced concrete pipe, to which I made a rough draft utilizing a 5' od, 6" wt, concrete pipe of unknown crush strength, with steel reinforced 8" concrete over the top, going to reinforced footings on either side.
To this he advised he would investigate on his own the utilization of PE pipe(s) the mines use, and just cover it/them with dirt! I think he wants a bridge for zero dollars!
Good Answers: 74
Re: Farm Bridge
03/30/2011 1:09 PM
He probably wants an engineering fee of zero dollars too.
Bruce
Re: Farm Bridge
03/30/2011 9:57 PM
I hope he is thinking about fire protection!
Lehman57
Re: Farm Bridge
03/30/2011 5:04 PM
How about a corrugated/galvanized steel culvert with earth fill on either side?
Good Answers: 74
Re: Farm Bridge
03/30/2011 7:09 PM
Sounds like a practical idea to me.
Bruce
Re: Farm Bridge
03/30/2011 10:02 PM
Some of the corrugated plastic pipes are pretty tough. There is one on the oil well access road beside me. It was put in the creek bed then covered with coarse fill. Size needed would depend on the largest creek flow in a huge storm.
Lehman57