Improving Earthing

04/17/2011 11:11 AM

i am working in power dept. as JE at a recieving station where the soil nature is rocky. so in order to enhance soil conductivity i want to do the chemical earthing as the conventional earthing doesnot yield good results for me...

can anybody tell me which chemical is used in chemical eathing and how this chemical increases the conductivity and what is the procedure of obtaining good chemical earthing?????????????

thankx........

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Improving Earthing

04/17/2011 11:22 AM

EARTH PIT CONSTRUCTION AS PER INDIAN ELECTRICITY BOARD
1. Excavation on earth for a normal earth Pit size is 1.5M X 1.5M X 3.0 M
2. Use 500 mm X 500 mm X 10 mm GI Plate (Plate may be use as big as possible to contact more and more area of Earth for low resistance & best result)
3. Make a mixture of Wood Coal Powder Salt & Sand all in equal part
(a) Wood Coal Powder use as good conductor of electricity, anti corrosive, rust prove for GI Plate for long life.
(b) Salt use as electrolyte to form conductivity between GI Plate Coal and Earth with humidity
(c) Sand has used to form porosity to cycle water & humidity around the mixture
4. Put GI Plate (EARTH PLATE) of size 500 mm X 500 mm X 10 mm in the mid of mixture
5. Use Double GI Strip size 30 mm X 10 mm to connect GI Plate to System Earthling
6. It will be better to use GI Pipe of size 2.5" diameter with a Flange on the top of GI Pipe to cover GI Strip from EARTH PLATE to Top Flange
7. Cover Top of GI pipe with a T joint to avoid jamming of pipe with dust & mud and also use water time to time through this pipe to bottom of earth plate
8. Maintain less than one Ohm Resistance from EARTH PIT conductor to a distance of 15 Meters around the EARTH PIT with an other conductor dip on the Earth at least 500 mm deep.
9. Check Voltage between EARTH PIT conductor to Neutral of Mains Supply 220V AC 50 Hz it should be less than 2.0 Volts
Read more: http://wiki.answers.com/Q/How_do_you_make_a_electrical_earth_pit#ixzz1JnIzSOdA

Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #1

Re: Improving Earthing

04/17/2011 1:25 PM

GA

You know, I'm beginning to think that in India there must be something cultural against search engines.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Improving Earthing

04/17/2011 1:31 PM

Thanks. I think it's more of a universal thing.

Register to Reply Off Topic (Score 5)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#9
In reply to #6

Re: Improving Earthing

04/17/2011 10:03 PM

Dear redfred,

There is nothing cultural against search engines with Indian Engineers. Unlike many other under developed countries India has a specific Indian Electricity act and engineers have to comply with these rules in each and every electrical work. So most of them quote from IE rules. You can also surf and get these rules. More over Bureau of Indian standards (BIS) provide complete specifications, the copy of which are mandatory for any contracting company or industrial houses for compliance of jobs. So engineers in India search these standards first for any job specification. Most of the information they need are available ,only in exceptional cases they need to go for search engines for additional information.

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Improving Earthing

04/17/2011 12:12 PM

From my experience, urine works pretty good in a pinch, at least temporarily. I had a similar problem with a portable generator on a road rock crushing quarry at a rocky mountainside. Couldn't get a consistant ground resistance reading and MSHA (Mine Safety & Health Admin.) would not give us a working permit. I had the backhoe operator dig a pit and went to the store, bought a case of beer, handed them out to all the workers and instructed them to "return the beer after processing" into the pit. Welded a stud on a 3ft x 3ft steel plate, connected the ground cable and tossed it in before the beer kicked in. When the crew finished their part, we buried it and the next morning called MSHA for a ground test. Passed!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Improving Earthing

04/17/2011 12:17 PM

Had a cousin who peed on an electric fence, once.

But, he was from Texas, so we didn't think much of it.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #2

Re: Improving Earthing

04/17/2011 1:16 PM

Didn't we just recently have a thread about great bosses?!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jan 2011
Location: Barrie ontario canada
Posts: 98
Good Answers: 2
#8
In reply to #2

Re: Improving Earthing

04/17/2011 5:38 PM

Did the inspector say urine luck when it passed lol great idea

__________________
i never said it would look pretty when i built it. BUT IT WORKS WHAT MORE DO YA WANT!!!!!!!
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Improving Earthing

04/17/2011 12:20 PM

The back-fill material used in all chemical earthing is a natual clay (formed out of valcanic eruption) called BENTONITE - with varying degrees of a wide variety of additives - like Sodium Chloride, Copper Sulphate, Calcium Chloride, Magnesium Sulphate, etc.

There is nothing so special in this chemical to increase 'conductivity' per se. Bentonite has a wonderful property of retaining moisture. With mositure and the additive salts present, the area around the earth electrode is actively conductive 'electrolytically' and that is the magic.

The procedure for good chemical earthing is to create a basin of size. say, 2 feet diameter, around the earth electrode and fill this chemical tightly in the basin. Or easy way is to go for commercially available safe earth electrodes, which come pre-filled with this chemical.

Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#10
In reply to #4

Re: Improving Earthing

04/17/2011 11:23 PM

This is especially for EE65, somewhere, instead of making a big earthing hole, I found that people drill directly to the earth. The lesser resistance they want to achieve, the deeper they drill.

And my question, is this practical?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#11

Re: Improving Earthing

04/18/2011 3:41 AM

Sodium bentonite is ideal chemical for the earthing in Rocky area.

Try the link below for checking availablity in India

http://www.alibaba.com/ppc/bentonite/IN.html

also Search Wickypedia for Bentonite to learn more for Bentonite

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Improving Earthing

04/19/2011 3:29 PM

Seawater would do.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); hien.nguyenquoc (1); JRaef (1); lyn (3); Panneer Selvam (1); PWSlack (1); redfred (1); steven phaneuf (1); Tornado (1); V.I.Abraham (1)

Previous in Forum: Relay   Next in Forum: Induction Motors

Advertisement