Water Loss Calculations in a Cooling Tower

05/16/2011 2:00 AM

anyone tell me how i can found out the water loss from a cooling tower in a simplified way ?

Register to Reply
Pathfinder Tags: cooling tower water losses
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: water loss calculations in a cooling tower

05/16/2011 2:36 AM

The evaporation of water requires about 1000 Btu/lb, depending on the temperature/pressure condition. From the Btu rejected by your process, it is thus easy to estimate the amount of water evaporated. (Similar in SI units.)

To keep contaminants from building up in the cooling tower water, it is necessary to treat and/or "bleed off" (i.e., drain) some water. Without other treatment, a rule of thumb is that the amount bled off should equal the amount evaporated. This is not precise, and would depend on how "hard" the water is, how dusty the atmosphere is, etc. If these conditions are mild, then less bleed-off; if severe, then more. But anyway, this is a reasonable starting point.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#6
In reply to #1

Re: water loss calculations in a cooling tower

07/30/2011 1:04 PM

Dear Mr. Tornado,

I want to supplement to your answer.

There is one more - item of Water Loss in the Cooling Tower, it is known as DRIFT LOSS - where minute water particles are carried away by the out going air - which will be hot, saturated or near to saturated condition depending upon the Relative Humidity.

The drift loss will be 0.2% to 0.5% of the total quantity of water circulated. The Drift Eliminators play a vital role in controlling this DRIFT LOSS.

You have referred " Water requires about 1000 BTU/Lb. Actually it is 970 BTU/Lb. or 540 K.Cal/Kg. of water or 2257.9 KJ/Kg.of water at atmospheric pressure of 14.696 PSI or 1.03 Kg/cm^2. which is at Sea-Level. If the Altitude goes-up, the latent heat will INCREASE - as referred in the Steam Tables.

Thanks,

RAJESWARI.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: water loss calculations in a cooling tower

05/16/2011 4:36 AM

Meter the tower make-up water flow.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3

Re: water loss calculations in a cooling tower

05/16/2011 5:59 AM

PWSlack gave a good answer. In case of no bleeding condition and no other leakages, the simplest way to find rate of water loss is to measure rate of make-up water added.

Calculating theoretically is also very simple. RH of ambient air is the biggest factor. Less the RH, more the water loss. At cooling tower outlet air quality will be 100% RH (fully saturated in contact with water to be cooled). Water is evaporated to make air saturated which is termed as water loss. Calculate specific humidity of air at ambient temperature and RH and specific humidity of out going air at outlet temperature and 100% RH. Difference of these two figures will give water added in per kg of air. Multiplying it with air weight flow rate will give minimum water loss rate. Actual loss may be more because of free water particles travelling along with air which depends on type & quality of packing.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: water loss calculations in a cooling tower

05/16/2011 7:53 AM

That doesn't sound like a "simplified way".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Water Loss Calculations in a Cooling Tower

05/17/2011 3:35 AM

Measurement ≠ calculation.

Measurement will tell you how much water is actually being consumed, but it won't tell you if that is the "right" amount of water.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

pritam (1); PWSlack (2); rajeswari (1); Tornado (2)

Previous in Forum: Cooling Tower   Next in Forum: Decoding Catalytic Reactions

Advertisement