Tubing

05/16/2011 7:28 AM

What is the Difference between Inpulse Tubing and Capillary tubing...?

Register to Reply
Pathfinder Tags: tubing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Tubing

05/16/2011 7:38 AM

In what context?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: May 2011
Posts: 5
#2
In reply to #1

Re: Tubing

05/16/2011 7:44 AM

Bascially I am a Mechanical Engineer, there was a Discussion happening within our design team About selection of Which type of tubing can be used for Level Transmitters. Someone tells that the impulse tubing is better than a Capillary tubing. And I cannot understand the difference..?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Tubing

05/16/2011 7:50 AM

Ask the someone to explain, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: May 2011
Posts: 5
#4
In reply to #3

Re: Tubing

05/16/2011 7:56 AM

Thank you So Much....

Register to Reply
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#5

Re: Tubing

05/16/2011 10:52 AM

I use the term "Impulse line" for the connection from the process to the instrument. The impulse line can be either tubing or pipe.

I would assume "Impulse tubing" to be commerical tubing, rated for the pressure involved.

In the USA, tubing is classified by its OD, pipe by its ID. Tubing is never threaded; flare or compression fittings are used for connections to the instrument.

Capillary tubing is very small diameter tubing which is always used for filled systems, like for the connection between the instrument and a remote diaphragm seal. On rare occasions, capillary tubing is used as a mechanical damper to dampen pressure oscillations. Capillary tubing will slightly delay, but not diminish pressure spikes.

My 1960's era Industrial Instruments and Control Piping book, an instruction guide to teach apprentices how to install piping, shows all connections in pipe, no tubing.

The table below shows sizing considerations for impulse lines

Register to Reply Good Answer (Score 2)
Member

Join Date: May 2011
Posts: 5
#6
In reply to #5

Re: Tubing

05/17/2011 12:56 AM

Hi...

Thanks...that helps me a lot...

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: Tubing

05/17/2011 4:58 AM

It seems a pity that the "someone" didn't know that....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Tubing

05/17/2011 2:59 AM

For level transmitters, capillary tubing would NOT be acceptable; too small in diameter to allow suitable flow under low pressure differentials.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9

Re: Tubing

05/17/2011 9:27 PM

Amazing what a EE can ferret out of the web with a simple Google query.. http://www.flowcontrolnetwork.com/containment/hose-and-tube/article/considering-capillary-tubing

Is the advice useful? I will leave that to the members with the proper training and experience.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Arun.Kumar (3); Iris (1); PWSlack (3); RAMConsult (1); Tornado (1)