D.I. Water

05/25/2011 11:09 AM

We are filling a closed loop chilled water system for an MRI cooler, with a mixture of 30% Glycol and DI water the piping is a combination of copper and iron. I believe their can be issues with using pure DI on copper and iron as the DI is aggressive in nature due to its purity content.

My question is does the 30% Glycol act as a buffer and will it prevent this possible corrosion?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: D.I. Water

05/25/2011 1:25 PM

Here's all I know. Most ready to use antifreeze is a 50/50 mix of antifreeze and DI water.

My assumption is that it would be ok, but I'd wait for an expert to drop by.

Register to Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#2

Re: D.I. Water

05/25/2011 6:54 PM

My instinct says you should be just fine. But, Like Lyn, I'm not an expert in this field.

__________________
Don't believe everything you read on the Internet!
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: D.I. Water

05/25/2011 7:02 PM

>Most ready to use antifreeze is a 50/50 mix of antifreeze and DI water.

A major brand who also private labels other automotive antifreeze brands in the US does not use DI water for the 50/50 mix. The water blended with the ethylene glycol (and additives) for 50/50 is city water.

Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Apr 2006
Location: Brigham City, Utah
Posts: 163
Good Answers: 5
#4

Re: D.I. Water

05/25/2011 8:01 PM

It's been a few years but if I remember correctly, We used DI (Deonized) Water to cool Lasers used to engrave serial numbers in steel casings. We never used automotive antifreeze, but purchased industrial glycol in 50 gallon drums. It was not diluted. I believe that we used propylene glycol rather than ethelyne glycol because it is non toxic and breaks down in the environment in a short period of time. We never had an issue with pipes, tubing or other items in contact with the DI water. I do remember checking the cooling water periodically to be sure it never exceeded a predetermined level of electrical conductance. If I can find any remaining data that could clarify this, I will return and post it. Hope this helps at least a bit.

__________________
Kindness knows no boundaries.
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#5

Re: D.I. Water

05/25/2011 10:35 PM

http://www.keytometals.com/articles/art160.htm

You might want to check this site out. Metal in contact with water, especially when there are different metals (because of different potentials), undergoes galvanic corrosion. Glycol may prevent or slow this but DI water is a strong solvent- do you have access to a materials scientist? Does the manufacturer of the MRI provide recommendations?

From the link above:

"Galvanic processes occur between different metals and between different areas of the same metal in the water environment. Water is an electrolyte, a poorly conductive one at the low dissolved solids content of fresh waters, and a highly conductive one at the high dissolved solids content of sea water.

When two different metals are immersed in an electrolyte and connected through a metallic path, current will flow. Oxidation occurs at the anode and reduction (normally oxygen reduction) occurs at the cathode".

"Galvanic corrosion occurs between weld metal and base metal, between different areas of the same metal and between different metals in water."

The glycol concentration may need to be greater than 30%

Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#11
In reply to #5

Re: D.I. Water

05/26/2011 10:53 AM

I worked in materials research and Lynn is right. DI is no longer DI once it comes into contact with a metal like copper or iron. There will be ion transfer and corrosion if you use both materials in your plumbing. I would limit the material to one type of pipe, copper or iron, or use Stainless steel throughout.

The glycol can buffer the reaction but will not prevent it. Iron may have a bad effect on an MRI machine too. It's magnetic, and you are ruining your DI water by passing it through Iron pipe! This may cause loading of the MRI.

Check with the manufacturer of the MRI machine. I'll bet they specify copper only or stainless only.

__________________
Most people are mostly good most of the time.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#13
In reply to #5

Re: D.I. Water

05/26/2011 4:48 PM

DI Water, has had all the free Ions removed. It's those pesky little Ions that do all the damage. DI (in theory) would not cause any corrosion, in fact you can take your computer, leave it on and plugged in, and go ahead and submerse it completely in a tank of (pure) deionized water, and guess what will happen? if you guessed nothing, then you'd be right. People have submersed their motherboards in tanks of DI water to keep them cool, and they have done this successfully. Now, on the other hand, if you tried this with any other form of water that does contain those free radical Ions, then you would be in trouble. Deionized water is NOT electrically conductive, and therefore will NOT cause Bi-Metallic corrosion. (until it has been contaminated with foreign particles which do conduct electricity.)

I'm not saying you wont see corrosion eventually, but in the initial few seconds the DI water remains pure (before atoms of other substances are dissolved into the water) it won't directly cause the corrosion (although inevitably it will occur). But in the end, you cannot keep the DI water from becoming contaminated, therefore the other mixtures, and corrosion preventatives will save the day.

But in the end, technically speaking, DI water is NOT an electrolyte until it has been mixed up with other things that will conduct electricity.

__________________
Don't believe everything you read on the Internet!
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#15
In reply to #13

Re: D.I. Water

05/28/2011 2:30 PM

RVZ717

Although galvanic cell does not form in a poor electrolyte like DI water, I do not agree with this statement at all. DI water is devoid or very low in conductivity but it is considered very aggressive. If you look up any of the saturation indices calculators available on the web and enter values for DI water you will find that the water will be very aggressive. DI is under-saturated in minerals and as a result will be corrosive to all metals it comes in contact. A computer will be destroyed by such water and relatively quick. I did a calculation using a conductivity of 1μS/cm, hardness of 1 mg/L ,d Alkalinity of 1 mg/L and temperature of 0 degrees C. If you use the calculator indicated it will be minus 5.5. That is very aggressive water.

As a guide to using the index consider values less than zero as aggressive, greater as scale forming, and zero as neutral. Anything less than -1 is considered very aggressive. At -5.5 the water is extremely aggressive. Conversely, water above 1.0 is considered very scale forming and if it was at +5.5 that would be extreme scale forming. Most water would be in a range of -0.5 to + 0.5 and even then can be problematic at the upper or lower ends. You are correct it is not galvanic corrosion.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#16
In reply to #15

Re: D.I. Water

05/31/2011 12:47 PM

Hey, I have no calculations to run, but I have seen with my own eyes, a motherboard suspended in a tank of DI water, RUNNING, and running well. It was left that way for quite some time, plugging away at it's calculations the whole time with no ill effects. I cannot say what effects it may have long term, but I know people use DI water in their water cooled computers as well. It was just a thought.

Water in any form is the universal solvent.

I am definitely no chemistry expert, and most likely should leave topic like this alone to avoid the foot-in-mouth syndrome.

__________________
Don't believe everything you read on the Internet!
Register to Reply
3
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#6

Re: D.I. Water

05/25/2011 11:06 PM

First job out of college was with a major pharmaceutical company (I'm now retired so it was a long time ago) where we were using DI water (because of its known lack of impurities to confuse things up) and an ethylene glycol mixture 50/50 by volume. Piping was all black iron as part of a chiller system to cool down reactor and mixing tank jackets. The ethylene glycol was reagent grade with no additives because it was the handiest and most readily available. Due to the size of the system the initial charge was about 300 gallons of glycol/water.

Big problem with the system was that without a rust inhibitor, such as that in automobile anti-freeze, the black iron pipe would rust internally almost instantly and system would develop leaks at a incredible rate. The rust particles would also clog up valves and other devices.

Solution was to change over to commercial automobile anti-freeze with a rust inhibitor purchased in drums such as a truck or bus fleet purchase. This solved the problem. Only people not happy were the bean counters since this was more expensive in initial cost. Maintenance cost and down time soon dropped dramatically.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: D.I. Water

05/26/2011 5:32 AM

No, it won't. Corrosion resistance is achieved by having wetted materials that are compatible with the fluid in question.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#12
In reply to #7

Re: D.I. Water

05/26/2011 10:57 AM

Old salt and PWSlack have both given good answers. You may want to consider propylene glycol from Nu-Galgon. It seems to have all the qualities you need. (not sure of price)

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#8

Re: D.I. Water

05/26/2011 6:30 AM

Dielectric unions where copper meets iron will help reduce electrolysis, whatever conductive coolant you use. One possible option would be transformer oil, such as Shell Diala AX. This hydrocarbon oil is an excellent insulator, as well as heat transfer medium. The flow rate for a given heat flux would be greater, as the specific heat is lower than water/glycol.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2011
Posts: 15
#9

Re: D.I. Water

05/26/2011 6:33 AM

Your belief is spot on about mineral depleted water. I have experienced piping failure in a centerless grinding operation. The grinder coolant was mixed to proper concentration w/D.I . water . Within 6 mo. of the test start,we had massive Cu pipe failures.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10

Re: D.I. Water

05/26/2011 9:29 AM

A bit of a bad choice of words - purity content? That's almost an oxymoron. There is no content. That's is the reason as you stated for the aggressive nature of the DI. Pure water with no ion content is not happy. As soon as you add the glycol, there are ions and the DI is no longer DI. We build many heat exchanger skids per year, and most of these are run on a glycol/DI water mix through both carbon steel and copper tubing. DI also creates other strange problems that is not associated with water. Any conductivity based sensor, such as a point level sensor, or magnetic flow meters do not function with DI. We caught ourselves the other day trying to put a water sensor in an area where DI might leak. It was based on conduction between two points. Will not work.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Associate

Join Date: Mar 2011
Posts: 34
#14

Re: D.I. Water

05/26/2011 4:57 PM

Since you are using this in a chiller, the effects should be slow, but glycols break down at higher temperatures and form acids in closed loop systems. That is why antifreezes for automobiles have inhibitors added to the mix. Also, as elsewhere stated, the water will slowly increase ionic concentration from reaction with the metals and set up a galvanic action. I would find a commercial antifreeze package that prevents (or technically slows) corrosion.

Register to Reply
Power-User

Join Date: Dec 2007
Posts: 142
Good Answers: 1
#17

Re: D.I. Water

05/31/2011 2:35 PM

Thanks you all for the input and advice, we are going to use 50% Glycol supplied by the chiller manufacture, the product has inhibitors to buffer the DI.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Deefburger (1); drbobwoolery (1); Iris (1); kevinm (2); lyn (1); Lynn (1); Matt3477 (1); old salt (1); oldchemist (1); Phys (1); pipeit (1); PWSlack (1); RVZ717 (3); Techart (1)