Wire Size When Replacing Machine.

06/07/2011 3:15 PM

This will probably be a stupid question for those who know but I am not 100% sure so here goes. I am replacing a machine that is wired for a 100 amp draw using a 100 amp breaker. The new machine will only have a 60 amp draw. My question is can I use the same wires that are already ran, which will be larger than needed for the new lower load, without having any detrimental effects? I intend to replace the breaker with a 60 amp breaker.

Thanks,

dgibson

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Wire Size When Replacing Machine.

06/07/2011 4:10 PM

According to the NEC:

You can use the existing conductors provided you do not have to alter or modify the lugs/connectors on the new equipment or the existing conductors in any way to get them to land properly.

Same holds true for the new 60A CB and existing conductors at the panel board.

You should check your local codes though to be sure you are in compliance.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Power-User

Join Date: May 2009
Location: Amarillo, Texas, USA
Posts: 188
Good Answers: 10
#3
In reply to #1

Re: Wire Size When Replacing Machine.

06/07/2011 4:14 PM

Thanks, there would not be any modifications of any kind necessary.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#2

Re: Wire Size When Replacing Machine.

06/07/2011 4:12 PM

Circuit breakers protect wire. It's the other way around that you would be worried about. Your concern here though is that your old wire isn't too physically big for the lugs on the new breaker. Also, why are you replacing in the first place. A failure of some sort in the past could have damaged your wire. If you're not just strapped for cash, I,d go ahead and R+R the wire too.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Power-User

Join Date: May 2009
Location: Amarillo, Texas, USA
Posts: 188
Good Answers: 10
#4
In reply to #2

Re: Wire Size When Replacing Machine.

06/07/2011 4:17 PM

Thanks for your comments. We moved into the building about 2 years ago and had new wire ran then. I am replacing a 1988 machining center with a new one, much faster and uses less electricity. There will not be any problems with the lugs. I was concerned about resistance in the larger wire, not sure why.

Register to Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#5

Re: Wire Size When Replacing Machine.

06/07/2011 4:24 PM

De-rate the breaker to suit the new equipment, attach the lines, and away you go. No issues that I can think of as long as nothing has been modified. The new wires will carry the load, and actually will have less resistance than a set designed for the new machine (considering the wires are in good operational condition and have not been overheated).

Sounds like you are good to go.

Enjoy the new equipment!

-R

__________________
Don't believe everything you read on the Internet!
Register to Reply
Power-User

Join Date: May 2009
Location: Amarillo, Texas, USA
Posts: 188
Good Answers: 10
#6
In reply to #5

Re: Wire Size When Replacing Machine.

06/07/2011 4:29 PM

thanks,

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#10
In reply to #5

Re: Wire Size When Replacing Machine.

06/08/2011 9:05 AM

I apologize in advance for getting very picky. ;-)

I would not use the term "de-rate" the breaker. I'm trying to think of a good example when you'd realistically de-rate the breaker (or anything)--de-rate implies (to me) that you use the existing breaker but apply it (that is, consider the rating) less than what it really is.

Maybe (not a good example) you'd derate a breaker if it was in a much higher ambient temperature condition than it was originally designed / rated for--maybe at 50 degrees C a 100 amp breaker should be derated to 80 amps.

What needs to be done here is replace the breaker with one suitable for the new machine, which, iiuc, is 60 amps.

(I was going to respond to this thread earlier--some machines (e.g., home electric furnaces) (sometimes) come with suitable overcurrent protection built into the equipment. If that is the case here, I'm pretty sure the 100 amp breaker could be left in place at the panel (to protect the old wires), because the overcurrent protection built into the machine would be suitable for protection of the machine.)

Now, should I mark this OT, or count on someone else doing it soon (after RVZ717 has seen it)?

Register to Reply
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#11
In reply to #10

Re: Wire Size When Replacing Machine.

06/08/2011 11:16 AM

What I meant by De-rate (poor choice of wording) is "replace with one of lesser value".

__________________
Don't believe everything you read on the Internet!
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#12
In reply to #11

Re: Wire Size When Replacing Machine.

06/08/2011 11:45 AM

Thanks for the reply--I was sure that was what you meant!

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#7

Re: Wire Size When Replacing Machine.

06/07/2011 4:32 PM

You could also install a new breaker panel fed from the existing 100amp breaker and have additional circuits available for expansion.

__________________
Mr.Ron from South Ms.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2009
Location: Amarillo, Texas, USA
Posts: 188
Good Answers: 10
#8
In reply to #7

Re: Wire Size When Replacing Machine.

06/07/2011 6:05 PM

Thanks ronseto, that is something to consider.

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#9

Re: Wire Size When Replacing Machine.

06/07/2011 11:47 PM

Sure you can - no detrimental effect.

Have you heard of Sir Isaac Newton.

He cut a big hole through main door for his(fat) cat to go out.

Later Sir Newton brought home a small cat . And NOW he cut a SMALL hole for small cat to go out!

Register to Reply Score 1 for Good Answer
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dgibson (4); KJK/USA (1); MUKULMAHANT (1); RDGRNR (1); rhkramer (2); ronseto (1); RVZ717 (2)

Previous in Forum: Automatic Transfer Switch   Next in Forum: How we can calculate “tone” in HVAC system?

Advertisement