HT Motors

07/22/2011 2:02 AM

why do we use star connection for ht motors

Register to Reply
Pathfinder Tags: ht motors
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: ht motors

07/22/2011 2:05 AM

Because you differ from people who use delta connection?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jul 2011
Posts: 13
#2
In reply to #1

Re: ht motors

07/22/2011 2:13 AM

well tried but sorry thats an uncool answer anyways

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: ht motors

07/22/2011 2:20 AM

Tough.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#4

Re: ht motors

07/22/2011 5:21 AM

Think about voltages and insulations. (primary)

Think about starting current (socondary) and why not go for star-delta starters (third point)

The interviews does not expect you to know, it tests (at least should had I been the interviewer) your capability to think.

Both this question as well as the other you have posted falls on same category.

Did you think the resistance/impedance of an (ideal) ammeter and volt meter. How to connect them so that even if they are exchanged nothing happens?

Under this condition which meter would read what?

Was it really difficult?

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 10
#5

Re: ht motors

07/22/2011 6:09 AM

because of star connection only V/sqrt(3) apllied across one winding which reduces starting current and starting torque useful to reduce voltage dip during starting and avoid jerk in the loads on the same line

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: ht motors

07/26/2011 8:31 AM

Starting torque?

The load determines the torque!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: HT Motors

07/26/2011 10:52 AM

The most obvious reason is to reduce the insulation costs. With a Delta connecetion, the pahse and the line voltages are same and hence the phase to earth insultaion has to be made for the line voltage. Alternatley, with a star connection, this needs to be done only for the phase voltage, which is about 57% of the line volatge. And, believe me! the difference in cost is quite considerable.

Then, you might ask, why not this is followed in LV Motors? Wouldn't you? In LV motors, there is not much cost difference between phase voltage (240V) insulation & Line voltage (415V) insulation. If you connect the windings in delta, you have an advantage (i.e.) for the same line current (kW output), the motor windings would carry only the phase current and thus the heating in the windings would reduce by 3 times.

In LV heating cost advantage outweighs the insulation cost and in HT it is vice versa. Hope it is clear.

Register to Reply
Anonymous Poster #2
#8

Re: HT Motors

07/26/2011 5:12 PM

Hi

you can use star or delta connections in HT motors...when it is connected in Delta you motor runs stronger

Register to Reply
Anonymous Poster #1
#9
In reply to #8

Re: HT Motors

07/27/2011 6:36 AM

Interesting concept. may I (I hope most of us) will like to know what is the meaning of when it is connected in Delta you motor runs stronger

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: HT Motors

12/25/2013 3:06 AM

Dear Mr.geetartha,

In HT Motors, Star Connection means Phase Voltage = Line Voltage/ Sq.Root of 3.

If 11 KV is the Supply Voltage for HT Motor, then the Phase Voltage will be 6351 Volts, i.e.6.351 KV, hence Insulation cost will be more Economical.

DHAYANANDHAN.S

Register to Reply
Register to Reply 10 comments