HVAC Electrical Room Cooling Dilema

10/05/2011 8:21 PM

We recently installed some electrical equipment and an instrument cabinet in an existing electrical room. The electrical room temperature is now going up due to the heat emmission of the new cabinet. The capacity of the existing central HVAC system is not enough to cool down the additional heat. Increasing the existing HVAC capacity and replacing the ducting is very troublesome for this system. We are thinking of adding a standalone HVAC unit to this room in addition to the existing HVAC system. The wall of the room is fire rated and I want to avoid making any penetraion for the duct work. Also water systems are not allowed in the room. Could anyone please suggest a possibly solution for this issue?

Thanks,

Kiran

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: HVAC issue

10/05/2011 8:41 PM

You could have prevented the issue altogether by planning for it before hand.

So, first, fire the person responsible for the installing the system without giving any thought to the additional heat load.

Then, with that person gone, hire someone who can see the entire installation first hand to solve the problem. There's no magic window here.

Without numbers and more site information, all you can do is maybe run a cooling hose out the door, or maybe through the roof.

Good luck.

Reply
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#2

Re: HVAC Electrical Room Cooling Dilema

10/05/2011 10:17 PM

Can you install an in-line duct fan that will pull more of the cooled air into this room? This does not require any increase to the existing HVAC system, nor any additional ducting. If other parts of the building suffer as a result of sending more air to the electrical room, an additional HVAC system could be added elsewhere where it would be more conveniently installed.

http://www.espenergy.com/in_line_duct_fan.htm

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Reply Score 1 for Good Answer
3
Participant

Join Date: Jun 2011
Posts: 2
Good Answers: 1
#3

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 7:56 AM

I would suggest a mini-split A/C system such as a Sanyo or Mitsubishi. You can mount the indoor unit on the wall or ceiling.The only penetration would be a 3" hole for the line-set and condensate;which can be easily fire-caulked.The only concern is how far you are from an exterior wall or roof to mount the condensor and where you can tie the condensate into a drain.They can be equipped with a condensate pump if you need to tie in above the room. They are variable capacity and when running steady-state are efficienct.

Reply Good Answer (Score 3)
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#16
In reply to #3

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 11:29 AM

GA from me. My first thought, before reading any comments, was that this would be an ideal situation for a mini split. -- JHF

__________________
If it's too good to be true, it probably isn't
Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#4

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 9:25 AM

How about louvers in the door to the room.

One in the top and another in the bottom will encourage a sort of thermosiphon. I have used this technique with success a number of times.

You mentioned a fire rated wall. Is the door in a rated wall? If yes, there are fusible link louvers available for fire rated doors.

__________________
Semper Ubi Sub Ubi
Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#5

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 11:51 AM

Johnroy is right. Do as suggested.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 10:39 PM

You will have a hell of a time balancing two independent cooling system in one airspace. Increase the present one's under one controller, or as a poor second watch carefully and regularly them. The problem is, that, if the smaller happens to be set a bit lower, it does not cycle off, and accumulates ice, freezing up.

Reply Score 1 for Off Topic
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#22
In reply to #6

Re: HVAC Electrical Room Cooling Dilema

10/08/2011 11:51 AM

Blank off the air duct of the existing and use the Split A.C. We do that in Control panel rooms and face no problem.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#7

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 10:50 PM

Hi Kiran,

If your door panel is swing out. what about to put an ducted exhaust fan directly from the new electrical equipment cabinet connected to the top portion of door panel with the rectangular end hole, the end point of the duct must be self sealed when you close the door, then you can remove the heat load directly coming from the new cabinet, this is i think most economical way. we did this in one of my project in the past and work efficiently with out additional cost in investing Split AC and low in operational and maintenance cost compare to split Ac.

Kind regards

Roman

Reply
Commentator

Join Date: Feb 2010
Location: Ceres, CA.
Posts: 61
#8

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 10:59 PM

Tell us about the walls of this room. Are any of them the exterior wall of the building? What is their make up.

How about the roof? Metal? Rolled roofing?

Could raising the solar reflectivity of the exterior surfaces enough to drop the heat gain of the building by around 50% help your problem? We have done that many times in commercial buildings with our coating.

Hal

Reply
Participant

Join Date: Sep 2011
Location: Wherever my tractor/trailer is...
Posts: 2
#9

Re: HVAC Electrical Room Cooling Dilema

10/06/2011 11:45 PM

If you have a clean compressed air supply, you could use a vortex chiller on the new cabinet, it cools the internal area of the cabinet in the same way a carburetor chills the fuel/air mixture entering an engine. Drawback, can be noisy if not silenced on exit. Used this on Navy test stands where fuel vapors were prevalent and sparks of an electric motor could be an issue.

__________________
There is no gravity, the Earth sucks!
Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#17
In reply to #9

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 12:13 PM

No matter what the heat is still in the room. It has just been moved from the cabinet.

As John stated the best solution is the Mini split. Depending on the building and its design, the condenser can be located in a return air plenum just outside the room keeping the cost down on installation. Or if located on an outside wall, core it and fire caulk it so you don't have to use a pump in the room for condensate. The inline pumps the MFT sells are crap and die leaking water into the room. If you need a pump look to a sump style (little Giant) pump to be wall mounted in the room.

__________________
To be or not to be........ok that's a trick question.
Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#10

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 2:02 AM

The new electrical equipment and the instrument cabinet can be fitted with an independent panel cooler and the exhaust of this panel cooler could be connected directly to the control room exhaust. If you could furnish some of the details of the additional heat load like the physical sizes and the control room general layout, it might be possible to suggest a better alternative.

Reply
Power-User

Join Date: Jul 2007
Location: Hyderabad, India
Posts: 212
Good Answers: 3
#11

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 6:56 AM

I would suggest a heat pipe based heat exchanger to throw the warm air from inside the panel to outside ambient air. However, as others asked, geometry of walls as well as placement of panel w.r.t. wall distance is to be known.

There is a possibility to handle this heat independently.

__________________
B +ve
Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#12

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 6:56 AM

Had the same problem in Malaysia, ambient outside 30C

Thyristor drive was added in the switchroom with another 10kW-20kW of waste heat, and no one anticipated that these would be added in the design some 20 years earlier.

The equipment cabinet had its own fans, we used these to duct the air outside with a sheet metal ducting made locally to fit, with a mesh at the outlet to stop flies/vermin. Not much more than a hood as this was an outside wall. This pulls in more via the HVAC makeup air which was around 10%, i.e. fresh air from outside. You need to consult with the HVAC designers to adjust the existing vents for make up air which is already happening, the system doesn't recirculate the same air, it adds a percentage of fresh air based on occupancy & other factors. This way all the heat from the thyristors went directly out and did not have any effect on the switchroom HVAC.

I did consider an independent inlet and outlet with extra fans, with flexible ducting to the outside air. The thyristor drive cabinet was designed to operate at ambient temperatures above 30C so with sufficient air movement and monitoring to check cabinet temperatures I considered it a workable solution. But the last paragraph design has been working for over 10 years now with no problems.

Reply
Anonymous Poster #2
#13

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 9:49 AM

Its a good thing that you guys planned ahead.....

Who would have thought that additional electrical equipment would be adding heat to an existing room ..?????!!

Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#21
In reply to #13

Re: HVAC Electrical Room Cooling Dilema

10/08/2011 11:49 AM

Absurd. A good Consultant is aware of this. Please note my personal experience that not only should you be aware of the heat electrical equipments and panel give off, it is important that you should take into account from which country your equipment is coming from. Say all equipments/panel from USA/Europe or colder countries would give problem in hot countries like Pakistan & India because they all have a maximum ambient temperature to operate. irrespective, all panels with lower ambient operating temperatures are enclosed in my projects separately in a room with split a/c.

Even a small 1/4" solenoid valve of Asco in my burners are specified with "H" class coils because the standard to not last long particularly when the ambient temperature goes above 110F.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply Off Topic (Score 5)
Guru

Join Date: Dec 2009
Location: Kansas, USA
Posts: 748
Good Answers: 64
#14

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 10:03 AM

We have used Liebert Units in our IT Data Center rooms and they provide very good temp and humidity control. Your firewall will have to be penetrated for set lines (seal with fire caulk) and you will need space for a condenser pad outside, etc.

With a different type of solution you add a new supply ducting and more return air ducting. You will then need to add fire dampers in the ducting.

__________________
One of the greatest discoveries a man makes, one of his great surprises, is to find he can do what he was afraid he couldn't do. Ford, Henry
Reply
Associate

Join Date: Jul 2006
Posts: 36
Good Answers: 1
#15

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 10:51 AM

We have several computer server rooms that utilize a small (wall mounted) split system similar to what Johnroy noted in his posting. Condensate is removed via a small pump and dumped to drain in another room. While the heat load is not as large for these applications as an mcc room, larger split systems are available. As a precaution, we installed a temperature alarm system to call the IT department if the room temperature exceeds a certain value; if you have concern that equipment may shut down unexpectantly if the electrical room temperature gets too hot then you might want to consder this notification feature.

Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#18

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 7:03 PM

Hi Kiran:

A split system with an air cooled condensing unit outdoors and an air handling unit (AHU) in the electrical room sounds like the easiest approach. There would be two refrigerant lines conecting the cooling coil in the AHU with the condensing unit requiring two round holes in the fire rated wall. Properly sealed they will not comprimise the fire rating. It is imperative the condensing unit has the necessarycontrols for proper starting and operation during the coldest winter conditions expected.

It's not rocket science but you will need a contactor who is qualified in the HVAC field. It will be important this contractor includes a control system designed to stage the existing and the new system for their proper sequencing. Well designed, the entire system will be simple and stright ahead. No bells and whistles required if done right. After installation the system will need to be professionally maintained to provide you with reliable and economiocal operation and longevity just as you hope the airline of your choice is providing for the plane you happen to be flying on.

Good luck,

Lou Bindner

Denver, CO

Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#19
In reply to #18

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 7:42 PM

One hole penetration for the insulated copper, drain line and EMT should suffice. Just be sure to seal it well.

As far as taking control of the system....stage it. Use the existing house system to control the room temp to the desired set point (though I understand it will not get there on its own now) and stage the remote style stat that comes with the mini split 5 degrees higher. So when the room warms both units run and when the room begins to drop in temp to set point the mini split will turn off having the house system carry the load until it warms up again. Hopefully once you get the concrete in the room cold it will help maintain the thermal load evening out run times.

__________________
To be or not to be........ok that's a trick question.
Reply
Anonymous Poster #1
#20
In reply to #19

Re: HVAC Electrical Room Cooling Dilema

10/07/2011 10:57 PM

Thanks every one for the valuable comments. I see great people are always here to help.

Since I am not an HVAC person, we will consider each of comments with the HVAC specialist to move forward to the resolution.

Kiran

Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#23
In reply to #19

Re: HVAC Electrical Room Cooling Dilema

10/10/2011 4:08 PM

My suggestion of a 'split system" was too general. Providing that the additional capacity required falls within the capacity range of mini-split systems that would be my choice also. The added cost of a two stage control system which will automatically bring on the added second stage when needed will be funds well invested.

I wouldn't advise attempting an "exhaust system" unless the temperature of the makeup air is the same as the desired temperature you are trying to maintain in the space in question. Go with a design/build team who will...keep it simple, keep it simple, keep it simple. This is not brain surgery as long as your design/build team knows their stuff. Attention to low ambient control of the added system is paramount.

Good luck

Lou Bindner

Reply
Reply to Forum Thread 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); capri (1); Circuit Breaker (1); Doorman (1); ducon (3); engineertony (1); facilitiesmgr (1); halskinner (1); johnroy (1); kbp1958 (1); kfkaralius (1); leveles (1); Lou Bindner (2); lyn (1); Priyadarshan (1); Roman (1); Stedou73ish (2); Usbport (1)