12/07/2011 8:54 PM
is it Necessary to maintain 10D & 5D straight Distance in Pipe for installation of Pitot Tube for flow measurement?
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member
Re: Pitot tube
12/07/2011 10:14 PM
In my experience...Yes for flow measurements....
Having said that.... Check the installation instructions.
Regards,
Sapper.
It's all about the Boom! - MythBusters
Good Answers: 49
Re: Pitot Tube
12/08/2011 11:07 PM
Those generic dimensions GENERALLY provide adequately "straight-line" flow needed to measure effectively, although SOME conditions would require even longer runs for optimum effect (seriously turbulent incoming flow OR rapid volumetric change or significant obstruction (including a grille or diffuser) down stream (that might trigger an erratic or non-standard pressure rise).
If your installation is "challenged", the best effective solution is to install two sets of 1/2" mesh thin-wall grids, spaced about 1xD apart, at least 1xD upstream of the pitot tube inlet. Such an arrangement would also help with the downstream "upsets" noted earlier as a way to give maximum downstream spacing.
Like just about any measurement system, you have to analyze the conditions.
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Re: Pitot Tube
12/09/2011 3:06 AM
Yes, though it is also possible to do a traverse across the pipe to establish the actual velocity profile, which is important in airflow-in-duct measurements.
Good Answers: 179
Re: Pitot Tube
12/09/2011 9:36 AM
IMO, yes.......those distances should be adhered to and free of any obstructions whatsoever. In most flow meter installations, especially when water flow is being measured, you want to be in a laminar flow regime. Also, you had better do a calculation check of the Reynolds and the Froude numbers during the design phase and before installation of any flow meter.
Re: Pitot Tube
12/09/2011 11:52 AM
Dear Mr. Lalit nawada,
The answer for your point is YES - 10 D and 5 D is minimum and can be more.
DHAYANANDHAN.S
Good Answers: 125
Re: Pitot Tube
12/09/2011 11:57 AM
You don't fully describe what you are doing. If you are checking a municipal water supply for adequacy, use 10D. Also, your data will likely include not only flow rate but also static and dynamic pressure readings.