Cable Size Calculation

12/13/2011 8:20 PM

Please help me to calculate the cable size for ,

1. 6.6kv, 510Kw , 50hz, Compressor Cable length 120M / underground

2. 110kW Blower, 415V, 3 phase, 50hz, Cable length 120M / underground

Please calculate the cable size.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Cable Size Calculation

12/13/2011 8:32 PM

No! Do your own homework.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Cable Size Calculation

12/13/2011 9:09 PM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Cable Size Calculation

12/14/2011 3:15 AM

...or go to British Standard 7671.

Next!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Cable Size Calculation

12/14/2011 4:20 AM

There have been countless posts on CR4 about "cable size calculation". As a practical matter, cable sizes are not normally calculated; instead, they are looked up in tables from electrical Codes and cable manufacturers. Of course, somebody sometime had to calculate the numbers that are given in such tables, but the calculations are too complex for easy day-to-day use. That is why the tables have been calculated beforehand, enabling users simply to look things up. Most local/regional/national Codes have this information. Please purchase a copy of your local Code, and go from there.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Cable Size Calculation

12/14/2011 7:26 AM

Pl. attend to our training programme on EDSA-A (Electrical Design of Switchgear Assembly-Advanced) wherein we also teach cable selection.

Register to Reply
Active Contributor

Join Date: Aug 2011
Location: Hyderabad
Posts: 14
#6

Re: Cable Size Calculation

12/19/2011 5:36 AM

1. 6.6kv, 510Kw , 50hz, Compressor Cable length 120M / underground?

Ans). Cable Size is 3.5C x 120Sq.mm XLPE Aluminium Armoured Cable, Full load Current is 124.34A after considering derating factor and voltage drop is 1.89% for this cable.

2. 110kW Blower, 415V, 3 phase, 50hz, Cable length 120M / underground?

Ans). Cable Size is 3C x 16Sq.mm XLPE Aluminium Armoured Cable, Full load Current is 28.99A after considering derating factor and voltage drop is 2.85% for this cable.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); lyn (1); PWSlack (1); Tornado (1); vasu.srinu001 (1); wareagle (1)