Induction Problem

12/16/2011 10:52 PM

We are having WEIGH FEEDERS for feeding raw materials.During installation all control cables are laid along with power cables(including drive outgoing cables).Recently we are facing induction problem.Value of Tacho automatically varies without ON weigh feeder.

Tacho Input:12 Volt dc

Tacho output:Varies from 08 volt to 11 Volt dc

We laid screened cable & grounded & grounded both sides also checked with one side grounded.

What precaution we can do to reduce this Induction problem

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Induction problem

12/17/2011 1:26 AM

Some various approaches I have heard of are:

1. Segregate conductor of widely differing voltage levels.
2. Use twisted pair shielded (screened) cable for sensors and logic signals.
3. Ground (earth) one end only of cable shields. The more usual preference seems to be to ground the sensor end.
4. If cables must cross near each other, arrange the crossings to be 90°.
5. For panels containing both logic and power cables, have the cables enter from opposite or different sides.
6. Pass the logic cables through ferrite cores.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4
In reply to #1

Re: Induction problem

12/18/2011 6:49 AM

All good solid and useful infos, gained from real experience I suspect!

Furthermore, low level signals sent over relatively long distances, often need to be sent as twisted pairs with a differential transmitter and receiver, especially where cables with higher level signals are close, mains voltages for example...

Changing the mains voltages to DC (for low current applications) can also often help, but sometimes difficult to arrange/achieve after the event!......

Otherwise cables need routing "apart" as you so correctly mentioned!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Jan 2012
Location: Australia
Posts: 49
Good Answers: 1
#13
In reply to #1

Re: Induction problem

01/17/2012 6:45 PM

Couldn't have said it better. One solution I have heard is to put a very small ceramic capacitor in parallel with the tacho terminals. This may help to dissipate some of the transience induced by motor starting etc. However it's a bandaid solution. All of the above mentioned are definately preferable. Hope this helps.

__________________
An educated man is not necessarily knowledgable, but has the intellect to call upon his resources.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Induction Problem

12/17/2011 8:31 PM

As Tornado says, ground one end only of shield. A common resolution to this problem is to ground the source end only to power supply negative (not panel ground). This would apply to all signal cables.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Associate

Join Date: Oct 2011
Posts: 25
Good Answers: 1
#3

Re: Induction Problem

12/17/2011 11:15 PM

If possible isolate zero volt side of tach output from all other zero potentials (grounds) If you have an oscope you can see spikes from the AC power you are near. If you are checking voltage with a meter you will see a small amount of voltage if you check for AC on your DC tach. Either device is helpful for checking your progress. I have lived in your exact shoes recently, and isolating tach is the best after you have switched to twisted pair with one side grounded shield.

Register to Reply
Power-User

Join Date: Sep 2006
Location: Houston Texas
Posts: 282
Good Answers: 16
#5

Re: Induction Problem

12/18/2011 12:13 PM

Other areas to consider:

Check the grounding of the individual weigh feeder motors, and measure the frame voltage potential to true ground while starting each motor. We had a problem with a feeder retrofit where the net weight would jump 50 KG whenever a motor started. We could not find the issue until our scale tech was zapped by the loadcell shield wiring. The motor was attempting to ground itself through the scale wiring.

If your weigh feeder controller is PLC-based consider using a communication network (EtherNet/IP, DeviceNet, etc) to transmit the signals. Mount the tach and weight transducers directly on the weigh feeder frame to ensure they float at the same ground potential as the motors. Having a local network also allows for easy control expansion in the future.

__________________
Specializing in Dynamic Weighing Systems for Powder and Bulk Solids Handling
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#6
In reply to #5

Re: Induction Problem

12/18/2011 1:41 PM

First is to look at this on an oscilloscope, is it 50 Hz on top of your DC output? Is it some high frequency from VSD or other stuff? If it's hf you may be able to filter with ferrite ring or capacitor filter across the tach output, you can see the effect on the 'scope.

These problems are often cause by loops, grounding should be in a tree formation, no loops. Also by power & instrument interaction, separate the power gounding to a single point, and similarly the control and instrumentation.

If you can isolate the tacho output signal from ground and receive it via two wires at a differential amplifier, then any pick up is cancelled as the amplifier only sees the difference between the two wires. The differential amplifier output will feed whatever circuit input you have at the moment.

I have some 4-20mA isolation modules at the moment, power in, 4-20 mA in, and 4-20mA out all electrically isolated. I think they exist in volts modules also, you might try to isolate the tacho volts from the tacho line volts because your problem may be an electrical circuit from the tacho power supply, is the -ve 12 volts grounded? Where?

Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#7

Re: Induction Problem

12/18/2011 4:58 PM

It is not just the signal wires which need attended to. A.C. variable drives should have a filter/choke/transformer mounted close after them to capture the worst transients. This reduces the interference caused by the cabling to the motor.

__________________
Madness is all in the mind
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#8
In reply to #7

Re: Induction Problem

12/18/2011 6:10 PM

GM1964,

Agreed, mine are Mitsubishi and they are mounted on a EMI filter which is supposed to block all those transients & spikes. All the inputs are electrically isolated from the mains.

I did have a problem similar to this with an encoder, the pulses had little glitches when I looked on the 'scope. The screen wasn't earthed at all, cured it with an earth at one end, I suspect this guy has a similar connection problem.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Induction Problem

12/19/2011 10:20 AM

<...reduce this Induction problem...>

Change the transmitted signal to a current-based one, such as 4-20mA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10

Re: Induction Problem

12/19/2011 6:47 PM

If the tacho DC output is showing readings on a DC moving coil (insensitive to most noise) which are "not-reasonable, then it is most likely the AC input signal to the tacho is being corrupted by pick-up. You need to look at the screening and grounding of the connection to the tacho probe.

Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#11

Re: Induction Problem

01/12/2012 7:23 AM

Routing signal wires next to variable-frequency drive cables is a recipe for disaster. One time I encountered a problem where a 4-20 mA signal became corrupted by noise simply by being lashed onto a drive conductor with a plastic wire-tie, and this was even on a properly shielded cable! Never, never route signal wires in the same conduit as power conductors, especially power conductors feeding or coming from VFDs with high-voltage spikes and high-frequency harmoncs.

One possible solution would be to replace the voltage-based tachometer with a pulse-type encoder, where the on/off pulse signal would be more immune to noise, but this would require signal conversion back to analog at the weighfeeder controller, and even then would not be a guaranteed solution given the amount of noise you're probably experiencing.

When you look at all the time, effort, and money you might spend on trying to solve the noise problem, installing a separate run of conduit for the signal wires starts looking pretty cheap.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12
In reply to #11

Re: Induction Problem

01/13/2012 6:20 AM

I agree with Tonykuphalt's remarks on putting signal & power cables together being a recipe for trouble.

Good specifications I have seen for plant installations require about the following distances between signal cables and other cables in runs.....

15 cm to DC control cables.

30 cm to AC cables (115/230V single phase).

100cm to high current or voltage cables.

-- and of course, separation of DC & single phase AC & power also applies.

At the design stage, just putting signal cables in a tray/hangers at top left of a duct, with other cables bottom/right can avoid trouble. But when the cables have been installed together and twisted round one another (always seems to be the case for the one cable you want to separate) fixing it is a major problem!

Shielding is no substitute for separation, at power frequencies effective shieldings are very expensive and less effective than separation.

67model

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); AKdude (1); Andy Germany (1); Delmar (1); engineertony (2); GM1964 (1); PWSlack (1); tonykuphaldt (1); Tornado (1); WJMFIRE (1); wopx8z (1)

Previous in Forum: ABB DCS   Next in Forum: Which is More Accurate DPT or Flow Meter

Advertisement