Temperature Rise At Upper Thrust Bearing Of Generator

01/09/2012 11:20 AM
Sudden Rise of Temperature at Upper Quide Bearing of Generator
As Hydro Engineer...please help me

I got a temperature rise at upper thrust guide bearing of generator (34MW,11KV & Ns=145rpm) at my working plant ..primarily i was thinking maybe my sensors was defectives but trouble shooting revealed that the sensors was okay...and cooling system (especially water flow at cooler parts is still Okay and water is clean ) but machine still trip at high Load ie 30,31,32,33MW at temp 78c.I don't know what's wrong with machine.

<email removed>

Sunday Matembo

Maintenance Engineer-Hydro Plant

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: TEMPERATURE RISE AT UPPER THRUST BEARING OF GENERATOR

01/09/2012 12:00 PM

What does the original equipment manufacturer have to say on the topic? How long ago was the telephone call made, and why is the response unacceptable?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: TEMPERATURE RISE AT UPPER THRUST BEARING OF GENERATOR

01/09/2012 1:12 PM

I would put a separate test sensor on the system with a graph and chart both the system sensor and my test sensor. I'd also check the water temps on the cooling system, incoming/outgoing. Your answer will be in that data.

Register to Reply
Anonymous Poster #1
#7
In reply to #2

Re: TEMPERATURE RISE AT UPPER THRUST BEARING OF GENERATOR

01/11/2012 2:07 PM

Fredski

The thing is, its very diffucult to remove sensors bcos its inbuilt otherwise major assembling (major overall) is reguired which is more costly as assembling new one ,secondly u know time consumed while m/cs always its in production.Water system is clear and cool and we use it in cooling system. of m/cs.

Register to Reply
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#3

Re: Temperature Rise At Upper Thrust Bearing Of Generator

01/09/2012 2:51 PM

So you are running and tripping at close to the rated load. Do you think this might have something to do with the relatively high temperature???

What is the trip set at, it it possible that protective devices are working as intended?

Do you normally or have you always ran the equipment at this percentage of load?

Again as another poster already asked, what does the manufacturer say about your situation?

Register to Reply
Participant

Join Date: Jan 2012
Posts: 2
#4

Re: Temperature Rise At Upper Thrust Bearing Of Generator

01/09/2012 8:33 PM

dear sir , how i contact you. our compay jinan levo bearing im.& ex. co., ltd. are the professional manufacturee of the bearings. our engineer maybe help you .

best wishes,

bill li

Register to Reply
2
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5

Re: Temperature Rise At Upper Thrust Bearing Of Generator

01/10/2012 12:04 PM

Upper thrust guide bearing indicates a vertical turbine generator. You have should two separate bearings in a common oil bath. The thrust bearing is supporting the entire weight of both the generator rotor and the turbine runner, while the guide bearing centers the shaft and prevents excessive oscillation.

There are several possible causes, but more information would be helpful. Is the sensor measuring the temperature of the bearing itself or of the oil? If it's in the bearing metal, is it the thrust bearing or the guide bearing?

I would start by checking the oil system. Is the oil contaminated? Is the oil pump actually pumping oil from the bath/sump through the cooler and back? Is the oil filter clogged? Has the oil flow rate changed?

If everything on the oil system is good, check the bearing clearances. If clearance is the issue would suspect the guide bearing first. A clearance issue on a vertical thrust bearing usually sends temperature straight up off the chart.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Good Answer (Score 2)
Anonymous Poster #1
#6
In reply to #5

Re: Temperature Rise At Upper Thrust Bearing Of Generator

01/11/2012 1:56 PM

pwr2thepeople

hi pw.....u know there separately sensors for oil and temperature ...i gatta no problems in oil sensors in same segment bcos if i could, then alarm would be indicate d in masterview computer or other indication device like sacco.Most confussion it comes when there is no bad or tripping at other sensor at the same segment .My generator have old segment(1,3,5,7....) and (2,4,8..) but this problems it come from seg7 and its upper thrust bearing. Plse u dont have to worry about oil bcos sensor is clear.

contact me:for more infro....its killing me.

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Fredski (1); levobearing (1); pwr2thepeople (1); PWSlack (1); Tim in Mexico (1)

Previous in Forum: Types of Hormonic Current   Next in Forum: Reverse Power on Diesel Engine - 415/240Vac

Advertisement