Sodium Lamps

01/30/2012 4:02 AM

Hi All,

I need to install 3 cold-start sodium lamps. Each one is 400w, giving a total power of 1.2kw. The line voltage is 230v. Can I get away with using a 6 amp mcb or do I need a much larger one, i.e. is there a current surge at start up on these type of lamps?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Sodium lamps

01/30/2012 4:10 AM

Match the circuit breaker to the wiring, just as British Standard 7671 requires. After all, it is the wiring that the breaker is selected to protect....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#2

Re: Sodium lamps

01/30/2012 4:12 AM

its look like learning swimming by postal.....

Register to Reply
Anonymous Poster #2
#7
In reply to #2

Re: Sodium lamps

01/30/2012 9:16 AM

Fly by internet wire.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Sodium lamps

01/30/2012 4:18 AM

There will be some current surge on start, but right off hand I don't know how much or how long. Running current is ~5.22A, so I wouldn't be surprised if it takea a 10A or 15A circuit breaker to handle the starting current. Determine that first, and then size the wire accordingly. (In the U.S., it would probably be 15A breaker and 14AWG wire, but your local requirements may differ.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Sodium lamps

01/30/2012 7:01 AM

Switching of discharge lamps is called Utilisation Category AC5a and calls for switching on and switching off 3X the rated current for 50 opeations, as per IEC 60947-4. You should really use a contactor for this duty, since it is meant for millions of operations. The MCB should be used for protection, preferably, not switching.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2012
Location: Tema
Posts: 25
#5

Re: Sodium lamps

01/30/2012 7:30 AM

yes i think u can u the 6amps MCB for your work. The total amp of the lamps is I = P/V = 1.2kv/230 = 5.217amp. In future u can add more load to it.

Register to Reply Score 2 for Off Topic
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Sodium lamps

01/30/2012 8:01 AM

Er...i read somewhere that gas discharge lamps operate at ≈ 0.5 PF (i could be wrong). If this is correct, the 6A MCB itself is a wrong choice. It will certainly nuisance trip. And, as i said, an MCB is not the best device anyway.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8

Re: Sodium Lamps

01/30/2012 1:20 PM

These should be on thhn #10 with 30A breaker, then individually fused with cartridge dual element 10A fuses...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
4
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#9

Re: Sodium Lamps

01/30/2012 2:35 PM

You will need to use a larger MCB, and/or use a D-curve breaker for best results.

On startup, on the striking of the arc, a discharge lamp tube initially has a very low impedance, and looks a lot like a short across the output of the ballast. As the tube warms up, more and more sodium (and other elements in the arc tube) vapourise and join the party, and the impedance of the tube increases so decreasing the current.

This means that there is a significantly larger current drawn during the first 2-3 minutes of operation than in the steady state. Just how much larger will depend on the type of ballast being used : If it is one of the old-fashioned reactor/choke-type ballasts that are commonly used on 230V discharge lamps, the startup current will initially be a little more then 2 x steady state, for perhaps 15 seconds or so; If the ballasts are the new you-beaut switchmode electronic type the startup will be a little less.

If you consult the ballast manufacturer's datasheet, this should give you some more accurate figures.

__________________
paulusgnome
Register to Reply Good Answer (Score 4)
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#10

Re: Sodium Lamps

01/31/2012 3:20 AM

discharge lamps take a massive current on start up - in the order of 30 times for a few milliseconds

Check manufacturers recommendations but a 10A or maybe 16A type C would do a single 400W lamp.

Suggest you go from 3 phase - use a contactor and a 10A type C MCB for protection.

The type B or C is important.

Remember you have to protect the wiring not the device so if your cables are not protected by a 10 or 16A MCB you will need to upsize.

The Merlin Gerin cat, as do others, will give you some good hints on breaker sizing.

If you are asking these questions though maybe its time to get a qualified guy.

Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 22
#11
In reply to #10

Re: Sodium Lamps

01/31/2012 5:32 AM

You must also take into account the voltage drop in the supply cables. If this is too high the lamps may not start up at all. This has happened to me! If I had the units I would rig up a test circuit and check the startup current myself. Better safe than sorry.

Register to Reply
Power-User

Join Date: Jan 2008
Posts: 127
Good Answers: 5
#12

Re: Sodium Lamps

01/31/2012 3:08 PM

We run 400w sodiums in our factory using 2.5 mm cable, 20 amp breaker and a 15 amp switch to run the 3 lights as a bank, if switching individually standard 10 amp switch should be ok. Naturally you will need to take length of cable run and how it is run when sizing suitable cabling for your installation. The above is a guide only.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#13
In reply to #12

Re: Sodium Lamps

02/01/2012 8:07 AM

You do not say whether you are running these lamps on a single phase or on a 3 phase supply - 1 lamp per phase.

At 3 phase a suitably rated switch could switch 3 x 400W SONs and a 20amp breaker would suffice.

You are running into fixed equipment so you have a known electrical load. The 2.5mm cable is within the load limits of the cable and the breaker only really needs to clear a short circuit fault.

Volt drop is still a consideration and the I.E.E. regs require no more than 3% under normal load conditions.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#14

Re: Sodium Lamps

02/05/2012 3:08 AM

Please refer Schneider Electric - Electrical Installation Guide 2010 . Topic is Reactive energy and power factor . It says a pf of 0.4 to 0.6 is to be considered.

Also, ZUMTOBEL STAFF - The Lighting Handbook -Chapter 9 Page 18

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#15
In reply to #14

Re: Sodium Lamps

02/06/2012 5:11 AM

if you running lamps with a PF of 0.4 its time to put them in the skip. Most discharge lamps are around pF 0.8 with a further improvement if are running the ones equipped with an electronic ballast.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#16
In reply to #15

Re: Sodium Lamps

02/06/2012 6:33 AM

Its not my recommendation , its by Schneider Electric who suggested . I was just referring it.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#17
In reply to #15

Re: Sodium Lamps

02/06/2012 12:10 PM

It is not important whether the PF is 0.1 or 0.9 or in between....the OP is dividing Watts by Volts and arriving at Amps. And one more poster is supporting it !!! Can prove to be a dangerous mistake....

It is important, i think, that they appreciate that the current will be considerably higher (a) due to power factor being below 1 and (b) there is always a current surge when switching on the lamps.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#18
In reply to #15

Re: Sodium Lamps

02/06/2012 3:45 PM

"if you running lamps with a PF of 0.4 its time to put them in the skip. Most discharge lamps are around pF 0.8 with a further improvement if are running the ones equipped with an electronic ballast"

In smaller installations, one would usually use control gear with an integral power-factor correction capacitor which would give a PF of better then 0.8.

In larger installations, it is common to install the lighting without the integral PFC, and use a large, central PFC-correction system. Without the integral correction, the PFC of the lights may well be as low as 0.4. Nothing wrong with them, mind, that's just the way they are.

To accommodate these two scenarios, the switchgear manufacturer's data usually publish sets of figures for both configurations.

__________________
paulusgnome
Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#19

Re: Sodium Lamps

02/09/2012 3:48 AM

I have a 1000W SV lamp connected with three capacitor of 25µF.

4 lamps are from 32A MCB.

Register to Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#20

Re: Sodium Lamps

02/13/2012 11:08 PM

I know this has already been stated by other members but Appart from the selecting the correct type of MCB to handle the current surge at start up The only answer I see here is You size the cable to be able to take the load & select the correct MCB to protect the cable supplying the lights because the MCB is not there to protect the load on the circuit it is only to protect the cable. & often many sodium vapor lamps I have seen have had an individule fuse built into the fitting

This is taught to apprentises in first year college & I fear if you do not have this knollege/ training you may not be qualified to carry out the work & I sugest you employ a tradesman to do the work

Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#21

Re: Sodium Lamps

02/28/2012 1:50 AM

I haven't posted for a while so this is like cracking my knuckles.

Good answer to Paulusgnome who is also from NZ so double points!

Several things have not been mentioned.

First circuit watts. 400W is the wattage of the lamp. The lamp has a ballast which also requires power. Lamp manufacturers like Sylvania will give you plenty of information but a rule of thumb is 10% for conventional wire-wound ballast (CB) and 5% for electronic ballast (EB). So the circuit takes roughly 1320w (CB) & 1260W (EB).

Power factor is ~1 for EB but ~0.4 for CB. This is typically corrected with a capacitor to ~0.95. However the cap dries out in use and we do calcs at PF ~0.8.

So for conventional wire-wound ballast VA is up to 1650 which equals ~7.2amps @ 230V.

However you have to allow for power supply voltage fluctuation which is typically +/- 6%. So running current could rise to ~7.6amps.

This is the figure you need to calculate voltage drop. Your 6A MCB is history.

Hot re-strike next. This is when the lamp is turned on again after just being shut off. This could be due to a power drop-out say, or simple switching. The lamp could take 4-7 mins to re-strike. Typically at 2-3 times running current. This should trip a 10A MCB unless its a Type D. I'm not a fan of Type D and would prefer a 16A Type C in this situation.

For the real anoraks, during hot re-strike the lamp can behave as a rectifier and the resulting DC will saturate a wire-wound ballast. The PFC cap then acts like a virtual short-circuit. My secret squirrel files tell me the cap in a 400W ballast is 40 uF; I leave you to do the maths.

So EBs are best for these lamps.

However, who wants sodium these days? I would heavily recommend HID for better colour rendering.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#22
In reply to #21

Re: Sodium Lamps

02/28/2012 10:34 AM

Finally a decent answer. All points go to New Zealand. You would need to weigh the shorter life of HID against the poor colour rendering of the SON. Depends on the application.

No points for the Guru who thinks PF plays no part in Watts, Volts and amps.

Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: