Frequency 50hz System by 60 hz System

02/17/2012 4:58 PM

advantages over 50hz system by 60 hz system?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: frequency

02/17/2012 5:10 PM

Slightly smaller conductors?

OK, I give up. What are they?

Register to Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#2

Re: frequency

02/17/2012 5:38 PM

Higher better... smaller

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: frequency

02/17/2012 5:49 PM

None, it just is what it is.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#4

Re: frequency

02/17/2012 6:08 PM

During the development of commercial electric powersystems in the late 19th and early 20th centuries, many different frequencies (and voltages) had been used. Large investment in equipment at one frequency made standardization a slow process. However, as of the turn of the 21st century, places that now use the 50 Hz frequency tend to use 220-240 V, and those that now use 60 Hz tend to use 100-120 V. Both frequencies coexist today (Japan uses both) with no technical reason to prefer one over the other and no apparent desire for complete worldwide standardization. Unless specified by the manufacturer to operate onboth50and 60 Hz, appliances may not operate efficiently or even safely if used on anything other than the intended frequency. http://en.m.wikipedia.org/wiki/Utility_frequency

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#5

Re: frequency

02/17/2012 6:16 PM

The higher the frequency, the "cleaner" the power. We had some extreme precision equipment in the US Navy that needed 400hz power.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #5

Re: frequency

02/18/2012 11:20 AM

The Navy reason for high frequencies were smaller inductors, therefore lighter equipment.

Also DC supplies could interfere with radio and radar signals due to the commutator switching being of a quite high frequency on DC ships.....so all RN masthead lighting, even on older DC ships was AC.

I personally see no advantage in 50 Hz, to my mind 60 Hz would be slightly more efficient (100Hz would be even better!), but I prefer the 240 volts as 120VAC needs such huge amounts of copper to transfer the same power.....

It has been proved time and time again that the safety aspect of 120VAC is a pipe dream....so that is no reason to use it.

So my vote would be for 240VAC at 60Hz, but we are so far down the paths set over a 100 years ago in many areas with either 50 or 60 Hz, its too far to back up and start again.....sadly!

So to answer the question exactly, but only with reference to the frequency is that 60Hz is better....

I would guess that these low frequencies are more to do with the technical problems of the prime movers for over 100 years than anything else....today higher frequencies would be no problem.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#15
In reply to #5

Re: frequency

02/18/2012 11:27 AM

There are not much relation between frequency and clean power.

The main reason for different frequencies is that higher frequencies use smaller magnetic components that save on weight. Weight is a big problem in the aeronautical industry. Since the Navy share high technology communication equipment with the Air Force, they use the same power distribution. I suspect the Army and related industries also use 400Hz for communication equipment.

Higher frequencies increase the losses in the cables through skin effect and magnetic cores from eddy currents. We would not use 400Hz for power distribution across a country.

DC power is more likely the next standard. It will start at the main lines, then large industries, and eventually reach the residential distribution.

The frequency used is a trade off between power losses and size of the magnetic components (Transformers, motors...)

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6

Re: frequency

02/17/2012 7:30 PM

One of these two frequencies will be the frequency of your power distribution. Even in the very few countries that utilize both power grid frequencies, one cannot choose which one resides at your location. So there is no advantage because one cannot choose which one to use.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: frequency

02/17/2012 10:08 PM

The chief advantage of 400Hz power in aircraft is the compactness and light weight of the motors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8

Re: frequency

02/17/2012 10:30 PM

More is better....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Oct 2011
Posts: 29
Good Answers: 2
#9

Re: frequency

02/17/2012 10:55 PM

Slightly tangential, but then, does equipment designed for 50 Hz work at 60 Hz too, and at voltage being the same?

Register to Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#12
In reply to #9

Re: frequency

02/18/2012 5:46 AM

Not all 50hz equipment can run on 60hz

Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#16
In reply to #12

Re: frequency

02/18/2012 7:29 PM

For example?

__________________
Never trade luck for skill.
Register to Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#17
In reply to #16

Re: frequency

02/19/2012 2:28 AM

Example fluorescent lamp with ballast designed for 50hz will not ignite on 60hz supply

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#18
In reply to #16

Re: frequency

02/19/2012 4:57 AM

Motors run slower on 50 Hz than 60 Hz, ask anyone with a vinyl record player if that matters.....!

A motor's speed may be important for the application.

Some 60Hz motors can possibly overheat on 50Hz.....not all but some. The mechanical load often plays a role as well...

Many motors can be used on either frequency, provided the change is speed does not matter for the application. Look at the name plate on the motor for advice in this area....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Dec 2009
Location: Kota Kinabalu, Malaysia
Posts: 39
#19
In reply to #18

Re: frequency

02/19/2012 5:09 AM

Electric motor still can run on 50hz with same speed and torque, all you need is 380v 50hz

Register to Reply Score 1 for Off Topic
Anonymous Poster #1
#20
In reply to #19

Re: frequency

02/19/2012 5:31 AM

??????????

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#21
In reply to #20

Re: frequency

02/19/2012 8:01 AM

The volt/second ratio should be about the same to keep the magnetic circuits polarized with the same flux. For a given design lowering the frequency requires lowering the voltage proportionally.

This applies to most motors and transformers.

Some magnetic devices have enough margins to operate at both. But even if it seems to work, the reliability can suffer in the long run.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#22
In reply to #18

Re: frequency

02/19/2012 8:31 AM

Nicolai Tesla did do a brilliant job inventing the induction synchronous motor. For many good reasons the induction synchronous motor is the most common electric motor used today but it is not the only motor used directly connected to the AC grid frequency. If the motor is a universal motor where the stator and rotor windings are wired in series then with the same voltage and no mechanical load a 50 Hz driven motor will run very slightly faster than when it is run on 60 Hz.

Getting back to the OP question. There are some task specific advantages for one power frequency over another. However, with 60 being only 20% greater than 50 this difference is not a significant difference. The major difference between the grid standards is the nominal voltage each provides.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#10

Re: frequency

02/17/2012 11:44 PM

60 Hz is better than 50 Hz, because 360º is evenly divisible by 60, not by 50. Makes the math easier...

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#11

Re: frequency

02/18/2012 1:56 AM

When doing calculations it is easier to visualize time periods in milliseconds as parts of a wave cycle at 50Hz. eg One cycle = 20 msecs

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#13

Re: Frequency 50hz System by 60 hz System

02/18/2012 10:07 AM

Motors, generators, and transformers need less iron and are slightly smaller.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#23

Re: Frequency 50hz System by 60 hz System

02/19/2012 1:50 PM

It depends on the country, for me 50Hz is superior to 60Hz because more equipment will run on our 50Hz power grid down here.

__________________
jack of all trades
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#24

Re: Frequency 50hz System by 60 hz System

02/20/2012 3:23 AM

@marcot, with respect I doubt wether "DC power is more likely the next standard" , as:

  • for the same ampacity, savings on conductors size is minimal
  • for people safety, it is clear that we cannot accept to do less than what exists.
  • people protection at high DC levels (ie 200V and above) would need protection and switching devices much more costy than what can be produced today.

So I think that DC will stay in some specific uses (ie railway, Data centers) but would be extremely slow to come (if ever) in buildings / residential.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#25
In reply to #24

Re: Frequency 50hz System by 60 hz System

02/20/2012 7:51 AM

Although in general I agree with you that I also cannot see us leaving AC for DC, especially since over the last 30 years or so we have such wonderful electronic components to help with motor speed control etc..

The reasons you cite though are mostly invalid. As has been shown time and time again and here on CR4 as well, DC IS SAFER THAN AC for the same effective voltage.

DC tends to throw people off, whereas AC puts muscles in a spasm and they cannot move.....

Please research your comments yourself here on CR4 as this subject continually arises with a new person or two with NO DC experience or practical knowledge, even some good engineers actually believe it!

Last but not least there are even textbooks around with the same wrong information.

Talk to someone that has worked on DC year in year out and has "tested" the voltage inadvertently HIMSELF, not secondhand from reading or listening to a professor in the Uni (they know nothing!!)....

I have to admit that there is plenty of wrong information around that misleads many, you are certainly NOT alone here.

By the way, I have worked on DC and AC ships in the RN, I have actually done fault finding on ground faults on DC 220V using two fingers on the same hand across the fuse positions (I can give you full details if the method is new to you, it is VERY simple). I would NEVER do that even on 120VAC let alone 240VAC....NEVER EVER!!! Too dangerous.

I have also had a few accidental AC shocks over the years of 120, 240, 380 and 440 volts (all three phases on one arm!), all were painful and pretty damn dangerous at the same time...... Your brain simply stops......sometimes maybe forever.... I was always lucky.....I think!! DUUUUHHHHH.......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#26

Re: Frequency 50hz System by 60 hz System

02/20/2012 7:54 AM

DC won't become the next standard but DC is cropping up in transmission systems. Long distance high voltage DC transmission has become desirable with the development of efficient solid state inverters. No capacitive and inductive losses with DC.

There are applications for both. I like the idea of all 400Hz but that would make series wound motors a tad lethargic. Think of the range on your VFDs and how compact transformers and synch/inductive motors would be. Aircraft and military went for better tech rather than shore compatibility. Its nice to see positive attributes exploited in favor of legacy thinking.

Didn't Tesla do his really long range conductorless electricity transmission at 8Hz utilizing the Earths resonant electrical frequency or something like that?

Maybe we should all switch to 8Hz....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#27

Re: Frequency 50hz System by 60 hz System

02/21/2012 9:15 PM

This entire thread subject is second only to the "Why multiples of 11..." subject as the most often asked and most annoying questions posed in this forum. If the posters of these questions would just use the Search function over to the right before launching this kind of thread, I would be less judgemental. But it never seems to happen.

Soooooo boring...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#28
In reply to #27

Re: Frequency 50hz System by 60 hz System

02/21/2012 9:49 PM

How many of the posts did you have to read to determine the thread was "Soooooo boring"???

Register to Reply Off Topic (Score 6)
Register to Reply 28 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Anonymous Poster (1); beentheredonethat (1); cwarner7_11 (2); jack of all trades (1); JRaef (2); lyn (1); madhavdivya (1); marcot (2); obouill (1); redfred (2); Rixter (1); SolarEagle (1); Tornado (1); visaseller (5); Wal (1); wangito (1); WJMFIRE (1)