Installing a Ball Valve Downstream from a Safety Valve

05/08/2007 2:35 AM

Hello friends...

I've heard that it's not appropriate to install a ball valve at the downstream of a pressure safety valve. Is that right? and if it is, why?

regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: A Ball Valve at the Downstream of a Safety Valve!!

05/08/2007 7:49 AM

A formal HazOp [Hazard and Operability] Study, a technique now widespread within the process industries, would throw out the posted suggestion on safety grounds.

The purpose of a pressure safety valve [PSV] is to vent overpressure in the vessel or pipeline it is intended to protect. Installing a ball valve, being an on/off device, downstream of the PSV in the vent line is therefore inappropriate at least, and potentially dangerous in the extreme, unless other protective devices, like bursting discs for example, are present in the plant item requiring overpressure protection.

Rhetorically, why would one want to do what is suggested in this post? If a ball valve is required in the line in question, then it would be better to put the pressure safety valve on a different branch with its own uninterrupted vent line so that both valves can carry out their intended function without the one interacting with the other.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2007
Posts: 35
#2
In reply to #1

Re: A Ball Valve at the Downstream of a Safety Valve!!

05/08/2007 8:06 AM

This is what I was talking about...

check out this piece of PID, they say that ball valve shouldn't be there.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: A Ball Valve at the Downstream of a Safety Valve!!

05/08/2007 10:16 AM

'They' might be right. Note that the valves upstream of the PSV are labelled, LO, standing for "locked open". Now, the original posted question makes no mention of an LO criterion for the valve downstream of the PSV! It might be OK for the downstream valve to remain if it too is LO except for maintenance purposes, and the lettering on the posted image is difficult to determine, so the remaining question is really quite simple: what does the HazOp Study report say about the valve downstream of the PSV (rhetorical questions)? Does it call for the valve in question to be 'locked open'? Are the keys for the lock under tight control?

It's time to check!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Apr 2007
Location: Newport Beach, California
Posts: 49
#4

Re: Installing a Ball Valve Downstream from a Safety Valve

05/08/2007 1:11 PM

A valve of any kind (locked open or not) is a complete mistake. Any competent insurance company inspector would immediately demand that it be removed. Any competent professional engineer would refuse to approve such an installation.

Any inexperienced operator could inadvertently unlock that valve and close it.

__________________
Milton Beychok
Register to Reply
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#5

Re: Installing a Ball Valve Downstream from a Safety Valve

05/08/2007 11:33 PM

Very true because the potential hazards and there is no reason to do it

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Register to Reply
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#6

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 12:26 AM

The use of valves to isolate a PSV IS a standard. In order to do PMs on PSVs they need to be ISOLATED. The valves DO need to be CAR SEALED OPEN and documented on a CAR SEAL LOG. This is part of being a PSM facility.

PSM = Process Safety Management.

And YES the insurance company's like to do business with company's that have PSM facility's. In order to have a PSM facility, the management has to prove that they have procedures in-place to control and manage the facility.

Register to Reply
Commentator
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2007
Location: CookInlet AK
Posts: 67
Good Answers: 2
#7
In reply to #6

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 12:46 AM

On your P&ID it shows two FB LO valves upstream of the PSV. They are Full Bore Locked Open valves. also the ball valve in question is also labeled FBLO.

Further down on the P&ID it shows a PSZ-012B flowing into the same header.

It appears the there may be TWO PSVs on the same loop, allowing one to be taken out of service at a time for PM work. Also the PSV are also acting as an ESD depressurising valve. by isolating each valve, the function of the ESD coil and PSV can be tested without taking the plant down and costing $$$$!

Not only is it common, but it makes Good Sense to use a Ball Valve both up and down stream of a PSV.

Register to Reply
Anonymous Poster
#8
In reply to #6

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 12:52 AM

To add some points on the installation arrangement of PSVs:

(1) When you have PSV (one or more) connected to a common flare header i.e. closed discharge system,the valves downstream of PSVs can not be avoided. If a PSV is discharging directly to atmoshere (at safe location) then there will be no valve on the discharge.

(2) Normally a Gate valve of pipe size (if PSV outlet size is smaller than pipe size) is preferred compared to Ball valve. The reason is that due to sudden discharge from PSV, there could be an incident of ball valve seals may get blown off. The Gate valve stem is pointing downwards or inclined below horizontal so as to avoid blocking the valve in case the gate and stem connection comes off in service.

(3) In order to avoid the human error of not keeping the inlet/discharge valve fully open, the valves could be LO with car seal arrangemnt as explained in the earlier response. In case of very critical application one can have interlocking key system (this is for more than one PSV in parallel) -- this will ensure that atleast one set of valve -- inlet and outlet will always be in open position.

Hope this answers the query.

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#9

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 2:35 AM

The LO valve may be required for repair purposes without closing down the rest of the system which may even be more harmful.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 3:47 AM

Quite.

It all depends on the HazOp Study report. It's still time to check...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#11

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 6:36 AM

"it's not appropriate to install a ball valve at the downstream"

No. You can install .......................

You can install the appropriate valve at either upstream and/or downstream, depend on your need for that valve.

Suppose you have a flare header connected to all downstreams of all safety valve at certain plant, and suppose that such a repair or maintenance is required to the equipment in which that safety is connected. To do that maintenance you have to shutdown the equipment which protected by that valve and then close the downstream valve as an isolating valve. At that moment you can made any repair or maintenance including the inspection & repair for safety valve itself, and that avoiding shutdown of whole plant.

Only you have to lock the valves and only allow the authorized persons to have the key to ovoid off the valve while working.

Also the valves shall have a mark showing if it is on or off.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Anonymous Poster
#12

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 9:36 AM

If you feel the need for a Ball Valve, remove the Relief, or Safety valve.

The two should not co-exist on the same line.

Register to Reply
Associate

Join Date: Feb 2007
Posts: 43
#13

Re: Installing a Ball Valve Downstream from a Safety Valve

05/09/2007 8:02 PM

You need to consider the governing "standards" (if any) for the process that the underwriters would expect to be adhered to. API, ASME, ISO? They will spell out what is permissible.

The most common and accepted method for preventing process downtime due to a faulty SRV is to have a Y-pattern switching valve upstream of two SRV's. They must provide a constant flow area while switching.

Isolation valves are sometimes permitted but only if there are additional redundant failsafe devices. Rupture discs installed upstream of the SRV as an example. The disc is set at the MAWP and the SRV somewhat below. In this scenario the disc is the primary "code" safety device and the SRV is the secondary, used only to prevent the disc from bursting during transients. But again, the standards will dictate what is permissible.

Register to Reply
Participant

Join Date: Jan 2026
Posts: 1
#14

Re: Installing a Ball Valve Downstream from a Safety Valve

01/26/2026 6:01 AM

You’re right - it’s generally not recommended to install ball valves directly downstream of a pressure safety valve. The reason is that a safety valve is meant to open fully to relieve pressure instantly. If a ball valve is closed or partly closed downstream, it can create backpressure or restrict flow, which can interfere with the safety valve’s operation and even damage the system.

Basically, safety valves work best with a clear, unrestricted path downstream - any isolation valves should be positioned where they don’t compromise that.

Register to Reply