Pressure Boosting Problems

04/03/2012 1:37 AM

I will try and be thorough in my explanation of the project I have undertaken in hopes that someone may offer their professional diagnosis.

I am a plumbing contractor with a contract to replace a triplex booster pump in a 10-story prison. The booster pump sits on the ground floor and pumps water through a 6" copper line, up to the fourth floor. On the 4th floor, the piping reduces to 5" and loops around the perimeter of the facility. There are multiple 3" branch lines that extend vertically from the 4th floor loop and rise up 5 additional stories of approx. 20' in hieght each. These stacks provide water to approx. 9 prison cells fitted with flush valves and lavatories. There are a total of 40 of these 3" risers/stacks going up. There are no pressure reducing valves installed on the system piping.

The previously installed pump consisted of three 40hp pumps, running two at a time, with a set pressure of approx. 150psi. Historically, there was a ludicrous amount of pipe movement, hammering and pipe failures, seemed to have been caused by oversized pumps.

The pumps we installed consist of three 15hp pumps, rated at 200gpm each, running on a VFD.

Here is the problem: With the new pumps running, I have noticed huge pressure drops, causes the back-up pump to short cycle, thereby increasing the pressure. Pumps were set to 145psi by the manufacturer.

Is there siply a problem with the pumps not being able to sustain pressure because of the frequent use of flush valves, or could there be an underlying pipe sizing issue, that brings high velocities into the equation, etc.

Let me know if you need any additional information. I normally don't post to forus, but my heads spinning around on this one.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#1

Re: Pressure Boosting problems

04/03/2012 2:36 AM

re-size the pumps. a good pump manufactorer will get you in the ball park. you'll need to know rise, needed volumes and needed pressures at each pump stage.

Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#7
In reply to #1

Re: Pressure Boosting problems

04/03/2012 3:26 AM

All of this was provided when the pump designer manuf. the skid. Pumps are:

600gpm

187TDH

What I am wondering is whether or not the demand was miscalculated or if there is a problem with pipe sizing upstream, that causes too much of a pressure drop for the pumps to handle. As I stated, there are over 600 prison cells being fed off of a 5" pipe.

I ran some numbers using Hunters Curve and calculated a potential demand of over 700gpm. But my underdstanding is that Hunters Curve is meant for more intermittent use, than we have seen in a correctional setting.

Register to Reply
Guru

Join Date: Nov 2007
Posts: 519
Good Answers: 11
#13
In reply to #7

Re: Pressure Boosting problems

04/04/2012 8:21 AM

Maybe I didn't catch all the details, and at the risk of sounding like an idiot, I'm going to say this anyway.

You said you have 10 stories and each story is 20 feet in height right? That's 200' of liquid head that you have to overcome (I guess maybe 180-190 since you don't pump to the top of the last floor). Without knowing the suction pressure of the pump, it sounds like you're probably undersized.

Register to Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#15
In reply to #13

Re: Pressure Boosting problems

04/04/2012 5:18 PM

I had read the initial description differently. From the 4th floor there are risers to service the higher floors. These risers are 20' high each.

[At least that's how I saw it.]

__________________
Just an Engineer from the land down under.
Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#17
In reply to #15

Re: Pressure Boosting problems

04/04/2012 8:40 PM

Sorry for the con fusion. The actual height of each floor is approx. twenty feet, so the risers are about 100 feet high each

Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#16
In reply to #13

Re: Pressure Boosting problems

04/04/2012 8:39 PM

You are correct on the total developed head. Overall it's 187 feet from base to top outlet.

The suction pressure at the pump is city pressure at approx. 60psi.

Register to Reply
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#2

Re: Pressure Boosting problems

04/03/2012 2:55 AM

Hi & welcome to CR4 (noticed the Post#1). Hope you can find assistance here.

If the problem is water hammer, there are ways to manage it.

My understanding of water hammer is that it is the change in momentum of the water. ie the moving water suddenly stops, or the stopped water suddenly starts. In either case, the sudden change in energy, is dissipated in the pipework as water hammer, either as pipework movement or a pressure wave bouncing up and down the line. Both effects are very serious and can cause real damage (pressure spike can cause line failures even).

In my experience the key to this is managing the change in momentum of the water.

Firstly the velocity of the water has big impact. If the velocity is greater than 2.5 m/sec, water hammer problems will be likely. At flows less than this much less of a problem. Can you checkthe velocity of water in each section of the network?

Secondly the start stop speeds ofthe water is also critical.

The opening and closing speeds of isolations valves should be checked, depending on the velocity and the diameter will determine the opening and closing speed. slow down the speed to smooth out the change.

The ramp up and shutdown speeds ofthe pumps should be checked. DOL pumps are notorious for this. Consider using soft starters or VSD to control both the ramp up and shutdown of the pumps. I use a soft starter for pumps of 15kW or greater is to manage this problem, or even a VFD/VSD if it is justified by the control uses of the pump. For VSD's ramp up over 20-30 seconds, ramp down over no less than 15 seconds.

So recommend the following to track down the source of the problem;

- Checking the velocity in each section of your network.

- Check the opening and closing speeds of valves

- Check the ramp up and shutdown speeds of pumps.

Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#5
In reply to #2

Re: Pressure Boosting problems

04/03/2012 3:15 AM

Thanks you for your response. My understanding of water hammer is the same. What I a wondering is how velocity plays a role in hammer. I intend to try and measure the velocity of the water and have found a formula that should work:

v = 0.4085 q / d2 (1)

where

v = velocity (ft/s)

q = volume flow (US gal. /min)

d = pipe inside diameter (inches)

The only thing I'm not sure of regarding the above calculation is....which pipe diameter do I use. If the main piping is 3" and I measure flow from a 3/4" outlet off the main, do I use the pipe diameter of 3" or 3/4"?????

As far as opening and closing speed of valves, the only fast acting valves are the diaphragms on the flush valves. These types of valves are not rated to open based on time, but rather on consumption, for instance, a flush valve will open until it has reached 1.6 gallons.

The ramp up and down speeds are controlled through the VFD, but being that the building has such a large quantity of high demand fixtures, with sporadic use, I think that by the time the transducer senses the pressure drop, the pump system is already being told to hurry up and boost the pressure, but since this pressure drop is related to a rapid closing flush valve, the pump boosts too late, and overpressurizes the system.

I hope i'm not confusing.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#14
In reply to #5

Re: Pressure Boosting problems

04/04/2012 8:46 AM

The only thing I'm not sure of regarding the above calculation is....which pipe diameter do I use..... 3" or 3/4"?????

I'm not sure about the formulae used to calculate but sure about which pipe diameter. Use the ID of the pipe size where want to know the velocity. If you want to know what is the velocity in 3" pipe, use ID of 3" pipe (from which pipe you are measuring the flow is immaterial). Do not forget to use correct units.

Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#18
In reply to #14

Re: Pressure Boosting problems

04/04/2012 8:41 PM

Thank you for the clarification. This should allow e to pull a reading from anywhere along a horizontal run and determine the velocity.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #2

Re: Pressure Boosting problems

04/03/2012 3:33 AM

A soft-starter will do nothing for the step-change in pressure and flow when the pump starts. All a soft-start does is soften the impact on the local electrical system of the pump starting.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#3

Re: Pressure Boosting problems

04/03/2012 3:04 AM

Sorry for second post, just read in alittle more detail.

So the water hammer was with the original 3 x 40 hp pumps (2 x duty, 1 x standby), and now you have replaced with 3 x 15 hp pumps (assuming all are running).

Even with 3 of the new pumps running, you have replaced 2 x 40 hp = 80 hp, with 3 x 15 hp = 45 hp (almost half as much energy - is this correct?).

You mentioned the new pumps are on VSD, what pump speed are they running at when they trip? Or is it just one pump in VSD and 2 x DOL (that come in and out based on pressure setpoints)?

Before the pumps trip are they making the required pressure? Then does the pressure drop rapidly when one of the pumps drops out ? If so consider a Soft Starter to ramp up and shutdown the pump in a smoother way.

Or are the pump stuggling to make the pressure?

Sorry more questions than answers?

Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#6
In reply to #3

Re: Pressure Boosting problems

04/03/2012 3:21 AM

Actually, when we started the new triplex system...one single 15hp pump sustained the building pressure at 145psi. This pump was running at a full 60hz and pulling about 20amps. Then, as needed, a second pump would start....run for a little while and full 60hz and then time out. What we noticed though, was that the pressure wold not stay consistent. The pressure would go up to 145psi, then drop to 120psi, a second pump would kick on and spike the pressure up to 160psi and then the second pup would drop off.

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#4

Re: Pressure Boosting problems

04/03/2012 3:11 AM

Do/did you have air release valves at the high points?

Your cause might be a case of organized "crime" by inmates organizing to flush toilets at the same time and thereby causing an overload that possibly resulted in privileges or diversions.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#8
In reply to #4

Re: Pressure Boosting problems

04/03/2012 3:29 AM

LOL. Inmates actually organize flushing at the same time as a means of passing contraband through the sewer system. And they flush and flush and flush, until the cell or cells below them can retrieve the goods fro the sewer pipe.

As far as air relief valves on the high points....we have not installed any, but have been discussing this option with the facility.

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#10
In reply to #8

Re: Pressure Boosting problems

04/03/2012 4:47 AM

That is illegal water use. Rather introduce a courier service and save water.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#11

Re: Pressure Boosting Problems

04/03/2012 5:51 PM

Welcome to the forum.

Do you have any pressure accumulator vessels in the system? (Normally near the pumps)

These may help your issue with the standby pump. Our water reticulation system uses this principal in many locations, even with VSD.

__________________
Just an Engineer from the land down under.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#12

Re: Pressure Boosting Problems

04/04/2012 3:14 AM

Is this not a triggered resonance problem? I like the idea of 10 gallon diaphragm-style water well accumulators, maybe at the ends of the lines, plumbed big. They'd be capacitors in an electrical power supply. Those toilet valves are not soft stop.

__________________
Align culture with nature...
Register to Reply
Member

Join Date: Apr 2012
Posts: 9
#19
In reply to #12

Re: Pressure Boosting Problems

04/04/2012 8:44 PM

I searched the entire piping network and found no pressure accumulation vessel. In the U.S. we call these expansion tanks or hydropnuematic tanks (for wells). I think one of these will definitely help compensate the surges in pressure and stabalize the system.

Still have the issue regarding the low system shut-down.

Register to Reply
Register to Reply 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ajwinemaker (2); CEMINC (8); cingold (1); durtieduck (1); Hendrik (2); Just an Engineer (2); ormondotvos (1); pritam (1); PWSlack (1)

Previous in Forum: Thermal Power Plant-Doubt   Next in Forum: Electrical Equipment Heat Load Calculation

Advertisement