I will try and be thorough in my explanation of the project I have undertaken in hopes that someone may offer their professional diagnosis.
I am a plumbing contractor with a contract to replace a triplex booster pump in a 10-story prison. The booster pump sits on the ground floor and pumps water through a 6" copper line, up to the fourth floor. On the 4th floor, the piping reduces to 5" and loops around the perimeter of the facility. There are multiple 3" branch lines that extend vertically from the 4th floor loop and rise up 5 additional stories of approx. 20' in hieght each. These stacks provide water to approx. 9 prison cells fitted with flush valves and lavatories. There are a total of 40 of these 3" risers/stacks going up. There are no pressure reducing valves installed on the system piping.
The previously installed pump consisted of three 40hp pumps, running two at a time, with a set pressure of approx. 150psi. Historically, there was a ludicrous amount of pipe movement, hammering and pipe failures, seemed to have been caused by oversized pumps.
The pumps we installed consist of three 15hp pumps, rated at 200gpm each, running on a VFD.
Here is the problem: With the new pumps running, I have noticed huge pressure drops, causes the back-up pump to short cycle, thereby increasing the pressure. Pumps were set to 145psi by the manufacturer.
Is there siply a problem with the pumps not being able to sustain pressure because of the frequent use of flush valves, or could there be an underlying pipe sizing issue, that brings high velocities into the equation, etc.
Let me know if you need any additional information. I normally don't post to forus, but my heads spinning around on this one.