Vide Clause 7.2.1.2 of IEC 60947-4-1, the drop-off voltage of electro-magnetic contactors with AC Coils is 75% to 20% and for DC Coils is 75% to 10%. I would like to know why there is this extra 10% flexibility for DC coils?
DC coils in contactors can be (a) economy resistor type, (b) double-coil type or (c) fully, continuously rated for the control voltage. The last one is the most reliable type (no late-break NC with its own problems), so much so that many industries like steel plants mandate the use of only such DC coils.
Now coming to your question, it is somewhat easier to achieve a 20% or even 40% drop-off in (a) and (b) types. Not so easy in (c). Bearing in mind that the coil must pick up cleanly at ≈80% when hot ! Quite a challenging design problem, since the coil can reach 100°C easily.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
i am getting more convinced that this is really the reason.
An extract from the Tesys catalogue of Schneider/Telemecanique shows that the dropoff voltage window starts at 10% for the continuous-rated magnet (image below) of the first two frames, and is 15% for the double coil. (The pickup and sealed consumption values also show the nature of the magnet system)
Is it anything to do with alternating current crossing through zero at twice the supply frequency and the magnetic field reversing at twice the supply frequency? - Full-wave-rectified, unsmoothed DC hits zero at twice the incoming AC frequency too, though the magnetic field doesn't actually reverse.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
I'd say you're right, in the case of AC contactors, at 20% of the voltage, you don't have 100% duty cycle but a couple zero crossings every 16 mSecs. that, for me opens a couple of weakened flux windows, which will lead to the release of the laminated core due to the pulling action of the spring.
Regards
__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
The hysteresis in the magnetic iron core of the electromagnet can prevent drop off a little longer with a DC field because the core may still be slightly magnetic when current is released. Remember, this specification identifies the range that drop off is acceptable for a contactor. This is not a designer's specification but an operations specification.
__________________
"Don't disturb my circles." translation of Archimedes last words
Redfred has the answer. The core of a contactor is soft iron and should not retain any magnetism , however it does and this will be the reason why dc coils will hold on longer as this is always of the same polarity and not reversed by the ac, as mentioned by others.
If you need a contactor to release at a higher voltage you need to add a non magnetic pole piece between the armature and the core nose. A piece of paper will work as a one off solution. This will also make it release quicker.
regards
capblanc
__________________
En la casa del herrero, cuchillos de palo!
Be careful with modifying the magnetic circuit on an AC contactor. Doing so significantly lowers the inductive reactance and therefore increases the current consumption which can result in over heating of the coil.
__________________
The hardest thing to overcome, is not knowing that you don't know.