Perplex With My 3512B Catipilar Diesel Generator

06/09/2012 2:24 PM

I got a 1000KW, 1605 amps diesel generator that have an issue with come up to speed and maintain desire frequency. When I start it up with all alignment in place, it would come up to 57 HZ and roughly 1534 rpm. If try to raise on the governor, it wouldn't go farther, but the frequency would go down slowly. Anyone has experiences this before, and what did you have to do to fix the problem?

Register to Reply
Pathfinder Tags: Catipilar diesel generator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Perplex with my 3512B Catipilar Diesel Generator

06/09/2012 2:59 PM

Try dropping the RPM....Do you know the recommended speed, you might check that....Probably 1500

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2012
Posts: 4
#4
In reply to #1

Re: Perplex with my 3512B Catipilar Diesel Generator

06/09/2012 6:08 PM

Thanks for the reply Solar. When dropping the speed, the frequency go up, but it wouldn't go past 57HZ.

Register to Reply
Commentator

Join Date: Apr 2009
Posts: 94
Good Answers: 3
#12
In reply to #4

Re: Perplex with my 3512B Catipilar Diesel Generator

06/11/2012 8:41 AM

Speed and frequency are the same thing. The hz should go up and down along with the RPM. What kind of governor does it have? EG3P, EG10P or 3161

__________________
"Never mistake intelligence for wisdom"
Register to Reply
Associate

Join Date: Jul 2011
Posts: 29
Good Answers: 2
#2

Re: Perplex with my 3512B Catipilar Diesel Generator

06/09/2012 4:00 PM

Is your generator a 60Hz? if so I may assume it is 1800 rpm speed.. check your governer and see in what mode it is running, is it running in isochronous, droop or based on output power? state do you run your generator as a standalone or in parallel with other generators? I would say check out your governor setpoint settings and see in what mode it is running first.. if everything is set the way it is suppose to be, then you may need to bring the vendor or someone to fix it for you..
Did you see if the output voltage is ok as well?
Good luck..

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2012
Posts: 4
#3
In reply to #2

Re: Perplex with my 3512B Catipilar Diesel Generator

06/09/2012 6:06 PM

Thanks for the reply B. The generator is 60HZ and its running speed is 1800 rpm. We had the generator in isochronous and it was running alone; just your normal start up. The output voltage was 450 as require. When you say, check the set point, do you have anything that would show how to go about it?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #3

Re: Perplex with my 3512B Catipilar Diesel Generator

06/09/2012 7:45 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2012
Posts: 4
#6
In reply to #5

Re: Perplex with my 3512B Catipilar Diesel Generator

06/09/2012 11:25 PM

Thanks for the files Solar. I'm currently task with a different issue that take precedence over this thing. Appreciates for the post.

Register to Reply
Participant

Join Date: Jun 2012
Posts: 1
#7

Re: Perplex With My 3512B Catipilar Diesel Generator

06/10/2012 3:29 AM

Try dropping the RPM....Do you know the recommended speed, you might check that....Probably 1500

shredguitarschool

Register to Reply
Member

Join Date: Feb 2012
Location: Trinidad & Tobago
Posts: 7
Good Answers: 1
#8
In reply to #7

Re: Perplex With My 3512B Catipilar Diesel Generator

06/10/2012 7:29 AM

Was there any work done on the engine governor? If the spline shaft was not set properly, the governor may go full travel and not move the throttle to the right position. This needs to be verified as it may have been interfered with before your intervention.

Register to Reply
2
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9

Re: Perplex With My 3512B Catipilar Diesel Generator

06/10/2012 9:01 AM

Blocked fuel filter?

Bad fuel pump?

Bad fuel?

Water in fuel/water catch filter?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10

Re: Perplex With My 3512B Catipilar Diesel Generator

06/11/2012 2:01 AM

Andy's GA makes sense; also, it might be that the generator is overloaded.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Perplex With My 3512B Catipilar Diesel Generator

06/11/2012 3:34 AM

One of the solutions to this problem may be found by making a telephone call to the original equipment manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Bibo92004 (1); Catmandu (1); LonnaCreighton (1); Mav (3); PWSlack (1); SolarEagle (2); Tornado (1); Trini (1)

Previous in Forum: Stablizer Out of Service   Next in Forum: DC Crane Coils

Advertisement