Fuel Consumption Per Load in Kw or Kva

07/14/2012 1:52 PM

Hi,

I would like to know how to calculate the fuel consumption of diesel using the data provided by manufacturer. The units are US Gal/ph, L/ph, BHP, & Kwm let say at 1500rpm carrying load 100% the Kwm=448, BHP=600, L/ph=107, & US Gal/ph=28.4 , it consumed how many liter per hour? Because I want to compare the difference in using single unit 800KVA generator versus 2 units 400KVA generator (synchronized). I believed its economical to use small capacity generator and its more flexible compared to single unit. The load is not steady so I think small capacity generator is the best option.

I want to make comprehensive comparison table to see the saving.

Thank you

dar76

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Fuel Consumption per load in Kw or Kva

07/14/2012 3:06 PM

Use "the data provided by the manufacturer", "to make comprehensive comparison table to see the saving".

What's the problem?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Fuel Consumption per load in Kw or Kva

07/14/2012 3:46 PM

First, one cannot do a theoretical calculation of fuel consumed to electric power because there are too many energy transfers happening simultaneously (chemical to thermal, thermal to mechanical, mechanical to electrical). Additionally there will be the complication of the random, variable electric load changes that will happen through out the day. So using the manufacturers numbers will be your best bet.

Having said that... I would expect that at close to maximum load, one larger diesel generator will be more efficient than two half the size smaller diesel generators. However, a large generator operating at just under half of its capacity will be less efficient than one half the size generator operating at most of its capacity. On the other hand operating any system at close to full load will likely produce early failures.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#3

Re: Fuel Consumption Per Load in Kw or Kva

07/14/2012 11:49 PM

Most manufacturers will provide charts of fuel consumption versus load- generally not linear. These only provide approximations, but are reasonably close to actual measured values in the installations where I have done this.

The issue is that the load is never going to be constant. Trying to use an "average" load to calculate this can be misleading, since the relationship between load and fuel consumption is not going to be linear (except over a small range of values). Power factor can also play a role, as can any load imbalance.

The quickest way to conduct the investigation of two 400 kW vs one 8 KW generators is to compare the manufacturer-provided curves for the candidate plants.

The most exacting way to determine the actual fuel consumption is to measure the fuel consumed over a period of time (not the fuel flowing to the generator- some of that goes back to the tank. You have to measure how much fuel has been sucked from the tank over the given period).

From the specifications you cited, I would say that "L/ph=107" is most likely Chinese or Korean for "Liters per hour", but you do not mention the make of generator you are using...Sounds about right from an energy standpoint.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Fuel Consumption Per Load in Kw or Kva

07/15/2012 5:59 AM

Dear dar76,

The fuel consumption will NOT HAVE LINEAR RELATION WITH LOAD. The best performance is achieved at Loads more than 80% to 85% of RATED or FULL LOAD.

You have not indicated the load pattern. If the load will not come below 60% of Rated Load. then use single generator set. If the load drops below 50%, for example 30%, it is advisable to have 2 sets and at lower loads, isolate the 2nd set. This also depends upon how often the load comes down or goes up.

Manufacturers Consumption data is valid only the set is loaded to certain minimum level and when there is NO-LOAD, the DG Set will run in idle and fuel will be consumed perhaps 8 to 10% of fuel at Full Load, which is a waste.

THANKS,

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 20
#5
In reply to #4

Re: Fuel Consumption Per Load in Kw or Kva

07/15/2012 6:29 AM

Dear dhavanandhan,

I had gathered data from our existing factory , DG set -1 = 912Kwh at 4.54hr operation and DG set - 2 = 768Kwh at 4.54hr operation. The calculated load for this factory is 672kw at 70% load, but in real situation as we can see from the data its only 370kw in total. But the load will rise up to 580Kw in few seconds. Now in new factory they want to use single generator with the same load pattern, because the new factory will be same as the existing one, here we use synchronized 2 units 400KVA.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Fuel Consumption Per Load in Kw or Kva

10/15/2024 7:38 AM

A dipstick and a clock is one method.

Intervals between quantities supplied is another.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856