Backup Time of UPS

07/24/2012 10:19 AM

Suppose I have two units of 10 kW single phase UPS with backup time of 30 minutes that supply two different loads:

- 5 kVA load with pf 0.8

- 5 kW load with pf 1

Which load will drain the ups faster?

Register to Reply
Pathfinder Tags: UPS Backup Time
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Backup Time of UPS

07/24/2012 11:18 AM

Switch off the mains and measure it.

What do the original commissioning records say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Backup Time of UPS

07/24/2012 11:37 AM

Er, wouldn't it depend upon the condition and state-of-charge of the batteries at the moment of mains disconnect? Are these batteries new or what?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Backup Time of UPS

07/24/2012 11:46 AM

And, are you powering both circuits at the same time?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Backup Time of UPS

07/24/2012 11:57 AM

...and is this 30min backup time governed by a pre-programmed timer within the UPS?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Backup Time of UPS

07/24/2012 12:23 PM

The second.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#6

Re: Backup Time of UPS

07/24/2012 5:39 PM

First up, If the 30min is due to software settings in the UPSs, they will both go offline at 30 mins.

Your first load is 5kVA X 0.8 = 4kW

Your second load is 5kVA X 1 = 5kW

Now that the values are the same, you should be able to work out which will drain first.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#7
In reply to #6

Re: Backup Time of UPS

07/24/2012 11:02 PM

With voltage level of 220V

The second load will draw 5kW real power (I=22.72A)

The first load will draw 4kW real power (I=18.18A) + 3kVAr reactive load (I=13.63A) with the same magnitude of 22.72A.

My question is: does the 13.63 A of reactive load give different result compare to 4.54 A difference of the real power?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Backup Time of UPS

07/25/2012 6:32 AM

Well, it does rather depend on the resistance of the downstream cable:

  • Are all the connections tight?
  • Is it correctly sized?

Has the experiment been carried out yet?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#9
In reply to #8

Re: Backup Time of UPS

07/25/2012 12:01 PM

Thank you all for the comments, but maybe I have to rephrase my question.

The rating of the UPS is 10kW/12.5kVA 30 minutes of backup time, that is equal to 6.25 kVAh.

Can I say that, with 5 kVA load, regardless of the pf, the backup time should be 1 hour and 15 minutes?

Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#10

Re: Backup Time of UPS

07/25/2012 12:57 PM

I think this paper should clear up any confusion.

__________________
Think big. Drive small.
Register to Reply