Octal Base Relay

07/25/2012 11:46 PM

I have a NO 120vac signal wire. When the wire is energized it closes a contactor that turns on a 150hp irrigation pump.

I need to use this same signal wire to control a 120vac butterfly valve.

When the signal wire is energized, it needs to open the valve. When the signal wire opens, I need to reverse the polarity to close the butteryfly valve.

Please help, I'm trying to learn. I'm not an electrician, but know my way around pretty good.

Register to Reply
Pathfinder Tags: octal base relay
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Octal base relay

07/25/2012 11:59 PM

What's the problem?

Let the, "NO 120vac signal wire" control a second contact that controls the valve.

Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#2
In reply to #1

Re: Octal base relay

07/26/2012 12:08 AM

The butteryfly valve actuator needs power to open and to close.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Octal base relay

07/26/2012 12:12 AM

Get a self closing valve.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Octal base relay

07/26/2012 1:08 AM

If using a wire off an NO (normally open) contact to open the valve,
then use a wire of the corresponding NC (normally closed) contact to close the valve.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: Octal base relay

07/26/2012 7:44 AM

With out full knowledge of all the devices it maybe little more complicated. Assuming you want automate something. As it is you are there and are able to shut it down if something fails. If automated you will not be. Some fail safes need to be incorporated in the change to protect the devices.

Are you manually opening the valve now. Or are you pushing a button to open and close it. What lets you know it's full open or closed? Is the motor holding the valve in position with electrical power or does the power cut out when open or closed? Reversing the motor will require two set of contactor.

If the pump tries to start up against a closed valve it may stall. So you may need a timer to give the valve time to open before the pump starts.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#6
In reply to #5

Re: Octal base relay

07/26/2012 8:18 AM

Thanks for everything so far. A self closing valve is not cost effective, this is a 8" valve.

Fail safes have been considered. Basically I need a pressure sensor. So if psi exceeds a set amount, it will shutdown the pump. A timer should not be needed. The well has to pump from 300' deep, and then over 1000' to get to the valves location. The valve will have plenty of time to open.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #6

Re: Octal base relay

07/26/2012 8:57 AM

Where did the pressure sensor spring from?

Sort out the full spec of what you want then come and ask questions.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#13
In reply to #6

Re: Octal base relay

07/26/2012 5:25 PM

So the scheme you are working with is:

This pressure sensor is to directly interrupt the 120VAC.

Pressure is low, switch completes circuit, valve opens, state of relay changes (energize pump)

Pressure is high, switch opens circuit, valve closes, state of relay changes (de-energize pump)

The 120VAC circuit components are the pressure sensor, the valve, the relay, the wire, and the source. That's all.

Yeah, no.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#15
In reply to #6

Re: Octal base relay

07/26/2012 5:55 PM

Normally, water piping does not empty between cycles. Water is considered incompressible. So as soon at the pump starts, the pressure against a closed valve will become very high, even if that valve is 1300 feet away.

__________________
Think big. Drive small.
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#8

Re: Octal Base Relay

07/26/2012 10:31 AM

I don't quite follow your concept of reversing the polarity of a 120VAC supply to a solenoid valve for open/close control but do understand the workings of a dual coil solenoid valve.

Is this what you are trying to do?

Excuse my drafting skills, been using CAD for way too long

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2012
Posts: 8
#9
In reply to #8

Re: Octal Base Relay

07/26/2012 12:03 PM

The actuator is not a solenoid. Its a reversing motor.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Octal Base Relay

07/26/2012 12:08 PM

Please post details.

The forum doesn't generally respond well to "20 Questions", plus having all the information up-front saves such a lot of time, which may be important; other postings come in and potential respondents to this one wander off to them.

A valid response so far would be "consult an experienced control circuit designer locally", for example, given the level of detail shared.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Nov 2007
Posts: 53
Good Answers: 1
#20
In reply to #8

Re: Octal Base Relay

07/26/2012 11:51 PM

A single armature on the valve relay swinging between the upper contacts without the permanent connection on the left would turn the valve on and off. Normally limit switches (not shown) shut off valve motor power at the end of travel.

__________________
Clintb3252
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#11

Re: Octal Base Relay

07/26/2012 5:04 PM

You say that you need to reverse polarity. That does not appear to make sense. Reversing polarity on a 120 vac valve motor will not cause it to reverse. The "whole idea" with AC is that it reverses polarity many times per second.

You may need to post a schematic of the valve operator.

__________________
Think big. Drive small.
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#12
In reply to #11

Re: Octal Base Relay

07/26/2012 5:19 PM

Reversing polarity is the wrong term, sorry. I simply need to reverse the direction that the motor operates.

Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#14
In reply to #12

Re: Octal Base Relay

07/26/2012 5:47 PM

Some of these units have three wires (or three terminals) neutral, open, close. They are wired in the same way as the solenoid shown schematically above. However you have to be sure that the valve contains at least the logic to prevent the drive motor from continuing to run when the valve is (for example) fully open.

__________________
Think big. Drive small.
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#16

Re: Octal Base Relay

07/26/2012 6:03 PM

Doorman, you are correct.

Kfry, In an irrigation well, there are no check valves like a residential system would have. This is because these pumps run for days, sometimes months on end without shutting down. They pump anywhere from 600-2000 GPM. Today I timed how long it takes for the water to get to the surface when the pump is initially turned on. It took 30 seconds. The valve I have spec'd goes from fully closed to fully open in 27 seconds. There isnt much difference here, but even if the valve was only half open, there would not be any damage done to the system.

An 8" valve is more than what is needed for the 700 gpm I am pumping, but that is what size of manual valve is currently installed, and the new electric valve will be a direct bolt in.

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#18
In reply to #16

Re: Octal Base Relay

07/26/2012 11:01 PM

Does the electric actuated valve have limit switches that open the circuit to the valve motor when it is fully open or fully closed?

__________________
johny451
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#19
In reply to #18

Re: Octal Base Relay

07/26/2012 11:45 PM

The actuator has its own limit switches built in.

The actuator has 3 terminals.
#1 is power to close
#2 is nuetral
#3 is power to open

Can anyone provide a link to a normally closed pressure switch? I want it to open the circuit at 60 psi. I will install it on the nuetral side of the circuit

Edit: The valve is 100-240vac and will draw .3-.6 amps

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#21
In reply to #19

Re: Octal Base Relay

07/27/2012 12:47 AM

Response #8 from KJK/USA is the diagram you are looking for.

He had already sussed out the probable operation of your valve.

__________________
johny451
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#22
In reply to #19

Re: Octal Base Relay

07/27/2012 2:54 AM

Switches should not be installed in the neutral side of a circuit (with the exception of certain motor overload switches).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Jul 2012
Posts: 8
#23
In reply to #22

Re: Octal Base Relay

07/27/2012 7:55 AM

If I cant use the nuetral side, then I will need 3 seperate switches. That is not a problem if that is the way it needs to be.

The switch needs to have a manual reset. That way, if the pressure exceeds 60 psi, kicks the pump out, it doesnt drop back below 60psi and attempt to restart the pump while water is rushing back down

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17

Re: Octal Base Relay

07/26/2012 10:48 PM

What is the rated current of the butterfly valve?

Does is have a forward-n-reverse wiring logic?

If so, please submit drawing of valve wiring.

Very simple if we have all the info provided.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#24

Re: Octal Base Relay

07/27/2012 10:04 AM

The simple automatic garage door opener controller matches what you want to accomplish. Together with the corresponding safety and limit switches, (in your application will be the pressure limit switches). It can simultaneously control the pump together with the intended valve's opening and closing operations. You only need to take into consideration the total current carrying capacity of the relay contacts, making sure it matches load requirement!

__________________
vsar
Register to Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#25

Re: Octal Base Relay

07/30/2012 10:48 AM

This should work. Make sure everything is turned off and locked out before commencing work. Stay safe Elroy

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#26

Re: Octal Base Relay

07/30/2012 11:48 AM

We don't know if it is a single phase motor, a 3 phase motor, a servo motor, a stepper motor, has it's own controller and just needs signals, nothing. Without FULL information, this continues to be a "20 questions" game.

So let's start fresh, I say is it "animal mineral or vegetable"?

Next?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 26 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Clintb32 (1); Dewey G. (7); Doorman (1); Elroy (1); HiTekRedNek (1); Johny451 (2); JRaef (1); K_Fry (3); KJK/USA (1); lyn (2); ozzb (1); PWSlack (1); TonyS (1); Tornado (2); vsar (1)