Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

10/31/2012 6:41 PM

While pulling cables I found it out that three conductor cable was pulled between two switchboards but four conductor cable should have been pulled as power system is designed to be three phase-four wires.

Is it OK if one single conductor cable is pulled for neutral phase instead of replacing four conductor cable ? If it is allowed, what is any consideration or constraints ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Three conductor cable plus one single conductor cable for three phase-four wire

10/31/2012 6:51 PM

Depends on the definition of OK, I'd say.

And what the customer says, assuming you were going to ask him for a deviation.

Is it allowed anywhere? I'd do it back on the farm in Ark.

I wouldn't allow it in anything I could be held accountable for if somebody were to lick the conductors.

Check the local codes, if any. Maybe you can use the conduit, itself, and save wire.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Three conductor cable plus one single conductor cable for three phase-four wire.

10/31/2012 10:10 PM

If there is an imbalance such that the neutral carries significant current, and if the neutral and the 3C cable enter a metal enclosure separately; then there could be inductive heating of the enclosure.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Member

Join Date: Jun 2012
Posts: 6
#3
In reply to #2

Re: Three conductor cable plus one single conductor cable for three phase-four wire.

10/31/2012 11:49 PM

I consider to pull same size of single conductor cable for neural phase same as main phase. In the case of magnetic flux causing heating, single conductor may be provided with brass armour or with non-metalic gland plates. I am not sure if cable clamp is to securely fix three conductor cable and single conductor cables.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #3

Re: Three conductor cable plus one single conductor cable for three phase-four wire.

11/01/2012 1:15 AM

Is it non-metallic or non-ferrous gland plate or gland plate with a groove cut to prevent circulation of eddy current.?.

__________________
pnaban
Register to Reply
Member

Join Date: Jun 2012
Posts: 6
#5
In reply to #4

Re: Three conductor cable plus one single conductor cable for three phase-four wire.

11/01/2012 2:53 AM

Yes. That's why I intended.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: Three conductor cable plus one single conductor cable for three phase-four wire.

11/01/2012 3:10 AM

Be specific.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

11/01/2012 8:45 PM

How would you're client / employer view your mistake? Not quite as badly as finding out you have tried to cover it up with a potentially dangerous remedy.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#8

Re: Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

11/02/2012 12:17 AM

If you were going to the trouble of pulling an earth conductor you might as well use the 3 phase cable to pull in a new 4 core cable, this would be the best practice.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

11/02/2012 4:24 AM

Do it correctly according to the local wiring codes.

If there isn't time to do it right, from where is the time going to come to re-do it correctly?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#12
In reply to #9

Re: Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

11/02/2012 4:14 PM

My thought exactly! I would also ask about the ground (earth) wire. Decades ago we used the conduit, not legal in most codes since the 60's. (Pretty good that I can still remember that far back. Now, what is my new wife's name?) If the ground is OK, The neutral may be able to be calculated. That is legal in the NEC (American Code). OP does not say what the applicable code is or where he is, and I don't know other codes. If in question, pull 5 new wires.

One of the posters said he would do it back on the farm in Arkansas. Still happens out on the farm, but Arkansas has come into the 20th century, you have to go by NEC 2008 in Arkansas now. -- JHF PS: GA

__________________
If it's too good to be true, it probably isn't
Register to Reply
Active Contributor

Join Date: Jul 2012
Posts: 15
Good Answers: 1
#10

Re: Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

11/02/2012 4:32 AM

You need to look at what was specified and for what use.

The 3 phase cables should all be together however if your using the neutral, that should also be in that cable, so, yes replace a 3 conductor cable plus 1 conductor with a 4 conductor cable.

However what is being used for the earth ?
Some people say to use the conduit or Steel wire of the SWA cable, but this can be considered bad practice, and indeed may not be allowed by local codes / electrical bodies.

As a general rule all conductors of the same circuit should be going through the same cable.
And yes, the earth to protect what ever this would be supplying is considered part of the circuit.

There could be many arguments on different ways to do this, but if its all in one cable hopefully there would be less issues.

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#11

Re: Three Conductor Cable Plus One Single Conductor Cable for Three Phase-Four Wire.

11/02/2012 10:52 AM

It is not "best practice". I would pull the wire out and replace it. And yes, it will be expensive. Mistakes usually are. Dangerous? No. Confusing to the next technician who might have to do this work? Very.

That being said, code item 250.134B (exception 1) might be applicable for adding ground wires in new installations as well as existing installations. Permission is granted to run a separate ground wire outside the conduit in accorance with 250.130(c) when installing replacement grounding type receptacles or EXTENDING A NON GROUNDED BRANCH CIRCUIT to a grounding type receptacle when no equipment grounding wire or means is available in the branch circuit.

Presumably if there was room in the conduit, you "could" run itside as well. But this is just MY opinion. I usually find that conduits are too small to play games like this.

The reason I am not sure if this code item applies is your statement that you accidently ran 3 wire instead of 4 wire between two switchboards. Its not a "branch circuit". If I were the inspector I would demand you replace the three wire with proper four wire cable for that reason.

__________________
If it was easy anybody could do it.
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Circuit Breaker (1); garth (1); lyn (1); pnaban (2); PWSlack (1); SeungHee Kim (2); TonyS (1); Tornado (1); vitessees (1); Yusef1 (1)

Previous in Forum: Reusing SMD-s from junk PCB-s   Next in Forum: AC Stepper Motor

Advertisement