Under Voltage Problem at DG Sets

12/02/2012 12:34 PM

Our DG set(625 kva) is showing under voltage indication and very low power factor around .325 pf. Yesterday on increasing load, DG SET automatically got shutdown after showing low power factor. Could you guys tell me that how can I trace fault?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: under voltage problem at DG sets

12/02/2012 12:52 PM

Find the troubleshooting guide in the owner's manual and follow the steps there.

Don't have one? Download it from the website of the manufacturer.

When none of this helps, call in a repair technician to fix it. Nothing lasts forever.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: Under Voltage Problem at DG Sets

12/02/2012 11:03 PM

Please remove the load. Check voltage output from generator. If the voltage is in order then check the cables and load. If the voltage is not in order check the alternator.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#3

Re: Under Voltage Problem at DG Sets

12/03/2012 9:06 AM

If you are experiencing generator undervoltage trips you need to:

1. Measure the generator voltage level in unloaded and loaded conditions.

2. If the voltage is too low, adjust the generator excitation voltage to obtain the correct output voltage level.

3. If the generator output voltage level is correct then you need to adjust your under-voltage protective circuitry settings or replace the relay with a new properly configured unit that matches your generator operation.

4. If none of the above stops the issue, you may be exceeding the generator's output capacity and you will have to identify the root-cause. (Ground fault, shorted conductors, faulty equipment, etc.)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Under Voltage Problem at DG Sets

12/04/2012 5:36 AM

Oooooh! It's a good bet that 4 comes before 1, 2 and 3!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Under Voltage Problem at DG Sets

12/14/2012 12:55 PM

It has to be a short-circuit somewhere. For instance this could be a locked rotor[starting] pf. when the voltage is very low and an induction motor could not start and the protection does not working to shut down.

__________________
Julius
Register to Reply
Member

Join Date: Dec 2012
Location: DK 7000
Posts: 6
#6

Re: Under Voltage Problem at DG Sets

12/23/2012 6:14 AM

Your voltage regulator is faulty.

Normaly You must adjust the pf to 0.9 by raising or lowering generator voltage.

Look at the A-meter and adjust it to minimum by adjusting generator voltage.

Then You have the correct current running in the system.

Register to Reply