Voltage Suits Up

12/04/2012 11:51 PM

Dear Experts,

I have came across a problem which is new to me. When 3-phase cutting machine started teh incoming supply voltage suits up from 380V to 420 V.

Generally I have came across drop in voltage while the load was connected to the supply. But here the voltage suits up.

Please help me why it is happening and how to solve it.

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: Voltage Suits Up

12/05/2012 12:08 AM

How does it "suit up"? In Adidas or Reebok or Nike or other?

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#2
In reply to #1

Re: Voltage Suits Up

12/05/2012 12:12 AM

I mean the voltage increased once the load was connected.

Register to Reply
Anonymous Poster #1
#3
In reply to #2

Re: Voltage Suits Up

12/05/2012 12:15 AM

Then that could be "shoots up."

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#4
In reply to #3

Re: Voltage Shoots Up

12/05/2012 12:28 AM

Thanks for the correction. How to correct in the question now?

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#5

Re: Voltage Suits Up

12/05/2012 12:33 AM

Kindly read it as Voltage Shoots up instead suits. Sorry for the speeling mistake

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#19
In reply to #5

Re: Voltage Suits Up

12/05/2012 11:56 PM

When you say the voltage 'shoots up' are you simply measuring peak values, or monitoring the waveform?

You could be seeing inductive spikes during load variations rather than increased line voltage.

Have a look with a suitably rated CRO and probes to see what is really happening.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#6

Re: Voltage Suits Up

12/05/2012 1:21 AM

What is the type of machine ?

hope it is a 3 phase induction motor. hp ?

normally a voltage drop when there is a load applied on motor , because of increase in current.

Is this rise in voltage is instantaneous or it lasts till the end of cutting process ?

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#7
In reply to #6

Re: Voltage Suits Up

12/05/2012 2:09 AM

Thanks for your kind response.

Yes it is 3 phase induction motors. 5 KW

Some times instantanious and most of the times till end of the process.

There are sequence of operations involved with various capacity of motors like 1 HP, 3 HP and 7 HP.

It is not rise only particular motor's operation. It rises at different motor's operations.

Register to Reply
Commentator

Join Date: Nov 2012
Location: Sunnyvale, CA
Posts: 62
Good Answers: 10
#17
In reply to #7

Re: Voltage Suits Up

12/05/2012 4:05 PM

I suspect that what you're seeing is an artifact of how the voltage is being measured, not a real increase in the peak voltage in the AC power cycle. Are you viewing the actual wave form on a scope, or using an instrument that integrates the wave form and displays something like an RMS value? And what are the points that you're measuring between? It may be that what you're thinking of as the "ground" reference may be affected by whether the motor is on or off. If so, you could conceivably have a hazardous wiring situation.

It's hard to say anything definite without a lot more information. However, what you're reporting is definitely anomalous. Something's wrong, and you need to resolve what it is.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#8

Re: Voltage Suits Up

12/05/2012 4:59 AM

is the power is from a DG set or it from EB ?

if it is from Dg , may be it is from Dg. when apply load dg rpm shoots up.

what is the Dg kVA

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#10
In reply to #8

Re: Voltage Suits Up

12/05/2012 7:08 AM

Thanks. The power is frmo EB as well as DG.

DG is 500KVA.

Same kind of machines running without any problem. Kindly advice.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Voltage Suits Up

12/05/2012 5:27 AM

What is the voltage rating of the motor(s) that drive(s) the machine? What does the rating plate say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#11
In reply to #9

Re: Voltage Shoots Up

12/05/2012 7:09 AM

380 V - 3 phase

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Voltage Suits Up

12/05/2012 7:21 AM

What has caused this phenomenon to be noticed? Why has the concern arisen?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#13
In reply to #12

Re: Voltage Suits Up

12/05/2012 7:49 AM

The Emergency circuit activated. So we checked the voltage and noticed this.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#14

Re: Voltage Suits Up

12/05/2012 8:24 AM

Is it happens both with EB(utility) and DG supply ?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Voltage Suits Up

12/05/2012 8:38 AM

Does the equipment work satisfactorily despite this phenomenon?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#22
In reply to #15

Re: Voltage Suits Up

12/19/2012 12:15 PM

Phase sequence relay has gone damaged after this problem.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16

Re: Voltage Suits Up

12/05/2012 12:36 PM

Do you have Power Factor Correction Capacitors on the AC motors by any chance? If so, and they are sized for a loaded motor, until the load engages you will be over correcting, which can raise (suit up ) your voltage measurement.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#23
In reply to #16

Re: Voltage Suits Up

12/19/2012 12:18 PM

No such or any other capacitors are in this circuit.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#18

Re: Voltage Suits Up

12/05/2012 10:51 PM

Dear Mr.tsmoorthy,

It appears to me from your statement - "the Voltage shoots up" when load is put on.

What is the type of load - you have not mentioned. My opinion is the your Load should be Capacitance dominated load or more capacitor bank is in the circuit - which will result in a higher TERMINAL VOLTAGE, than the INDUCED VOLTAGE of the Power Source, be it Grid Power or Diesel Generator.

Let us see the comments from other CR4 MEMBERS.

Thanks,

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#24
In reply to #18

Re: Voltage Suits Up

12/19/2012 12:46 PM

Yes it is SHOOTS Up. (Is it posible to correct the spelling now??)

The type of load is just a cutting machine with Induction motors. It happens in both the supply sources.

Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#20

Re: Voltage Suits Up

12/05/2012 11:57 PM

this is the first time in my experience i heared, by connecting the load voltage boots up to 380V to 420V. as u mentioned the application is for cutting machine, the voltage never boots up by connecting normal induction motor for cutting applications, may be the motor getting over excitation due to changing the motor properties, due to over excitation only we can see voltage boots up, normally happens when we connect "synchronous motor" for power factor improvemnets.

thanks

__________________
Shaju Khan
Register to Reply Score 1 for Off Topic
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#21

Re: Voltage Suits Up

12/06/2012 2:31 PM

OH, my poor English language, what has become of you?

I suspect if DG, the DG cannot react quickly enough to the starting of your motor(s) in various locations, resulting in AVC circuit overshooting, and if trouble with AVC, then it will fail to regulate back down after the current surge. One of the posters mentioned (most accurately) that capacitive load during motor switch-on is high, and this results in a surge of current. If your supply is from the grid, there may be an undersized transformer in the works. Just IMHO (in my humble opinion). You should consult with your equiment supplier as to the exact electrical requirements, and consult with your local power company as to your transformer output characteristics. Likewise consult with the manufacturer of your DG, about how to maintain it in a ready state, for example some small constant load (some lighting perhaps) might be used to help the problem...?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#25
In reply to #21

Re: Voltage Shoots Up

12/19/2012 12:51 PM

It happens both with Grid and DG.

Already the machine was running wihtout any such issues with the same sources. But recently got this problem. It is not just 420, but some instants it goes to 480 or more, but just for a while.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#26

Re: Voltage Suits Up

12/20/2012 12:23 AM

Its within the system. Not from out side. You have to investigate one by one. I have come across voltage going down as ampere shoots up as in motor starting or similar cases. Check what change you made on the machines before and after these phenomena.

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#27
In reply to #26

Re: Voltage Suits Up

12/20/2012 2:17 AM

We have checked the complete wiring inside the machine, power supply and swaped the Stabiliser, but still we are getting this issue and really not able to find the solution or the reason.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#28

Re: Voltage Suits Up

12/20/2012 2:51 AM

"Phase sequence relay got damaged " . This gives me some clues ...

please go behind this - phase sequence

Register to Reply
Active Contributor

Join Date: Jul 2010
Location: Tirupur, Tamil Nadu, India
Posts: 14
#29
In reply to #28

Re: Voltage Shoots Up

12/20/2012 3:21 AM

We feel that due to this problem that relay may damaged. The machine will not start if the phase sequence changed.

Thanks a lot for your continuoues tips