Need Help: Noise/Inteference/Grounding Problem VFD

12/07/2012 9:43 PM

Dear All,

We are having lots of problem in communicating VFD with SCADA. The scenario is:

We have a panel of 5 VFDs, in which we can communicate perfectly with one drive. As soon as we start another drive we start getting corrupt messages, and as a result both the drives trips. Surprisingly, we have tried couple of days ago by running all the drives, which was pretty successful.

Y'day, on someone's suggestion, we measure the voltage between neutral and ground, and the observations are:

Without running any VFD the voltage is 0.05V.

By running one VFD(which runs successfully by SCADA) the voltage is same.

If we run the second VFD(rating 7.5Hp) we start getting voltage difference of 6.0V, I am not expert in interference/grounding. Please help.

Manish

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Need Help :Noise/Inteference/Grounding problem VFD

12/07/2012 10:43 PM

Things like this are usually the result of poor termination and shielding practices. Describe how you have everything wired, both power and control.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Dec 2010
Posts: 23
#2
In reply to #1

Re: Need Help :Noise/Inteference/Grounding problem VFD

12/07/2012 10:53 PM

For control, we are using 4-core shielded cable from SCADA, which is connected to the terminal of our panel, from there again we are using shielded cables to all VFDs.

We have connected the shield to the ground.

This was a retrofit project, so For Power, we have taken Three phase and neutral wire from the existing system, and connected the ground of all VFDs to the Panel box, which again is connected to the entire ground system.

One doubt, that all of our power and communication shield are grounded together, can this be a problem?

Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Need Help :Noise/Inteference/Grounding problem VFD

12/08/2012 11:10 AM

Ground is ground is ground, although because there can be different resistances, there is the possibility of ground loops. But did you ground BOTH ends of the control cables? You do that for the power cables, but control cable shields must be grounded at only ONE end or the other, never more than one. That is the most common error and causes the exact type of thing you are experiencing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#12
In reply to #3

Re: Need Help :Noise/Inteference/Grounding problem VFD

12/09/2012 12:08 PM

GA from me. In the audio world the signals are even more important to keep clear or you end up broadcasting your ground loop problems as noise, hum or static. Ground the control cables at the control box end, and leave the shield ground disconnected at the power end. That way you do not send power ground fluctuations back into the control gear.

__________________
Most people are mostly good most of the time.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/08/2012 11:10 PM

Your problem area is earthing .Communication cable not to be taken along with power cable .communication and control cable shield earthing to be done at one end only

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/08/2012 11:53 PM

Problem culd be grounding loops. Check your grounding.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/09/2012 3:02 AM

Dear Mr.mjain,

You have not mentioned anything about earthing in the system.

The panel Board Casing also to be earthed and the Earthing Flat should be DOUBLE the SIZE of the NORMAL Earthing Flat.

We also had a similar problem. By checking the earth and providing additional Earthing Flat for the casing, the problem what we have faced is solved.

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: Dec 2010
Posts: 23
#7
In reply to #6

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/09/2012 4:07 AM

Thanks Everyone.

We are using the existing earthing done for the system, we don't have any idea about the existing earthing. We also suspect the earthing is flawed.

Can anyone suggest some good technical document for earthing and how can we check if the earthing is proper or not.

Manish

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8
In reply to #7

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/09/2012 7:03 AM

British Standard 7671 - it's a good bedside book, Uncle. Order one for Christmas.

__________________
Good moaning!
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#9
In reply to #7

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/09/2012 7:58 AM

Dear Mr.mjain,

The existing Earthing IS NOT AT ALL SUFFICIENT. Whether it is PERFECT to satisfy the Electrical Requirement.? For name sake - Earthing provided means it will be the problem. Supposing you need one Number of 50MMx6MM G.I. EARTH FLAT, you provide 2 Numbers of 50MMx6mm G.I FLAT and pl. do not forget to wet the Earth Pit daily with water. Also provide a seperate Earth Flat to the MCC PANEL CASING.

As already suggested by the CR4 MEMBER, provide grounding of the Power cable on one side only.

I shall try to provide details seperately as I have to locate in my Data Archives or you can google it.

Keep the Power Cable and Control cable/Data cable - a minimum distance of 1.2 Metres or use cable suitable for Protection against Induction. Last year it was a havoc for us and now totally solved.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #7

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/09/2012 9:24 AM

IEEE 1100 -The IEEE Recommended Practice for Powering & Grounding Sensitive Electronic Equipment

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#11

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/09/2012 10:30 AM

The common mode voltage between the drives and the scada is higher that the communication voltage. Grounding may help but the basic issue is that the communication links should have isolation at each point in order to avoid this type of problems.

What kind of communication network are you using? Ethernet, RS-485...

Is the drive manufacturer saying anything about communication isolators? Are they built in? Did you bypass them by mistake?

Did you connect the control ground with the power ground? In most drives, the controls are floating with respect to the power. You ground all the controls together at the PLC (scada) independantly from the power ground. This prevents the power noise from affecting the controls by using the "built in" insulation of the drive. You might have to remove a ground jumper on the control terminal to "free" it from the power section.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Active Contributor

Join Date: Dec 2010
Posts: 23
#13
In reply to #11

Re: Need Help: Noise/Inteference/Grounding Problem VFD

12/18/2012 11:19 AM

Thanks All,
Even after getting new earthing done, we are still not successfull in eliminating noise.Following are our observations:(The setup includes 6 VFDs connected in a single Panel)

  1. If the COM port of VFDs are disconnected and they are made to run the motor, and one of the VFD is connected with 485 port, there is no noise, IMO , it indicates that there is no Noiise because of power cables going from VFD.
  2. If all the COM ports are connected and VFDs are not made run, there is still not any problem of interference.
  3. As in point 2, if we make one of the VFD made run, we start getting Noise in the data.We are monitoring noise by seeing the data in Moxa Modbus RTU-TCP converter.

We are running out of options, Please help, on what can we do.
Thanks in Advance,Manish

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: