Bus Bar Transposition

12/07/2012 11:30 PM

I have a 4000A, TPN (Three phase & Neutral) 415V, 50 Hz. bus duct with Aluminium Bus bars. I have one run of bar per phase. To reduce heating due to skin effect/proximity effect, I propose to transpose the RYB Bus bars at regular intervals. If the bus duct length is 30 meters, what is the suggested interval of trasposition of the bus bars?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Bus bar transposition

12/07/2012 11:49 PM

31 meters...

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: Bus Bar Transposition

12/08/2012 11:04 PM

Please let us know size of the bus bar.For 4000 Amps no single bus bar can carry this much current.Even 1 number 10 x 1/2 inch can carry 3640 Amps for an ambient temperature of 35deg C .By interleaving the busbars you can reduce the deration but the open air current carrying capacity can not be altered. The above data taken from book Aluminum busbars by Thomas & Rata

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#6
In reply to #2

Re: Bus Bar Transposition

12/10/2012 8:36 AM

Sinlge 300x16 is ok for 4000A

__________________
A day without a smile is a day lost
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#3

Re: Bus Bar Transposition

12/08/2012 11:23 PM

The major degradation of your bus bars is caused by temperature rise related to the power dissipated in them. Use larger bus bars to reduce the power, cool the bus bars, or use copper bars. Heating due to skin and proximity effect will not be altered by transposing the bars.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Bus Bar Transposition

12/10/2012 5:29 AM

"The bars are too sma-all

Dear Lysa

Dear Lysa

The bars are too sma-all

Dearl Lysa

Too small."

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#5
In reply to #4

Re: Bus Bar Transposition

12/10/2012 8:31 AM

Then grow them dear expert dear expert

Then grow them dear expert

Grow them.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

peterd (1); PWSlack (1); ramvinod (1); Tornado (1); welderman (2)

Previous in Forum: Need Help: Noise/Inteference/Grounding Problem VFD   Next in Forum: Control Wiring

Advertisement