I have a 4000A, TPN (Three phase & Neutral) 415V, 50 Hz. bus duct with Aluminium Bus bars. I have one run of bar per phase. To reduce heating due to skin effect/proximity effect, I propose to transpose the RYB Bus bars at regular intervals. If the bus duct length is 30 meters, what is the suggested interval of trasposition of the bus bars?
Re: Bus bar transposition
12/07/2012 11:49 PM
31 meters...
Good Answers: 19
Re: Bus Bar Transposition
12/08/2012 11:04 PM
Please let us know size of the bus bar.For 4000 Amps no single bus bar can carry this much current.Even 1 number 10 x 1/2 inch can carry 3640 Amps for an ambient temperature of 35deg C .By interleaving the busbars you can reduce the deration but the open air current carrying capacity can not be altered. The above data taken from book Aluminum busbars by Thomas & Rata
Ramesh,Freelance Electrical/automation Consultant
12/10/2012 8:36 AM
Sinlge 300x16 is ok for 4000A
A day without a smile is a day lost
Good Answers: 58
12/08/2012 11:23 PM
The major degradation of your bus bars is caused by temperature rise related to the power dissipated in them. Use larger bus bars to reduce the power, cool the bus bars, or use copper bars. Heating due to skin and proximity effect will not be altered by transposing the bars.
12/10/2012 5:29 AM
"The bars are too sma-all
Dear Lysa
Dear Lysa
Dearl Lysa
Too small."
Good Answers: 58
12/10/2012 8:31 AM
Then grow them dear expert dear expert
Grow them.