Anonymous Poster #1

Blast Freezer

12/12/2012 10:09 PM

working on a blast freezer for the first time. low side reads -30, high side 250. Room temp is 60 degrees. Unit cools to -19 degrees. Customer wants me to add freon. What do you think?? Also wants to improve efficiency, any ideas?? Customer wants to drop temp to -28 or -30...??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: blast freezer

12/12/2012 10:48 PM

I think your client should hire someone who knows refrigeration systems. Your guage readings indicate that the system is working, something that is obvious since cold air is coming out. Whether it is working to its design point is an entirely different matter, and is something that can only be determined by reading the manuals or calling the manufacturer.

Adding Freon to a system that's already at its design point will not make it any colder and will most likely make it warmer, and consume more energy moving the additional Freon against a higher head pressure.

Also when your client says "improve efficiency" I believe he means "reduce energy consumption". Although related they are not the same; i.e., you can have a system that does more work (makes things colder) at a lower per unit energy consumption, but you still have to pay for the additional energy for the additional cooling effect.

There is no free lunch, you'll need more evaporator and/or condenser surface area to pick up and reject the additional heat required for a greater temperature difference. Hire an expert.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: blast freezer

12/12/2012 10:58 PM

Do you have any pressure readings? What type of "Freon®"? Does the system ever run in partial vacuum? Is there a purger? Etc., etc.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #1
#3
In reply to #2

Re: blast freezer

12/12/2012 11:56 PM

freon is 404a, low side is -30, high side is 250. no partial vacuum, no purge.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: blast freezer

12/13/2012 3:29 AM

How did the call to the equipment manufacturer go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #3

Re: blast freezer

12/15/2012 9:16 PM

The "-30" can't be a realistic pressure.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Jan 2009
Posts: 29
Good Answers: 1
#5

Re: Blast Freezer

12/15/2012 9:06 PM

You need to gather all the data before you can diagnose the system. You need to take superheat and subcooling reading in order to verify the system is low on charge.

Reply