Formula for Density Calculation Steam
01/12/2013 4:54 AM
Dear friends, please provide me the formula for calculation of density of steam by using temperature and pressure?
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -
Good Answers: 46
Re: formula for density calculation steam
01/12/2013 8:33 AM
Use a steam table. Based on empirical measurements, it will be better than any formula approximating density.
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
01/12/2013 11:47 PM
Please tell me the formula, since some formula is used in our plant, i want to find the authenticity of the reading,
Density = (Pressure * 19)/(1.48+0.01*Temperature-0.0452*pressure).
Pressure - MPA,
Temperature - Degress celsius.
pls check the autenticity of the formula.
Good Answers: 19
Re: Formula for Density Calculation Steam
01/12/2013 11:46 PM
All Flow Meters for Steam & Gas MUST have "Density Compensation" to safeguard against error in reading depending on difference between the specific density and the actual flow density.
Error in Orifice /Differential Pressure Device :
[√ specific volume actual/specific volume -1 ] x 100
= :[√ 4.44 cu.ft/lb/3. cu.ft/lb -1 ] x 100 = 6.8% over reading by Meter
Error in Vortex Pressure Device :
[specific volume actual/specific volume -1 ] x 100
= :[ 4.44 cu.ft/lb/3.89 cu.ft/lb ]- 1 x 100 = 14.0% over reading by Meter
Calibrated for 100 psi (specific volume 3.89 cu.ft/lb ) when
actual is 85 psi (specific volume 4.44 cu.ft/lb)
Example case, the Boiler House Boiler is at say ≤8.0 Bar = 115 psi or 3.46 cu.ft/lb specific volume. Whereas you are getting ≤5.0 Bar at your Header = 70 psi or 5.19 cu.ft/lb specific volume.
Now your meter was calibrated at obviously 8.0 bar or 115 psi while you are getting
≤ 5.0 bar or 70 psi. Therefore based on above the Error in Reading without density compensation on an Orifice flow Meter will be :
= :[√ 5.19 cu.ft/lb/3.46 cu.ft/lb -1 ] x 100 = 22.47 % over reading by Meter
01/13/2013 8:41 PM
devitg
03/03/2013 9:09 AM
If you want a program, I use WASP (Water and Steam Properties) excellent results.
http://www.katmarsoftware.com/wasp.htm
08/23/2016 2:55 PM
You can always use pV=nRT and get fairly good results. Knowing that m=Mn where M=18.0538 g.mol-1 for water and steam, and R = 8314 J.kmol-1.K-1, we have:
p * V = (m / 18.0538 g.mol-1) (8314 J.kmol-1.K-1) T
V / m = (1 / 18.0538 g.mol-1) (8314 J.kmol-1.K-1) T/p
rho = m/V = (18.0538 kg.kgmol-1) 1/(8314 J.kmol-1.K-1) (p/T)
rho is the density
rho = ( 18.0538 kg / 8314 N.m.K-1) (p / T)
where p is expressed in Pa and T is expressed in K. The density, rho, is in kg.m-3.
I think that you live in a country that uses SI units, so I did this that way.
08/23/2016 5:08 PM
You could also look on page 24 of this book:
https://books.google.com/books?id=EQYa6gzXXtoC&pg=PA24&lpg=PA24&dq=647.096+1.84408259+-11.7866497&source=bl&ots=eI3iH6dHJu&sig=VSv5H_nizjgFFW0RdFdWVUUWR9E&hl=ru&sa=X&ved=0ahUKEwi4zsiPtNjOAhVJyWMKHeXuDR4Q6AEIHjAA#v=onepage&q=647.096%201.84408259%20-11.7866497&f=false
Physical Property Data Book: For Engineers and Scientists
Авторы: David C. Shallcross