33kv Fault Level Calculation

03/08/2013 5:11 AM

Total capacity of Transformer 2500KVA 33KV/433V X4Nos =10000KVA, So i want HT Side fault level calculation and total Amps.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 33kv fault level calculation

03/08/2013 5:55 AM

Hire an Electrical Engineer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#2

Re: 33kv fault level calculation

03/08/2013 6:55 AM
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: 33kv Fault Level Calculation

03/08/2013 10:05 AM

Fault level on the high side of the transformers will depend first of all on what the utility can provide, so you have to start there. They will have fault current levels for your connection. If you are downstream from that point in your own (privately-owned) system, you will need to do a system fault analysis to find out what the currents are at the transformers. This will also have to include any contribution from generation that you have on site.

As someone else said, hire a qualified electrical engineer to do the analysis for you.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: 33kv Fault Level Calculation

03/09/2013 12:42 AM

The ht side fault current depends on source fault level indicated by EB grid. This will not have any bearing on your transformer capacity and no of transformers, as long as you do not generate power and export to utility grid.you should find out the fault currents down stream and select devices suitable to withstand such fault currents.also protective relays are to be set based on such fault currents.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster #1
#5

Re: 33kv Fault Level Calculation

04/11/2013 7:05 AM

HT side is 1750amps at 10MVA

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); nobodysomebody47 (1); PeterT (1); PWSlack (1); ramvinod (1)

Previous in Forum: Questions Regarding "Plugging" of Induction Motor   Next in Forum: Need Technical Detail of Energized Cable Sensing Device

Advertisement