Eratic Reading in Weigh Bridge

03/12/2013 3:13 AM

Hai,

We are having 50 ton weighbridge for Measuring our incoming raw material.Recently we are facing frequent variation of readings(like with out weight it is showing readings of 1Ton/2Ton),We got doubt with Neutral to Earth voltage.Its swing between 10 to 15 V.Then we put Salt & water in Earth pit & reduce the voltage between Neutral to Earth to 4V.Even though we are not getting 100% perfect reading.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Eratic reding in Weigh Bridge

03/12/2013 4:17 AM

Well, there will always be a voltage between neutral and earth as it expresses the current flowing in the neutral conductor, which isn't a perfect conductor in itself and is there to carry the imbalance current presented by a range of single-phase loads connected to a 3-phase supply, and the earth loop impedance, so that's nothing to worry about. The earth conductor is a safety provision and its job is to carry the fault current until the circuit protective device(s) operate(s) to disconnect it from the supply.

There should be a very-high-to-sort-of-infinite resistance between the earth conductor and both the live and neutral conductors with the device's cable disconnected from the supply. If there isn't, then it needs correcting; call a qualified local Electrician.

More likely to be the cause of the problem is a piece of the raw material jamming up the mechanism in some way so as to give a deflection that suggests 1-2ton at the read-out. Another possibility is a loose connection onto the primary measuring device. Another possibility is water ingress to the primary measuring device or some part of its cabling. These are the things that need to be checked out first, if necessary in the company of the equipment supplier's local Service Technician; make the phone call and get 'em in.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 4)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#3
In reply to #1

Re: Eratic reding in Weigh Bridge

03/12/2013 9:08 AM

Yes, I saw that it in our own scale, it was water ingress to the transducers wiring. The scale is installed outdoors.

You hear OP ? check that first.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: May 2007
Location: Ohio. USA
Posts: 578
Good Answers: 30
#7
In reply to #1

Re: Eratic reding in Weigh Bridge

03/13/2013 9:37 AM

PWSlack, thank you for that neutral to earth explanation. I have seen it and wondered about this. Now I know why.

To me this is the biggest value of CR4. Posters oftentimes explain the reasons behind something instead of just spouting standard practice. I am glad I read topics that are not in my area of experience because I can learn something.

__________________
Everything I know about opera I learned from Bugs Bunny
Register to Reply
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#2

Re: Eratic Reading in Weigh Bridge

03/12/2013 9:00 AM

Have you ruled out a defective load cell?

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Eratic Reading in Weigh Bridge

03/12/2013 3:52 PM

Also if an older scale the weight load may be on the load cell with pivots and arms. These pivots can get worn out or contaminated. Most trucks scales will have load cells on each corner. By moving a load from corner to corner you can usually find a discrepancy to give indication of where to look.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2008
Posts: 9
#5

Re: Eratic Reading in Weigh Bridge

03/13/2013 12:00 AM

I agree with that first check if you have any material that is jammimg the functioning of the load cells.

secondly, in my opinion check the resistance of the load cell and try to install filters in series with the load cell. Standard RC filters will do.

finally call technician.

hope it helps.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Eratic Reading in Weigh Bridge

03/13/2013 5:28 AM

Dear Mr.rubeshrishna,

You have indicated the Earth Voltage. What is the Earth Resistance - it should be below 2 OHMS, in some cases it should be 1 to 1.5 Ohms only. What is the size of Earthing Conductor.? Is it single Earth or Double Earth.? What is the supply Voltage.?

All these Factors have impact on the Working on Weigh Bridge.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8

Re: Eratic Reading in Weigh Bridge

03/13/2013 11:49 AM

I suggest you verify and ensure that the shielding and static drains on all the instrument wiring from the weight sensor (load cell?) and all other sensitive devices are intact and properly terminated to earth ground with <1 ohm impedance.

These electrical noise "drains" should only be attached on one end so that a circulating induced voltage loop is not created.

If the shielding and drains are ok, and you still have the issue:

Procure/obtain a dual channel oscilliscope and following the scope operation OEM directions for safe operation:

1. Set one of the channels of the scope up on AC coupling and connect the probe between the signal conductor and earth or circuit reference.

2. Set the other channel to DC coupling and connect it in parallel with the AC coupled channel.

3. Operate/activate the scale and observe the scale signal circuit waveform to determine the type and magnitude of signal variation.

4. Move the scope probes throughout the signal testpoints and identify the source of the issue.

5. Repair or replace the component that is causing the issue.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 2)
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

DaveB (1); dhayanandhan (1); JNB (1); nrmahadeokar (1); ozzb (1); PWSlack (1); SHOCKHISCAN (1); Yahlasit (1)

Previous in Forum: Temperature Data Logger TC-08 (USB)   Next in Forum: How to Tune a =% Valve with Linear Plug

Advertisement