Insufficient Cooling

03/14/2013 3:22 PM

Pls i checked an a/c it not cooling well. D gas is ok, it thought d fault was due to a dirty evaporator, av cleaned it, av set d fan to d highest speed(although am not satisfied with d speed of d fan) but av set it to d highest speed, infact i dont know what to check again pls help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#1

Re: Insufficient Cooling

03/14/2013 7:28 PM

Did this AC system ever work properly before? Or is it a new installation.

What is your "figure of merit" for determining Insufficient cooling? Is the thermal capacity of the system enough to cool the space? What is the thermal capacity of the system? How much cubic volume are you trying to cool? What is the outside temperature? Where is the condenser located, in the shade or direct sun?

I'm going to assume the evaporator fan speed is what you are muddling with, correct? If so why would you put that at maximum speed? You need to let the air flow slow enough to get a temperature decrease, as well dehumidify. But if the capacity of the system was enough, it would still cool everything down eventually.

__________________
ignator -
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Insufficient Cooling

03/14/2013 11:24 PM

Dear M.viqu,

Did you or the AC mechanic check the Compressor Pressure.? Please check the COPRESSOR OUTLET PRESSURE. Normally it WILL BE in the range of 150 psi or 10.5 Kg/CM^2.

I am of the view that the compressor is not developing required pressure, then only cooling will be proper.

DHAYANANDHAN.S

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Insufficient Cooling

03/15/2013 4:32 AM

Maybe it's time to call the technician in from either the original equipment manufacturer or the local service agent to give the system a good seeing-to?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#4

Re: Insufficient Cooling

03/15/2013 6:29 PM

1. Is d compressor running?

2. Is d evaporator colder/is there a temperature delta?

3. Is d condensor frozen?

Register to Reply
Anonymous Poster #1
#5
In reply to #4

Re: Insufficient Cooling

03/16/2013 2:00 AM

The compressor is ok, infact d suction line sweats back when running. D condenser is not frozen

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#6
In reply to #4

Re: Insufficient Cooling

03/16/2013 12:42 PM

What is the indoor temperature?

What is the discharge air temperature from the evaporator?

What is the outdoor temperature by the condensor?

What is the capacity of the equipment that you are using?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Insufficient Cooling

03/16/2013 5:08 PM

if you can come up with a thermometer you can check "the split" take a temp of the air entering the evap and let that number settle...then take the temp of the cooler discharge air and do the math, if its running correctly you should have around 20F degrees difference

Register to Reply
Active Contributor

Join Date: Mar 2013
Location: Nigeria
Posts: 10
#8
In reply to #7

Re: Insufficient Cooling

03/16/2013 5:51 PM

Thank u

Register to Reply
Register to Reply 8 comments