Voltage Stabilizer

03/26/2013 7:00 PM

In our domestic single phase 230v system,the voltage drops as low as to 120v making it impossible to use appliances. i searched the market and found voltage stabilizers with rating of 4000 watt and input from 80 to 250v and output 230v . it the voltage specs are clear but what does the 4000 watt mean on the stabilizer.does it mean we can use this stabilzer for a load of 4kw. help please.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Voltage stabilizer

03/26/2013 7:11 PM

Where are you located?

Register to Reply
Anonymous Poster #1
#2
In reply to #1

Re: Voltage stabilizer

03/26/2013 7:17 PM

He's located in La La Land.

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Voltage Stabilizer

03/26/2013 8:09 PM

What do YOU think it means.

Come on now, what have we told you about performing a simple internet search and reading the manual.

__________________
jack of all trades
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Voltage Stabilizer

03/26/2013 10:25 PM

Fix the loose connections.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#5

Re: Voltage Stabilizer

03/27/2013 3:31 AM

It sounds as though you are in a country that has issues with the power grid. If so there is not much your going to do to improve the end product. I would offer this advise; pick up a generator unit that will supply the needed power at the voltage you need it, until the power company fixes their issues.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Voltage Stabilizer

03/27/2013 4:01 AM

Dear Mr. coolyaar,

The answer is YES. When Input and Output Voltage Range is given along with WATTS, THE CAPACITY is 4.0 KW. It appears to me me that the voltage Stabilizer is 5.0 KVA.

My view is Input Voltage Range of 80 to 250 Volts appears to be very large.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Voltage Stabilizer

03/27/2013 4:53 AM

If the supply isn't capable of supplying 4kW without voltage drop, then adding a voltage stabiliser isn't going to improve matters.

The issue is that the supply cables are undersized. Get onto the power supply company and have a commercially expletive moan.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Mar 2012
Posts: 23
#8

Re: Voltage Stabilizer

03/27/2013 5:42 AM

both the answer from dhayanandhan and PWSlack are correct. if you ask about capacity of the voltage stabilizer, it is 4 kW which means you can have it loaded for 4000 watt but if your main power supply is less than 4 kW you can't have it loaded

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#9

Re: Voltage Stabilizer

03/27/2013 9:50 AM

Have the main supply lines checked by the power company, if the voltage drop occurs within your property, you're risking your house to a nasty fire, if it occurs outside, you're probably setting things up for a sudden meltdown of the power lines, which can lead to electrocution risk for pedestrians if it's located at the primary of the step-down transformer.

This is serius stuff, don't buy any stabilizer to "correct" this !!

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10
In reply to #9

Re: Voltage Stabilizer

03/27/2013 12:09 PM

Dear Mr. Yahlasit,

You have mentioned - a VALID and IMPORTANT Point, and Thank you for the same. I replied only from Tech. Point of view, but working aspect did not strike to my mind.

I have NOTED DOWN your Point.

Thanks,

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#11
In reply to #10

Re: Voltage Stabilizer

03/27/2013 5:00 PM

You are wellcome Dhayanandhan, what may come before safety ? common sense.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#12

Re: Voltage Stabilizer

03/27/2013 10:45 PM

I really get the feeling that if you attach a voltage stabilizer to a 230 VAC power source that is dropping to 120V, whatever the reason for the voltage drop will become painfully and dangerously obvious. I think it would be a much better idea to fix the source of the problem.

__________________
johny451
Register to Reply
Participant

Join Date: Mar 2013
Posts: 1
#13
In reply to #12

Re: Voltage Stabilizer

03/28/2013 5:17 AM

Do your neighbours also have the same problem? If so it is very unlikely that it is something on your property that causes the voltage to drop.Get all your neighbours to combine and then go to the authorities. There is strength in numbers.

Using that stabiliser could keep you comfortable as long as you draw less that the designed power output of the unit. (<17 Amps if it is a single phase supply).

Register to Reply Off Topic (Score 5)
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#14

Re: Voltage Stabilizer

03/28/2013 9:01 AM

Be careful.

Allthough the stabilizer is rated for 4KW you must determine if the rating is for continous or intermittent usage as dictated by the "duty cycle" rating.

For instance:

A maximum KW rating of 4KW at a 40% duty cycle usually means the 4KW would only be sustainable for 40% of 1 hour = 24 minutes.

The amount of KW sustainable after this point is dependent on the quality of the stabilizer components and usually decreases substantially.

A graph and/or table should be available from the manufacturer that illustrates all of the values and information you will need to know.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Participant

Join Date: Mar 2013
Posts: 3
#15

Re: Voltage Stabilizer

03/28/2013 9:14 AM

First thing to check is your neutral good, if its bad, voltage could flux from 40 to 200 V. It could be bad at wheatherhead from bird dodo or water damage inside meter or if basement damp in panel. device you are proposing to use is for single appliance and can not be used to install on buss for multiple as it has no neutral - CAUTION - . Some 230v appliances have 120v controls so could not be used.

The 4000 is amp/heat rating of stabilizer. With motor load and normal power-factor = 5 hp or it may operate a resistive heater with no power-factor up to 5000watts.

Yes 4000w is 4kw.

Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#16

Re: Voltage Stabilizer

03/28/2013 9:41 PM

Yes, You can load it up to 4KW, but act as per duty rating.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#17

Re: Voltage Stabilizer

03/31/2013 10:54 AM

The 4KW rating means any combination of volts x amps will total 4KW.

__________________
Mr.Ron from South Ms.
Register to Reply
Active Contributor
Engineering Fields - Electrical Engineering - New Member

Join Date: Mar 2013
Location: Papua New Guinea
Posts: 10
#18

Re: Voltage Stabilizer

04/02/2013 8:27 PM

Before you buy a stabilizer, I recon you check your main service cable, terminations/connections at the entrance box, your fuse connections, metering connections, and the distribuiton board connections.

__________________
"Whatever your mind can concieve, and believe, it can achieve"...Napolean Hill
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 183
Good Answers: 6
#19

Re: Voltage Stabilizer

04/03/2013 1:38 AM

I have seen 160 volts instead of 230 at peak hours of consumption, but 120 is quite low. Looks like the distribution transformer is some kms away from you. Give an application signed by many, to the concerned authority for installing a transformer nearby.

Gajanan Phadte

Register to Reply
Participant

Join Date: Mar 2014
Posts: 1
#20

Re: Voltage Stabilizer

03/20/2014 4:03 AM

Domestic single phase of servo voltage stabilizer is available in standard fluctuation range of + 20%. All models can be factory preset for any output voltage from 215 to 240V P-N. standard protections include overload & short-circuit protection.

http://www.tsielecpower.com/indoor-automatic-voltage-regulators.htm

Register to Reply
Register to Reply 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bolang (1); dhayanandhan (2); fixitorelse (1); gmphadte (1); jack of all trades (1); jennifermethow (1); Joel Helms (1); Johny451 (1); nick.mapun (1); pillay (1); PWSlack (1); ronseto (1); SHOCKHISCAN (1); Tornado (1); wareagle (1); Yahlasit (2); zs6bli (1)

Previous in Forum: TCC Curve   Next in Forum: Fuel Cells

Advertisement