Anonymous Poster #1

Engine Room

04/28/2013 11:51 PM

Dear all friends,

I am designing a genset room for 3 x 1600 KVA gensets as follow.

1) Size of each genset is L x W x H : 4500 x 1800 x 2300 .

2) Because we do not have enough space,therefore, we put 3 consecutive gensets in length, so the room is quite long L x W x H : 18000 x 4500 x 4500.

3) 3 remote radiators L x W x H : 11000x2400x 800 are horizotal type ,we modify to be vertical type and put on the top roof of genset room.

I am not sure this solution correct or not. Please give me an advise .

Thanks and gest regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: engine room

04/29/2013 12:01 AM

No, it isn't.

What units are you using?

How did you get into this situation?

I advise you to hire an engineer to evaluate this mess.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: engine room

04/29/2013 12:13 AM

The supplier must give minimum space requirements for this equipment....What do they say ?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Member

Join Date: May 2012
Posts: 6
#6
In reply to #2

Re: engine room

04/29/2013 8:09 AM

I can not contact the supplier,the space around genset and the wall is 1.5m . is it ok ?

regards

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: engine room

04/29/2013 12:42 AM

It appears that the room will accommodate the gensets with enough space around each, but have you also included the switchboard (if located in this same room)?

The 11,000 length of each radiator seems unusually large; what are the dimensions of the vertical version? Are they air cooled, or evaporatively cooled?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Member

Join Date: May 2012
Posts: 6
#7
In reply to #3

Re: engine room

04/29/2013 8:17 AM

The switchboard locates at the next room. the dimension of the vertical version is 2.3m.

the remote radiator is water coolling,it cools the heat exchange locate in the engine room.

Regards

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: engine room

04/29/2013 3:33 AM

...and why are the radiators to be reconfigured vertically if they are designed to operate horizontally? What does the manufacturer have to say about this?

Quite a lot here doesn't make sense yet.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#16
In reply to #4

Re: engine room

05/02/2013 12:13 PM

Diesel locomotive engine "rooms" have radiators mounted over the top with fans discharging the air vertically. Most liquid to air heat exchangers are not smart enough to know how they are oriented, as long as air and liquid flows are adequate and 'dirt' is kept away from them.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: engine room

04/29/2013 5:08 AM

Dear Friend,

Just in between the engine and radiator, a FAN will be working through VEE Belt, and air will be forced. If you install at the top of the room, the cooling will be affected.

Pl. consult the Generator supplier. Unless we are sure on technical aspect, we should not decide on our own,

DHAYANANDHAN.S

Reply
Member

Join Date: May 2012
Posts: 6
#8
In reply to #5

Re: engine room

04/29/2013 8:53 AM

The remote radiator is water cooling type, it cools the heat-exchanger in the engine room. it is located on the roof top of engine room but on the independent structure. I do not have any technical spec of its.

Regards

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15
In reply to #5

Re: engine room

05/02/2013 1:41 AM

Fan could be driven by an electric motor controlled by a thermostat.

__________________
pnaban
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9

Re: Engine Room

04/29/2013 3:38 PM

11m long water heat exchanger radiators seem very odd in this situation, are these custom designed or something?

What does the radiator supplier say regarding installation of the radiators?

Why water cooling in the first place?

__________________
jack of all trades
Reply
Member

Join Date: May 2012
Posts: 6
#12
In reply to #9

Re: Engine Room

04/29/2013 9:33 PM

I can describe as folow: 11m remote radiaor -->l heat exchanger --> engine,I can not get the properly answer from the supplier. I do not know how to paste the sketch to this topic.It's easier to understand .

Regards

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#13
In reply to #12

Re: Engine Room

04/29/2013 11:50 PM

When you post a reply there is a little green camera button in the message options. Use this to attach the sketch picture to post it here.

A picture would likely help us.

__________________
jack of all trades
Reply
Member

Join Date: May 2012
Posts: 6
#14
In reply to #13

Re: Engine Room

05/01/2013 1:34 AM

Dear friends,

Many thanks, I will follow your advise.

Regards

Reply
Commentator

Join Date: Oct 2012
Posts: 74
Good Answers: 1
#10

Re: Engine Room

04/29/2013 5:55 PM

So what do these generators sit on? Any time you can get a cooling advantage by adding natural convection for a generator room, it's usually a good idea. Passive intake vents around the bottom of the exterior wall, or maybe a swamp cooling system? I don't know what you deal with in your area regarding small pests like snakes and such, nor what is actually wise in practice for your location due to building materials and local temp/humidity conditions.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #10

Re: Engine Room

04/29/2013 7:17 PM

or maybe a swamp cooling system?

Oh that just made my day!

__________________
jack of all trades
Reply Off Topic (Score 5)