Single Phase 240 Volts to 3 Phase 240 Volts

05/30/2013 2:11 AM

Hello Group,

I'm looking for a way to produce a reliable and efficient 240 volt 3 Phase Power from residential 240 volt Single Phase. I know there are static converters but not quite sure how they work and I'm told their power output isn't clean enough for electronics, as the powered devices have servo motors, PLC'S and such.. There are rotary converters, which I understand the third leg is under powered because that third leg is induced by the stator to the winding.. Then there are transformers, which one guy claims on you tube you can build a home made transformer that he keeps covered up and has a bank of capacitors he switches in and out so I presume that isn't producing 120 degrees of separation per phase.. I've also seen two single phase transformers connected in a open delta configuration, don't see that having 120 degree separation either.. A VFD is also a consideration but I'm looking to have about 15 KW out, once you hit the 7.5 KW point they require 3 phase input, or is there a way to sync the output from two separate VFD's.. Any thoughts, considerations, ideas is appreciated.. Just trying at do this at the lowest price and not blow a ton of money on what doesn't work..

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: Single Phase 240volts to 3 Phase 240 volts

05/30/2013 2:22 AM

Not being the electronics electric guy, but what I woul do is to take a single phase motor driving a three phase generator.

Not cheap, not efficient but pretty straight forward.

__________________
Common Sense Dictates
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #1

Re: Single Phase 240volts to 3 Phase 240 volts

05/31/2013 6:35 AM

Correct, that is also how rotary converters work anyway, NOT as the OP thinks.

VFDs can also be used nowadays I believe.....set to a single frequency of course.

-------------------------------------------------------

What the OP has forgotten to mention is "How much single phase has he got available?", the number of amps would be enough.

How much 3 phase does he want to have, again amps per phase would be enough.

He cannot get more out than he put in, minus the amount lost due to inefficiency of the conversion/heat losses etc..

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Single Phase 240volts to 3 Phase 240 volts

05/30/2013 3:11 AM

15kW is north of 60A on a UK domestic single phase supply. Many houses have a supply fuse that opens at 80A, so that doesn't leave a lot of headroom for all the other things that get used around the home.

It might be worth getting the utility company to run-in a dedicated three-phase line. Another option would be to hire-in a generator for the time that the three-phase is needed and ditch it afterwards.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#3

Re: Single Phase 240volts to 3 Phase 240 volts

05/30/2013 8:24 AM

The power company's distribution system is true 3 phase. Get it thru a separate meter and service entrance. 15 kW is no problem.

All cases you listed are gimmicky, if you REALLY need clean power. To drive a three phase motor I would use one of them, as perfect phase or amplitude is no big concern.

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/30/2013 10:58 AM

Chances are that if you are looking at a machine tool (servos, PLCs etc), the power supplies for those devices are single phase anyway. So if you have a 3 phase motor, such as the spindle, then just get a VFD for only the 3 phase motor and separate out the other power circuits that connect to single phase, and make sure they are powered by you true AC single phase source. If you have multiple motors that need 3phase, and they do NOT need to vary the speed, a single VFD can power multiple motors. But if you want to vary the speed of one separately from others, use separate VFDs.

You can use almost any VFD as a phase converter, it's just that above certain sizes, you must double the VFD size with respect to the motor load and make sure AHEAD OF TIME by reading the manual that the VFDs Phase Loss detection (if any) can be defeated.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#5

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/30/2013 12:24 PM

Here you go. Miller 3 ph converter design.

All you need to know about making a good reliable and stable phase converter of your own.

I am the same guy there as here so I know the design works well!

Register to Reply Good Answer (Score 3)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/30/2013 3:37 PM

lets try this.....why don't you state how you intend to use the power, what you're trying to drive, etc, some of us might be able to help. 3 phase is generated quite efficiently by power companies, all the gimmicks you cited wont get you there

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/30/2013 3:47 PM

When it really boils down to it an additional 15kW is quite high to be pulling out of a residential supply. A separate 3-phase supply may be your best option and may be the cheapest solution too.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#8
In reply to #7

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/30/2013 5:58 PM

It must be a foreign thing. Around here it's standard issue to have a 200 amp 120/240 single phase service in the average home. Larger houses and farms are running 400 amp services now.

A buddy of mine built a new shop a few years ago with all electric heat and they stepped up his main service to a 600 amp system. 200 for the house 400 for the shop.

I have a 200 amp service on my place and I am already thinking that in a few years I may need to have that redone into a 400 amp feed.

To me his 15 Kw load seems completely normal by my standards. Heck my plasma cutter draws more than that and so does my 15 Hp air compressor when it starts.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jun 2012
Posts: 9
#9

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/31/2013 1:02 AM

Ok, here we go.. The load center I have in the house is a 200 amp panel, which is pretty standard these days in the USA, though the power company said they upgraded the service, but to me it looks like the old #6 aluminum wire that was there before.. The equipment I intend to connect will a lathe, mill, plasma cutter and welder. The lathe and mill are going to be converted to CNC control as well as the plasma table. The servo's I plan on using are 240 volt A/C either 1 phase or 3 phase. I figure in the long run it would be more efficient and cheaper to run every thing using 3 phase power. I plan to be adding more equipment in the future as well..

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#13
In reply to #9

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/31/2013 11:46 AM

Not really. You will be money ahead to just go ahead and pull the larger wire you need for the service.

To get 15 Kw off of a rotary unit it would need to be built out of a 20 HP electric motor plus the rest of the gear needed to make it into a phase converter would set you back close to $1000 or so if it was all done with new parts. I can't imagine that that cost plus the cost of the purchase and installation of the third line would ever pay for itself in power savings over just running the correct side of wire for the single phase supply.

At 15 KW on a 240 VAC service you are only drawing 63 amps peak which is safe to do on a 6 ga copper line or 4 ga aluminum line set unless you are more than 100 feet from the main service. At a short distance 6 ga aluminum will also handle 60 amps but does take short term peaks over that without issue.

Wire and Cable Ampacity ratings.

If you have issues with too much voltage drop before the main panel that is easily corrected by the utility company and their responsibility to keep up to meet the required service capacity codes and if it is after the main service $1000 - $1500 buys a lot of heavy 240 V 4 ga commercial power cord and few hassles over wiring codes being it's still technically just an extension cord.!

4 ga 3 conductor SOOW power cord. $7 a foot. Good for up to 70 amps cont and well over 100 peak.

4 ga 5 conductor SOOW power cord. $11 a foot. Double up on the two supply lines and you are good for 140 amps cont and well past your 200 amp service capacity peak.

Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#10

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/31/2013 1:39 AM

3 phase residential in the US may be close to unobtainium. It does exist in some parts.

If your going to convert the mill and lathe to CNC and you need speed control, then why not use a 240 VAC single phase input to 3 phase VFD out per speed controlled motor.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#12
In reply to #10

Re: Single Phase 240 Volts to 3 Phase 240 Volts

05/31/2013 9:43 AM

You can get 3 phase at a residence. You only have to lie to the power company and tell them you are starting a business in your garage/shop/storage shed/whatever. Show them the 3 phase equipment, which should appear to be equipment for a business, and they will swallow that line and will then run the 3 phase for you. Seen it done several times around here with used welding equipment - as long as the payments are sent on time, they never really check back to verify that a business does exist.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Off Topic (Score 5)
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Fredski (1); IdeaSmith (1); jack of all trades (1); JRaef (1); KeepItSimpleStupid (1); leveles (1); Phys (1); PWSlack (1); RElbe0579 (1); tcmtech (3)

Previous in Forum: Disturbance Recording   Next in Forum: Contact Gap in VCB

Advertisement