Reducer right?

06/01/2007 12:41 AM

Guys

Please please confirm

I am using a Vortex flowmeter which on standars requires a

1.5 ft / sec minimum velocity requirement, how could I achieve this velocity if I have a large pipe?

I think I have to install a reducer to increase the flow of my fluid to achieve the minimum flow requirement....

Am I right or do you have any ideas?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Reducer right?

06/01/2007 12:46 AM

sorry guys

wrong community

my bad

Reply
Associate
South Africa - Member - ShoSholoza Engineering Fields - Mechanical Engineering - New Member Popular Science - Weaponology - New Member

Join Date: May 2007
Location: South Africa
Posts: 44
#2

Re: Reducer right?

06/01/2007 12:50 AM

Yes, a reducer would increse the velocity. Flow rate constant, area decreases hence velocity increases [Q = A*V]

__________________
Can you imitate yourself?
Reply
Associate

Join Date: Jan 2007
Location: Chennai, India
Posts: 28
#3
In reply to #2

Re: Reducer right?

06/01/2007 2:11 AM

Yes, a reducer would increse the velocity. Flow rate constant, area decreases hence velocity increases [Q = A*V]

But take care of the pressure loss, if that is not an issue,reducer is good.

but a good engg practice is to size the pipe to meet the velocity of 1- 5 m/s

__________________
NatNat7
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Reducer right?

06/01/2007 4:30 AM

Yes, use reducers, though one needs to take into account any requirements imposed by the manufacturer in terms of the minimum diameters of straight pipe both upstream and downstream of the sending element. These requirements are to establish an even velocity profile across the pipe and are usually important in deciding the best pipe/location arrangements for flowmeters.

In large diameter pipes it is also necessary to make sure the pipe is full.

So if all else fails, read the instructions!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#5

Re: Reducer right?

06/01/2007 8:26 AM

Is that how you selected your flowmeter?

When we select flowmeters, we specify the nominal flow rate that is expected to flow through the tube and then select the size of the flowmeter that would satisfy the requirement.

Using this method, we never had problems with getting the minimum flow velocity through the tube. Occasionally, the flow tube would be smaller than our pipe which made a reducer necessary.

Keep in mind also that vortex flowmeters need several pipe diameters of straight pipe run after the reducer to minimize the turbulence created by the reducer. The manual will tell you how much. The ones we used specified 15 pipe diameters for reducers, 30 if you have elbows before the flowtube.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#6

Re: Reducer right?

06/02/2007 2:18 AM

Yes, using a reducer will increase the velocity with a pressure drop (ΔP must be calculated and studying its effects on total pressure and flow rate) . But you have to check with the supplier instructions if there is a limitations or not on upstream and down stream pipe lengths, with respect to the location of your flowmeter.

__________________
It is better to be defeated on principles, than to win on lies!
Reply
Power-User
Peru - Member - New Member Engineering Fields - Biomedical Engineering - New Member Popular Science - Genetics - New Member Fans of Old Computers - Commodore 64 - New Member

Join Date: Nov 2006
Location: Perú
Posts: 111
#7

Re: Reducer right?

06/02/2007 12:08 PM

Flowmeters Vortex:

Regardless of the numbers of shedder bars, all vortex flowmeters utilize the same basic design. As fluid moves around the shedder bars, vortices form and move downstream. The frequency of the vortices is directly proportional to flow rate. Vortices cause pressure fluctuations which are sensed, amplified, and converted to a 4 to 20 mA output.

To maintain system accuracy, a Reynolds number > 10,000 is needed.

To calculate, use the following formula: Reynolds number = DV/v

D=internal pipe diameter (m)

V=flow velocity (m/s)

v=Kinematic viscosity (m2/s) ♦ Water (v)=1*10-6m2/s

__________________
We must understand the things like are and not to try that they are as we want.
Reply
Power-User

Join Date: May 2007
Posts: 105
Good Answers: 3
#8

Re: Reducer right?

06/03/2007 8:36 AM

You need to put reducers to obtain the flow rate of 1.5 meters/sec. These should be eccentric reducers with the flat side on top to avoid air entrapment in the reducers and resultant turbulence. The counter flanges of the flow meter (i.e. flanges welded to piping and bolted to the flow meter) should be ground inside at the weld joints if required to obtain a smooth surface without any excess penetration of weld metal to avoid turbulence.

The normally used minimum straight length of pipes upstream and downstream of the flow meter are 20 times and 10 times respectively of the Nominal dia of pipes. However the manufacturer's recommendations should be observed.

Reply