Earth Conductor Sizing as Per IS 3043

06/18/2013 3:17 AM

The earth fault current dissipates throuh earth conductor surface area for which we also check necessary dissipation area . Please inform then why we are bounding minimum cross section area of earthing conductor by Ixroot(t)/k.What is the significance of this cross section of conductor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Earth Conductor Sizing as Per IS 3043

06/18/2013 8:55 AM
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5
In reply to #1

Re: Earth Conductor Sizing as Per IS 3043

06/19/2013 5:16 AM
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Earth Conductor Sizing as Per IS 3043

06/19/2013 8:53 AM

dhayanandhan,

Suggest you look again.

Scroll down and after the first page "Disclosure to Promote the Right To Information" and a blank page you will see that all 85 pages of Indian Standard CODE OF PRACTICE FOR EARTHING (First Revision)

Fourth Reprint June 2007 UDC 621316.99 : 006.76 is there in its entirety.

At least, that's what I get on my PC.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#7
In reply to #6

Re: Earth Conductor Sizing as Per IS 3043

06/19/2013 12:36 PM

Dear Mr. lyn,

Thank you very much for your guidance. Now I got it. When opened earlier, except the 1st page RIGHT TO INFORMATION, NOTHING WAS THERE.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Earth Conductor Sizing as Per IS 3043

06/19/2013 7:09 PM

dhayanandhan,

That omission may have been caused by the switch over of servers performed earlier today by sparkies.

There were many blank screens and blank parts of screens today, till the switch over was refined and the electrons were properly restrained and taught where to go.

Kindest Regards.

Register to Reply
Associate

Join Date: Nov 2009
Posts: 27
#2

Re: Earth Conductor Sizing as Per IS 3043

06/18/2013 1:52 PM

I have read that code in details with latest ammendment but not understood .Pleasae help

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Earth Conductor Sizing as Per IS 3043

06/19/2013 3:34 AM

Consult an Electrical Engineer locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#4
In reply to #2

Re: Earth Conductor Sizing as Per IS 3043

06/19/2013 4:52 AM

Keep reading....... Small hint: the selection of cross section of conductor is a function of time withstand capacity of the conductor, which in turn is based on required design defined parameters. This is the start point of any earthing system design.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: Earth Conductor Sizing as Per IS 3043

06/20/2013 3:04 AM

I wish you read IS 3043 a bit more carefully. In India, we largely follow the TN-S system, in which there is a dedicated, separate earthing protective conductor, to carry the earth fault current back to the source. Thus, in such a system the earth fault current does not flow through the natural earth. It is also documented in the first section of IS 3043 itself wherein it is stated that "the earth now rarely serves as a return path for the fault current....".

Thus, as a metallic conductor is going to carry the earth fault current, the cross section of the conductor is very much significant. (Ohm's Law)

Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (2); electricalexpert65 (1); lyn (3); Pattabhiraman (1); PWSlack (1); saraswata1981 (1)

Previous in Forum: Why WTG Has No Effect on This Circuit?   Next in Forum: Common ESD Trip

Advertisement