Common ESD Trip

06/18/2013 3:53 AM

Hi friends, please can someone enlighten me with a solution to this. I am having a 6.6 kV switchgear with 2 incomer feeders with bus section and 4 nos outgoing motor feeders all circuit breaker controlled (2 motors on each side of the bus section). There is a requirement to trip all the motors with one common ESD push button and I need to know how to wire this ESD pushbutton to all the motor feeders. Thanks in advance for your valued suggestion.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#1

Re: Common ESD trip

06/18/2013 5:18 AM

If your breakers are fitted with shunt trip coils, then, Use a emergency push button with 4 nos. potential free normally open contacts of suitable current make and carry rating. Each of the potential free contact should be wired to trip respective motor master trip relay ( in parallel with existing trip initiating contacts ), which in turn will trip the breaker through its shunt trip coil. If your breakers are fitted with no volt coils, then, Use a emergency push button with 4 nos. potential free normally closed contacts of suitable current break rating. Each of the potential free contact should be wired ( in series ) to interlocking logic circuit for permitting the no volt coil to latch and allow the breaker to close. Among the two options, building logic with no volt coil is preferable. Care should be taken that the control wiring amongst the breakers are not intermingled. Please take the help of a qualified electrical wire man for carrying out this modification.

Register to Reply Good Answer (Score 4)
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Common ESD Trip

06/18/2013 8:39 AM

If you don't know how to put this simple circuit together I really don't think you should be anywhere near 6.6KV switchgear.

As this is an emergency stop a relay or some device should de-latch to prevent the motors from being restarted.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: What I Should Have Learned in School, But Didn't

06/18/2013 8:46 AM
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Common ESD Trip

06/19/2013 2:45 AM

I can help you. Please send the control wiring diagram of one motor circuit feeder. I can mark in the diagram and submit to you so that you can incorporate in the panel.

Some one suggested the no volt coil. Generally there will not be any no volt coil on 6.6 kV switch gear. However no volt coil will be available in LT Switch gear.

It is preferable to use one push to lock push button with 4 individual NO Contact block.

It should be wired such a way that master trip relay picks up when push button is actuated. In turn master trip relay will trip the breaker

It is not advisable to actuate Switchgear Trip coil through push button element as the NO contact of Pushbutton element may not be able carry the current and over a period of time contact block will get damaged.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Off Topic
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#6
In reply to #4

Re: Common ESD Trip

06/19/2013 5:57 AM

Please do not skim read and answer. All points mentioned by you are covered in my reply, albeit qualified with "if", "suitable" etc.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#9
In reply to #6

Re: Common ESD Trip

06/19/2013 10:53 PM

Dear sir

It is not my intention to comment on other's answer. In the interest of the subject and helping the poster I have answered.

If I had hurt you, I am sorry for this.

ramesh

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 21
#7
In reply to #4

Re: Common ESD Trip

06/19/2013 7:41 AM

Thanks Ramesh and Pattabhi for your valued response, please find attached the control wiring of one motor feeder wherin I have marked within the cloud. Please advise, it shall be NC contact instead of NO contact.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#10
In reply to #7

Re: Common ESD Trip

06/19/2013 10:55 PM

The sketch is not readable.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Common ESD Trip

06/19/2013 3:33 AM

Are the equipment manufacturer's "as-built" drawings unavailable for some reason?

Is the equipment manufacturer's telephone number unavailable for some reason?

Are local electrical engineering companies' telephone numbers unavailable for some reason?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8

Re: Common ESD Trip

06/19/2013 5:27 PM

"Please advise, it shall be NC contact instead of NO contact."

I rest my case.

<unsubscribe>

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

lyn (2); Pattabhiraman (2); PWSlack (1); ramvinod (3); TonyS (1); vinsue (1)