Short Circuit Rating of Cable

12/06/2012 4:29 AM

Hi guys, just need your professional opinion, if the short circuit rating of 22 kV Switchgear busbar is 40 kA for 1 sec, should I size the outgoing cables for Short circuit 40 kA/1sec too? Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Short circuit rating of cable

12/06/2012 4:45 AM

What does the characteristic curve of the circuit overload protective device look like?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Short circuit rating of cable

12/06/2012 5:06 AM

Only if you want every wire in the facility to be as large as the bus bar....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Short Circuit Rating of Cable

12/06/2012 1:22 PM

You should size based on the upstream and downstream protective settings which should hopefully be lower, if not then yes unless you want to do a study to calculate fault currents at various points upstream and downstream of the switchgear to get the actual maximum expected fault current.

Remember, the switchgear may be rated for 40kA/1sec but the supply never has infinite capacity and the cabling is never a perfect conductor.

__________________
jack of all trades
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Short Circuit Rating of Cable

12/07/2012 12:35 AM

I agree, of course, with jack.

You have to recalculate the short-circuit current at the end of the cable. The resistance and the reactance of the cable could reduce the current dramatically.

Second, usually 0.1 sec it is enough time to clear the short circuit.

If the cable is XLPE or EPR insulated the maximum temperature it is 250 deg.C.

If you need to take into consideration a reserve protection 0.15-0.2 sec still will be fair.

For 0.15 sec [for adiabatic phenomenon] 250 MCM at 40 KA [rms] will be the minimum copper cross section.

__________________
Julius
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#7
In reply to #4

Re: Short Circuit Rating of Cable

12/10/2012 8:07 AM

Beware, 0,1 sec seems a bit short . It depends on your protection scheme, this time may be mich longer specially in MV where you have time discrimination.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8
In reply to #7

Re: Short Circuit Rating of Cable

12/11/2012 12:51 AM

I agree with you, obouill, it is very short, but 5 cycles [total] clearing fault it is still possible.

__________________
Julius
Register to Reply
Member

Join Date: Aug 2011
Posts: 5
#5

Re: Short Circuit Rating of Cable

12/07/2012 8:51 AM

It is depend on your design philosophy.

1. primary protection tripping time (relay 50/51 of outgoing feeder)

2. secondary protection tripping time (relay 50/51 of main breaker)

If you are a good engineer with money to invest, choose cable to tolerate SC time in 2.

If you are on budget, choose cable rating of SC time in 1.

Now you know what I mean.

Register to Reply
Anonymous Poster #1
#6
In reply to #5

Re: Short Circuit Rating of Cable

12/08/2012 6:05 AM

"Now you know what I mean." No?

Register to Reply
Commentator

Join Date: Jan 2013
Posts: 70
#9

Re: Short Circuit Rating of Cable

06/18/2013 1:29 PM

I agree with Jack.

But also the cable manufacturer catalog shall give to you a curve showing the maximum admisible sc againt time in sec., ask for this information.

Bye ( now definitive becouse tomorro I lose the computer and internet, Chaoooo Dear friends)

Register to Reply
Register to Reply 9 comments