10/11/2012 6:19 AM
Hi Friends, What will be the MVA rating of the 22/6.6 kV transformer to feed a 4.65 MW unit motor 6.6kV, 3PH, 50Hz, FLC=625A and starting current (Is/Ir) = 4.67, PF@ full load=0.93, PF@ starting=0.15. Infact can anyone provide me a guideline how to do the calculation or is there any thumb rule. Thanks in advance for your valued advice.
Good Answers: 137
Re: Transformer rating for unit motor
10/11/2012 6:28 AM
What's a unit motor?
10/11/2012 11:27 AM
Unit motor means one transformer to feed one motor
10/11/2012 7:14 AM
I have some confusion related to the given motor name plate 1. Confirm P.F is 0.93 at Full Load. 2. Confirm nameplate is correctly stated. Repeating the given Nameplate : 4650 KW, 6600 V, 50 Hz, 625 A, P.F 0.93 , (may be 994 RPM) Electrical Power = 1.732 * V * I * P.F Electrical Power = 1.732 * 6600 * 625 * 0.93 = 6644.38 KW Assume motor is 95 % efficient Mechanical Power = Electrical Power * Efficiency = 6644.38 * 0.95 = 6312 KW But according to given nameplate data it is 6312 KW instead it should be in the range between 4600 to 4800 KW. As per my understanding the nameplate may be: 4650 KW, 6600 V, 50 Hz, 487 A, P.F 0.87 Please confirm the exact name plate so that we proceed further toward the main problem. Thanks in advance
Good Answers: 34
Re: Transformer Rating for Unit Motor
10/11/2012 1:57 PM
What is the starting method, DOL, soft starting etc.? What will be the starting torque?
10/12/2012 12:52 AM
3. Is it a Wound Induction motor (having Liquid Resistance Starter) ?
Thanks in advance
Aghvel Niazi
10/13/2012 12:28 AM
The starting method is DOL. The starting torque is 19162 Nm.
10/12/2012 12:57 AM
Please go through the following:
http://mcglynnconsultancy.co.uk/html/tx_sizing.html
This will give you complete guidance on your question and the solved example will further help you.
10/12/2012 8:43 AM
Thank You my Friend, it was helpful
10/12/2012 10:22 AM
Rule of thumb: 1 KVA per HP.