NiCd Battery Ah Calculation

01/15/2012 5:16 AM

I need to replace existing Alcad VN357-2 batteries connected in series parallel, the nominal voltage is 48V, the total nos. of batteries are 70 nos., 2 cells per battery(2.4V) and the discharge capacity at 5 hour rate is 357 Ah. Can anybody kindly tell me how to caculate the total Ah?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: NiCd Battery Ah Calculation

01/15/2012 10:39 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: NiCd Battery Ah Calculation

01/16/2012 5:03 AM

2.4V into 48V gives 20.

20 x 3 is 60. => 3 strings of 20 batteries in parallel.

If each battery is 357Ah then the Ah capacity of the 3 strings is 3 x 357Ah = 1071Ah @ 48V.

What happens to the 10 batteries left over?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#3
In reply to #2

Re: NiCd Battery Ah Calculation

01/16/2012 7:00 AM

i get the impression that the capacity of the whole assembly is 357 Ah, so each of 3 hypothetical strings must have a capacity of 119 Ah, which must also be the capacity of a single cell. The problem is that I have never seen and cannot find an NiCD cell with a capacity of more than 2 Ah, so there may be a decimal point problem somewhere, or we should be going to sealed lead-acid batteries.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: NiCd Battery Ah Calculation

01/16/2012 8:58 AM

If only the original poster would say....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#5

Re: NiCd Battery Ah Calculation

01/16/2012 2:54 PM

I suspect that you have 72 batteries three strings of 24. You only get the 357 Ah if you discharge them to 1V (2 volts for each pair): so that's a total of 1,071 Ah.

Alternatively you may have 4 strings of 18 (still 72 batteries). Fully discharged (down to the 1V/2V level) you'd still have 36V, which seems like a reasonable minimum for equipment spec'd to run on nominal 48V. That would give you 1,428 Ah.

Over 3000 Kg of batteries WOW!

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#7
In reply to #5

Re: NiCd Battery Ah Calculation

01/16/2012 4:48 PM

These question can be more of a puzzle than our challenge questions.

Because the OP has mentioned both 2.4V individual battery voltage and 48 volt nominal, and because the 2.4 v is the correct nominal voltage of the Alcad VN357-2 battery, I'm guessing that there must be 20 such batteries per string -- leaving one to wonder where the extra 10 cells go (after paralleling three such strings.)

Putting 3.5 parallel strings in a car would result in castration of the perpetrator. But apparently it is done in the telecom industry.

Or the op's finger slipped, and he typed 70 when he meant 60.

__________________
Think big. Drive small.
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#6

Re: NiCd Battery Ah Calculation

01/16/2012 4:32 PM

This does not add up in the traditional way.

To keep with the existing terminology, I'll call two cells in series a battery. The whole group of series parallel cells I'll call a pack.

Each battery of two cells in series is 2.4V nominal. Therefore, to make 48V nominal, you would need 20 such batteries in series. Then paralleling these in 3.5 sets would give you 70 batteries, for 1249.5 Ah. Of course, you cannot parallel the last 10 batteries as a series string across any existing 48 volt string. The 10 additional batteries could be added at random to the pack (each in parallel with any 2.4V battery) or first connected in series and paralleled with a 24 volt group.

This never used to be done, but apparently works -- although it would seem to cause problems in keeping the pack balanced. Here's an article.

__________________