Anonymous Poster #1

350 kVar Capacitor Bank

07/01/2013 7:14 AM

there is a requirement for 350Kvar Capacitor Bank. In the SLD it is mentioned as 10 nos of 35KVar Capacitors. But i couldnt find any 35Kvar Capacitors ...So i offered 2nos 50Kvar capacitor and 10 25KVA Capacitors....it was rejected by the client....can i get any technical Justification as to why it happened...the client s not telling me y, but simply he s rejecting....can any guys help

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 350 kvar capacitor bank

07/01/2013 7:41 AM

In the absence of a telephone conversation to determine why it was rejected, try offering 7 x 50kVar on the basis of the unavailability of 35kVar. That way, it could all go on for years...

http://www.google.co.uk/#safe=active&q=35+kVAr+capacitors&spell=1&sa=X&ei=UG3RUf24LYm-0QWvp4H4CQ&ved=0CCgQBSgA&bav=on.2,or.r_qf.&bvm=bv.48572450,d.d2k&fp=63298ca061231fce&biw=1035&bih=548

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#2
In reply to #1

Re: 350 kvar capacitor bank

07/01/2013 10:44 AM

How about 14 25kVar's?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: 350 kvar capacitor bank

07/01/2013 11:07 AM

Would the Client reject it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4
In reply to #3

Re: 350 kvar capacitor bank

07/01/2013 11:10 AM

Probably not, but we could keep this strung out longer

Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#5

Re: 350 kVar Capacitor Bank

07/01/2013 1:00 PM

Your answer is of course fully technically correct . The only reason why I could imagine your customer rejhected it is the multiplication of spares . With 10 identical capacitors, he needs only one spare in case he wants to have one ...

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6

Re: 350 kVar Capacitor Bank

07/01/2013 9:52 PM

Tell the client that technically the capacitors are added or switched off in steps and for that reason they are normally provided in small denominations. Otherwise proper PF correction cannot be done for the system. Depending up on the minimum requirement 50 kVAR may be connected permentantly and the rest to be added in steps. the 25 kVAR can be switched on and off for fine control. Tell them that your proposal is technically more efficient for smooth and efficient power factor correction. (But the client may require suitable switching system to put the system to operation, actually his system may be designed for 10 step switching hence not accepting your proposal.)

Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#7
In reply to #6

Re: 350 kVar Capacitor Bank

07/01/2013 10:35 PM

Yes.

And the secondary consideration of the circulating currents passing thru every individual capacitor. Their margins, their heating. Hence their life expectancy. If the customer has any estimates, he is right on insisting of being convinced, with data.

Reply
Participant

Join Date: May 2013
Posts: 4
#8

Re: 350 kVar Capacitor Bank

07/02/2013 1:13 AM

Dear all

10 no 35 Kvar is not wrong ,where ever if the step of contoller is increased it is fine tune with PF relay & it will better maintained.If to take 12 step relay then take 5x50kvar +3x25kvar +2x10kvar +1x5kvar +1step spare better for operation.

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#17
In reply to #8

Re: 350 kVAR Capacitor Bank

07/02/2013 6:39 AM

There are standard APFC controllers who have specific preset programme depending on your load conditions and variations of PF depending on how much capacitance need to be added automatically and what PF level to be maintained to avoid low PF penality. If the PF is to be controlled properly with the exact desired amount of capacitance to be added is to be chosen by a technical study of the load. So it is not the job of a layman but the job of an experienced designer. So the actual user only can deside what steps are to be programmed and when to add depending on his load conditions. Some loads may be highly inductive ( like Induction Heating )and even though they may have in built PF correction a back up correction at Substation will be needed to maintain proper PF of the system.

Reply
Active Contributor

Join Date: Apr 2013
Location: East Africa
Posts: 19
#9

Re: 350 kVar Capacitor Bank

07/02/2013 1:49 AM

From your mail, u said the client needs a Capacitor Bank, Meaning your client only need the bank comprising of 10x35KVar capacitor because they already have the Switching controller which is 10steps and hence if you offer 12 Capacitors thats 12 Steps switching which is not going to work with the available 10 step switching controller because the other 2 Capacitors will be up for waste

Possibly the reason they cant accept your offer.

__________________
"Do not follow where the path may lead. Go instead where there is no path and leave a trail."
Reply
Participant

Join Date: May 2013
Posts: 4
#10
In reply to #9

Re: 350 kVar Capacitor Bank

07/02/2013 2:14 AM

As per my view 10 step is correct but the subject to avialability of 35 kvar.As 10 & 12 step controller cost is merely same ,it is better to take 12 instead of 10 for fine tune & life of bank.

Reply
Anonymous Poster #2
#11

Re: 350 kVar Capacitor Bank

07/02/2013 2:37 AM

If 35 KVAR Capacitor is not available as a single unit, your basic lack of engineering knowledge is preventing you from combining two or more units of say 25 + 10 KVAR to achieve the required per unit bank.

The client is only rejecting your lack of technical knowledge but has the decency not to tell to your face.

Reply
Participant

Join Date: May 2013
Posts: 4
#12
In reply to #11

Re: 350 kVar Capacitor Bank

07/02/2013 2:45 AM

Its based on client design data not mine,so what,s lack.

Reply
Active Contributor

Join Date: Apr 2013
Location: East Africa
Posts: 19
#13
In reply to #12

Re: 350 kVar Capacitor Bank

07/02/2013 2:54 AM

Like what i said in my last mail, the client seems to have already the 10 step controller, i advice u suggest any combination that leads to 10 steps and present to your client not 12 Capacitors coz thats will mean the client now suppose to change the controller to accomodate 12 steps.

Hope were Talking the same language Here ...

__________________
"Do not follow where the path may lead. Go instead where there is no path and leave a trail."
Reply
Participant

Join Date: May 2013
Posts: 4
#15
In reply to #13

Re: 350 kVar Capacitor Bank

07/02/2013 3:08 AM

Try to convince ur client bcos its the the right d/n to adopt.

Reply
Anonymous Poster #2
#14
In reply to #12

Re: 350 kVar Capacitor Bank

07/02/2013 3:07 AM

Does the client design data specifically exclude use of parallel connection of two banks to achieve the required 35 KVAR stage. It is basic engineering. I have personally combined and used various such combinations and had no problem whatsoever.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16

Re: 350 kVar Capacitor Bank

07/02/2013 3:20 AM

Maybe some sources can be found by searching for "35 kvar capacitor" on line.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#18

Re: 350 kVar Capacitor Bank

07/02/2013 7:19 AM

Is it thyristor based switching or contactor based switching. Is any voltage rating specified. Why not follow combination bank as already suggested by other peer.

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#19

Re: 350 kVar Capacitor Bank

07/02/2013 8:44 AM

You could use higher voltage capacitor banks at a lower voltage to achieve your goal.

660V 50Kvar rated banks give you about 35kvars at 480V. They will last for ever!

The problem is that they cost more and are bigger...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply