Restart of Motor After Stopping It

07/13/2013 11:29 AM

Hi, would like to know the effects of restarting a motor right after stopping it. The restart interval was trended to be 1 sec after a stop signal was initiated. Under such scenario whereby the rotor current may still be present and yet fully decay.. How will the transient effect affects the electrical compoent such as contactor in the starter? Will i expect ahigher inrush current as a result of this? Though rotor speed is stil high at the point of restart

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Restart of motor after stopping it

07/13/2013 11:33 AM

Is this a trick question? First you say, "restarting a motor right after stopping it".

Then, it's, "Though rotor speed is stil high at the point of restart".

Make up your mind. Is it stopped or just de-energized?

Try it 5,000 times and report your findings back here.

My uneducated guess is that there will be no effect.

What's your uneducated guess?

Register to Reply
Member

Join Date: Jul 2013
Posts: 8
#2
In reply to #1

Re: Restart of motor after stopping it

07/13/2013 11:45 AM

Sorry for confusing. What i meant was at the point of restart, the rotor is still turning. Hence does it mean lesser torque and amps required to run motor back to near syns speed?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Restart of motor after stopping it

07/13/2013 11:47 AM

Yes. Less rotor inertia to overcome.

Register to Reply
Member

Join Date: Jul 2013
Posts: 8
#4
In reply to #3

Re: Restart of motor after stopping it

07/13/2013 11:53 AM

Thanks for the reply. This is a DOL starter design. And while the contactor opened and reclosed..is there a possibility of closing 2 voltage sources of different phase? Namely one from the swgr and the other source from residual voltage of the motor? will this accelerate failure on the contacts of the contactor?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Restart of motor after stopping it

07/13/2013 11:58 AM

Do you mean something like:
Backfeeding - Wikipedia, the free encyclopedia

I'm taking myself out of this thread. There are many here who are far more qualified than I to speak to this subject.

Good luck.

Register to Reply
Member

Join Date: Jul 2013
Posts: 8
#6
In reply to #4

Re: Restart of motor after stopping it

07/13/2013 12:15 PM

Hi,,what i meant was closing the contactor on 2 separate voltages that is not in sync? Will it damage or burnt the contacts upon closing?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Restart of motor after stopping it

07/13/2013 12:36 PM

I'd worry more about the motor windings than the contactor.

Wait for the experts to get here.

Register to Reply
Member

Join Date: Jul 2013
Posts: 8
#9
In reply to #7

Re: Restart of motor after stopping it

07/13/2013 12:42 PM

Thanks lyn. For my case..the contactor was fused and burnt. Have yet to determine if the root cause was a result of this. Anyway..i thank you again

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26
In reply to #2

Re: Restart of motor after stopping it

07/15/2013 3:45 AM

<...lesser torque...>

It is the load that presents the torque to the motor. So if it is still rotating while de-energised, as would be the case were it to be driving a humungous flywheel, the motor would experience very little torque were power to be re-applied.

It wouldn't still be rotating were it to be turning a centrifugal pump, or something similar that had very little rotational inertia. Were the power to be reapplied here, the full starting load would be applied to the incoming supply.

Nothing would see any significant distress were it to be correctly sized and rated for the application. If it were not rated for frequent multiple re-starts, then it behoves the circuit designer to introduce such (a) device(s) to the starter, either hardware or software, that would prevent the maximum permissible frequency of starting to be exceeded.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Restart of motor after stopping it

07/13/2013 12:41 PM

So now that we determined that you mean "re-energizing a motor immediately after de-energizing it", we can get somewhere.

The salient issue is residual magnetic fields. If you re-energize a motor BEFORE the stator magnetic fields have COMPLETELY collapsed, then yes, you will potentially be re-energizing into a regenerating motor that is out of phase with the line and the effects can be disastrous, not only to the electrical system, but also to the motor. In theory you can create a brief yet extreme voltage transient, with a corresponding severe current transient as high as 2200% of the motor FLA. That then translates to a severe torque transient that has been known to shear motor shafts, couplings and gearbox shaft keys, as well as damage belts and break gear teeth.

The amount of time it takes for the motor fields to collapse is not predictable, it depends on the motor construction and the magnetic permeability of the steel used in the laminations, which affects the overall residual magnetism in the stator and rotor. Large motors have been known to hold up for several seconds, so a one second re-start can indeed be extremely risky. Most high end motor protection relays used for large AC motors have a "Minimum Time Between Starts" protection function that is recommended to be no less than 5 seconds, but your mileage may vary.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Member

Join Date: Jul 2013
Posts: 8
#10
In reply to #8

Re: Restart of motor after stopping it

07/13/2013 12:57 PM

Thanks JRaef.your reply is consistent with the observation of a trend recorder which i had placed on the system. Whereby the motor drawn current was trended to be over- range at every time of the motor restart , which i was not able to explain. The motor is a 380vac, 75kw motor. Just a question, if indeed there is residual mag field in the system ..does it make semse to say that the contactor is literally closing/ making on a possible fault condition?

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#12
In reply to #10

Re: Restart of motor after stopping it

07/13/2013 5:06 PM

Just an observation, I have worked in heavy industry for over 40 years. In this time I have had in operation many thousands of electrically driven motors. Some operated by Lug-head operators who could not even tell what time of day it was and others put in by automation experts that couldn't even spell expert and have never seen a failure as such. Now I know I have not seen it all, but I have to believe that the engineering departments at the big name motor manufacturers have worked this one out long ago. So people like me don't have to worry about replacing their motors when some Lug-head miss starts a motor. Just my guess.

So having said all of that, what are you trying to do with this information?

Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#14
In reply to #10

Re: Restart of motor after stopping it

07/13/2013 11:28 PM

Which country is that allowing a 75kW motor to start with DOL starter??

Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#25
In reply to #14

Re: Restart of motor after stopping it

07/14/2013 11:16 AM

By the way, which country prevents it?

It is agreed that starting large motors direct-on-line causes huge voltage drops in the system due to the large starting current magnitude. But, this becomes a social issue only when the power supply for the motor is drawn from Low Voltage lines, because if you start a higher than prescribed HP motor Direct-on-Line, the LV line voltage drop might affect the loads of a neighbour connected to the same LV line. Thus, the authorities of respective provinces might impose certain limitations as to the largest capacity motor that could be started Direct-on-Line, say 7.5HP or 10HP. But, such regulations are applicable only to LV customers.

As regards a HV customer, any such DOL starting of a motor may not affect a neighbouring HV customer, as there would be a transformer absorbing the voltage drop. Also, in HV terms, the voltage drop might be insignificant to cause worries to your HV neighbour's loads. So, if you are a HV customer, it is your discretion that would limit the largest size of motor that could be started DOL.

In my experience, there are instances where I had to go for star-delta starting even for a 15HP motor and DOL starter for motors as high as 400HP.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#19
In reply to #10

Re: Restart of motor after stopping it

07/14/2013 6:04 AM

The Motor speed is droping when disconnected and may be driven by the load inertia for some time, thus generating a voltage and current in the motor.

When reconnected, the shorter the time of disconnection, the less damage since the synchronising issue will be less significant, having an almost synchronised opposing voltage that will be quickly oercome (and not an additive current flow).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#29
In reply to #19

Re: Restart of motor after stopping it

07/15/2013 10:53 AM

<...The Motor speed is droping when disconnected and may be driven by the load inertia for some time, thus generating a voltage and current in the motor....>

Where does the magnetic field come from with which to generate this voltage?

How does current come out of the motor if, from the moment it was disconnected to de-energise onwards, there is no connection to the supply?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#32
In reply to #29

Re: Restart of motor after stopping it

07/15/2013 12:47 PM

Well, it depends on the type of motor, its size and any remnant magnetism that might remain ... The field might not have completely died if the re-start time is very short (?) I am not disputing the fact that if the re-connection happens after 1 second, you could assume that there will be no current flow, but action reaction of the dyeing fields could still produce some current at the moment of re-connecting.

By the way, You must have heard of what is called "Regenerative power" when a motor is driven by the load inertia after disconnection. Google it. This regenerated power is sometime sent back the mains grid. Depending on the Motor type and size, this could be significant enough when dealing with VFD's. You could also use this effect to slow or Brake the motor ...

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#37
In reply to #32

Re: Restart of motor after stopping it

07/16/2013 5:12 AM

Fine with regeneration in principle

As the thread has progressed, the motor type has been revealed as induction, which type is not renowned for use in regenerating systems. One awaits developments.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#35
In reply to #8

Re: Restart of motor after stopping it

07/16/2013 4:36 AM

.....

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#36
In reply to #8

Re: Restart of motor after stopping it

07/16/2013 4:46 AM

Excellent explanation by the most consistent & reliable person........

__________________
"Know something about everything and everything about something"
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11

Re: Restart of Motor After Stopping It

07/13/2013 4:01 PM

You have not told us the type of motor, although everyone is assuming it is an induction motor it may not be. As Jraef has pointed out, the construction of the rotor plays a very large part in determining the strength of the magnetic field, and the resultant time it takes to decay.

Another thing to consider is the load that is being driven and its inertia. While a lightly loaded motor may not take much energy to pull up to speed, high inertia systems will require great mechanical force to do so, and that will come as a huge inrush current, sufficient to melt your contactor shut.

If this is combined with a large residual voltage that is sufficiently out of phase with the line voltage, then the contactor and motor windings may be subject to voltages that are near twice normal. This coupled with the excessive mechanical forces point to a complete inspection of the motor and its external components. Please let us know what you find.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Jul 2013
Posts: 8
#21
In reply to #11

Re: Restart of Motor After Stopping It

07/14/2013 7:31 AM

Thank you for all your contribution. I have received good guidiance here. The motor is of imduction type and i will be following up with more trends at faster sampling rate to verify the suspects transient effect. I am not comfortable with what i have observed at site..which was to restart almist immeidately after stopping. Will be verifying the cause of this switching. Will keep you all posted on my finding. Tks

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13

Re: Restart of Motor After Stopping It

07/13/2013 6:06 PM

See "plugging duty" motors and starters.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #13

Re: Restart of Motor After Stopping It

07/14/2013 2:49 AM

I'm curious to know why someone thinks that is off topic.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#22
In reply to #16

Re: Restart of Motor After Stopping It

07/14/2013 9:15 AM

It isn't now.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#15

Re: Restart of Motor After Stopping It

07/14/2013 2:03 AM

What will be the result if the motor is driven by VFD?

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#38
In reply to #15

Re: Restart of Motor After Stopping It

07/16/2013 5:14 AM

[Undoes 1 off-topic vote] Very little difference from if it weren't. After all, the motor doesn't care where the power comes from!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#40
In reply to #38

Re: Restart of Motor After Stopping It

07/17/2013 2:12 AM

There is provisions in our VFD for "fly start". Means motor can be stsrted while it is in rotation. I thaink in that cace there shoud be a provision in VFD to match the phase angle before switching ON. ?

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#41
In reply to #40

Re: Restart of Motor After Stopping It

07/17/2013 6:17 AM

Yes, it matches the frequency, phase and voltage.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#44
In reply to #40

Re: Restart of Motor After Stopping It

07/25/2024 3:25 AM

So, make sure that facility is programmed-in, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17

Re: Restart of Motor After Stopping It

07/14/2013 3:50 AM

I wander how an Automatic Transfer Switch will assure induction motor operation continuity.

__________________
Julius
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#39
In reply to #17

Re: Restart of Motor After Stopping It

07/16/2013 9:56 PM

It won't, unless it is extremely fast, intelligent, and very expensive. Only added mechanical inertia in the form of a flywheel, or electrical inertia in the form of a continuously available bumpless transfer UPS system, will keep the machine operating. This assumes, of course, that the contactor didn't open due to a legitimate problem somewhere.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate
Australia - Member - New Member

Join Date: Jun 2013
Location: Central Victoria Australia
Posts: 45
#18

Re: Restart of Motor After Stopping It

07/14/2013 4:18 AM

Check your starter duty specs I was always told that you will not hurt the motor but the starter may overheat with too many close excitements. Farmer---Jack of all trades and master of none.

__________________
Luck definately comes and goes----- I had a win today,,,,I saw the sun rise.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#20

Re: Restart of Motor After Stopping It

07/14/2013 7:04 AM
__________________
Julius
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2011
Posts: 20
#23
In reply to #20

Re: Restart of Motor After Stopping It

07/14/2013 9:53 AM

In my factory I have new big motor, the manual are inform not to start directly after stop. But wait until 15 minutes. Maybe this is for waiting the residual magnetic fade away.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#24
In reply to #23

Re: Restart of Motor After Stopping It

07/14/2013 11:03 AM

Actually, this is recommended for another reason: Prevent Overheating due to starting current!

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#27

Re: Restart of Motor After Stopping It

07/15/2013 5:42 AM

If the motor is de-energised, then no rotor current can be present.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor
Engineering Fields - Power Engineering - Thermal Power Plant Electrical Engineer

Join Date: Sep 2010
Location: INDIA
Posts: 18
#28

Re: Restart of Motor After Stopping It

07/15/2013 9:47 AM

In our plant, we have faced a similar problem.. we have 200KW compressor motor which run continuously,once it stopped and started immediately, then the motor burned.The reason is "as motor is started in "HOT CURVE" mode and it has drawn 4 to 6 times of its rated current in hot mode, so the motor failed.

So, u have to consider weather you are starting the motor in "HOT curve" or "COLD curve" mode also matters.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#31
In reply to #28

Re: Restart of Motor After Stopping It

07/15/2013 12:31 PM

Most likely, it is the fact that a compressor produces pressure upstream and re-starting it immediately will mean that the motor has to overcome the esisting back pressure which did not have time to dissipate! You are supposed to start such equipment with no back pressure!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#30

Re: Restart of Motor After Stopping It

07/15/2013 10:55 AM

If it is to be re-started 1 sec after stopping, it may be better to avoid stopping it altogether.

So why is a 1 second stop required, please? Can it be avoided by more sensible process requirements?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#33
In reply to #30

Re: Restart of Motor After Stopping It

07/15/2013 12:50 PM

Here also you are trying to tell him what to do instead of explaining why he is getting or think that he is getting whatever he stated.... Maube he is experimenting ???

Register to Reply
7
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#34

Re: Restart of Motor After Stopping It

07/15/2013 1:18 PM

The magnetic field of a running machine just prior to de-energization is the same immediately after de-energization. This MMF does not collapse immediately but decays exponentially according to the time constants that are based upon the construction of the motor.

Depending on the size of the motor and in particular the type of rotor, these transients can be from sub-cycle to many cycles long. During the period when the rotor is decelerating and the field is decaying, the motor acts as a generator producing a decaying voltage that is sub-synchronous and out of phase (except once every 360º) with the original line frequency.

Re-energizing the motor before this voltage has decayed sufficiently is no different than trying to synchronize a generator whose voltage, speed, and phase are not all precisely matched. If you're lucky and you're within a few percent of where you should be then you probably won't notice much more than the ammeters and voltmeters dip/pop momentarily.

If you're really unlucky and you do it under the worst possible conditions (residual voltage > 75%, speed < 95%, 180° out of phase, and driving a high inertia mechanical load)) then you subject your motor to up to 2.0 times normal voltage and/or 12 to 25 times normal current, which can shift the stator windings, shear the shaft, and/or tear the motor off its base.

That's why unless you have a very intelligent high speed transfer scheme, time delays of sufficient duration (5 to 10 time constants) are required to prevent reclosing of breakers and ATSs (Automatic Transfer Switches) until those transients have decayed to safe levels.

As others have pointed out, time between hot motor restarts is an entirely different matter. The thermal time constants are on the order of minutes to hours, and the timing is intended to prevent adding the heat from the restart to an already at-temperature machine and thereby overheating it.

However the damage described by the OP is unlikely to have been caused by thermal overload since the incremental current increase due to hot windings would be within the limits of the contactor rating, also the damage would show up inside the motor. In this case all evidence points to the the damage being consistent with out of sync reclosing.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 7)
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#42
In reply to #34

Re: Restart of Motor After Stopping It

07/27/2013 3:19 AM

Is there a upper limit for restarting just like minimum time between stop & start?.Reacceleration can be done at any time after motor stops?Generally 8sec is the maximum time set almost everywhere.

Thanks

__________________
"Know something about everything and everything about something"
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#43
In reply to #42

Re: Restart of Motor After Stopping It

07/28/2013 1:29 AM

Your question requires clarification. Are you asking if 1. there is an upper limit to the amount of time it takes to accelerate a motor , 2. if you can reaccelerate (restart) a motor any time after is de-energized, or from zero speed, 3. if 8 seconds is some kind of recommended number to get from zero speed to full speed?

If so then the answer is generally No to all of them, it is highly dependent upon the motor size and design, the type of load and its inertia, and the number of attempts and amount of time between tries. Restarting a stopped heavily loaded motor every 8 seconds will quickly overheat it unless it is specifically designed for plugging duty.

The manufacturer is the only one knowledgeable enough to answer these questions correctly.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#45

Re: Restart of Motor After Stopping It

08/06/2024 10:51 AM

It is not clear as to whether the restart is after motor comes to stop or while still coasting to stop.If a motor is started from rest after switching off and while in hot condition manufacturers recommendation on hot starts to be followed.Normaly up to 160 Kw (4P) 3 cold and 2 hot starts are allowed but can change depending upon severity of application.For MV motors and large LV motors manufacturers usually furnish number of hot and cold starts it can have but mostly one hot start is allowed.If restart is attempted while motor is still coasting voltage applied can be in phase with residual voltage and create mechanical forces particularly on end which are braced and motors are designed for this as now a days in many places especially in power stations auto bus transfer is allowed and motors face similar condition.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 45 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments: