Previous in Forum: Roll Center of Vehicle   Next in Forum: 5 Ton Split AC Gas/Electric
DM Water Heating
07/22/2013 3:27 AM
Can I use LP steam before desuperheating which is the extraction of our 14.5MW turbine(i/l hp steam pressure 62 kg/cm2) to heat the dm water of a 90tph afbc boiler? If it can what type of equipment I to use for heat exchanging..please specify
Parameters:
lp steam: pressure : 4.5 kg/cm2
temperature: 201(before desuperheating)
avg flow : 90 to 110 tph
dm water pressure : 6.5 kg/cm2
temperature : 65 degC(dearator i/l)
average flow : 70 to 80 tph
Re: dm water heating
07/22/2013 3:38 AM
If the steam is clean, then a simple sparge pipe into the boiler hotwell may be all that is needed, although why the equipment is not provided already is a bit curious, as is the need to use steam to heat water to make steam; if the second boiler is of lower pressure than the first, then a pressure regulating valve between the HP and LP systems is all that is needed.
If additional equipment is needed then compact plate heat exchangers are readily available and an internet search will reveal local suppliers.
It sounds as though an experienced Utilities Engineer is needed for a short period to effect the design.
Look at ways of maximising the return and re-use of steam condensate from the downstream users, as this will considerably enhance the economics of the operation and payback from investment in installed equipment is usually short.
07/26/2013 5:43 PM
here we are running utilities department in a paper mill.the outlet steam of turbines is need for paper m/c's.thats why the reheater equipment not provided.but now i am a bit curious to meke it possible.and thanks for ur sugegestion
Re: DM Water Heating
07/23/2013 1:51 PM
Dear Mr.srik231,
YES. You can heat the DM Water. You have to use a Tubular Heater of Proper Design.
We are using the Blow-Down Water from the Boiler at 282 Deg.C, for heating the Condensate from 46 Deg.C as well as DM Water from 32 Deg.C and the Boiler Capacity is 90Tonnes and Power Turbine is 17.5 MW. A tubular type Heat exchanger is used.
DHAYANANDHAN.S
07/26/2013 5:45 PM
we have that system of blowdoen water.but heating with lp steam is not exist
07/31/2013 9:27 PM
Dear Mr. srik231,
You can use a tubular heat exchanger, for heating the DM water, by the bled steam. Care to be taken - for the Temp. of the out-let steam, from the heat exchanger for further use. If the temp. of the steam falls below the required level - then process side problem may arise.
DHAYANANDHAN.S