Inovatec 30kVA UPS

11/19/2013 11:38 AM

Hi,

We have connected a UPS (Brand Inovatec, 30kVA) to supply the server room. However, during testing the UPS goes to bypass mode and display message manual bypass is ON or cable is damaged. We inspected the UPS there is no cable damage and the bypass switch OF. What might be the cause of the problem.

Regards

D.D.Mtonyole

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inovatec 30kVA UPS

11/19/2013 12:02 PM

The solutions include getting the original equipment manufacturer to call under product warranty arrangements. Pick up the phone, and stop wasting time on CR4.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Inovatec 30kVA UPS

11/19/2013 2:48 PM

Do as PWSlack said. Ask someone who may have dealt with the problem of inept customers before:

Customer Support Area

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Inovatec 30kVA UPS

11/19/2013 3:08 PM

The bypass switch may have failed....the cable may have a loose connection.....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Inovatec 30kVA UPS

11/19/2013 11:29 PM

Apart from Chinese Alibaba references I got zip tech info when I Googled Inovatec 30kVA UPS

Seems it may be a badged up Chinese OEM generic.

Have you checked the batteries and their connections yet?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #4

Re: Inovatec 30kVA UPS

11/20/2013 8:24 AM

I already did the work for you:#2

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: Inovatec 30kVA UPS

11/20/2013 7:24 AM

It may be installed incorrectly, may even be dangerous to life and limb.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Inovatec 30kVA UPS

11/20/2013 8:43 AM

If the machine is correctly programmed and is not manually selected to "bypass" mode and if the power side wiring is correct:

Check the input circuit breaker position feedback contacts and the power source selection switch position feedback contacts.

If the feedback wiring is connected to the wrong contacts (N.O. vs N.C) the machine will "think" it is in "bypass" mode when actually in the "online" mode.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply