Induce Voltage in Multi Core Cables

11/20/2013 12:15 PM

I have an 8 core copper conductor 12 meter piece. for a test purpose i carried out megger at 1000 volts the result was infinity. The Interesting part is that when i introduce 220vac to any one core i have around 180 to 160 volts in rest of the cores.

Kindly provide support in eliminating the subject issue because this phenomena is causing all indications on my MCC and Local control to glow. and what will be long term effects on the system.

Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: induce voltage in multi core cables

11/20/2013 12:34 PM

What you are experiencing with the AC power is called capacitive coupling.

Basically each individual conductor is acting like a plate in a capacitor allowing some voltage at a microscopic current level to being transferred from the live line to the open floating lines which would be enough power transfer to get mini neon bulb type indicator lights to flicker a bit.

A simple fix would be to put a grounding resistor on each line to drain off the capacitively coupled voltage you are seeing. Anything around 250K - 500K ohms in parallel with your indicator bulbs should work just fine to keep them off.

Register to Reply Good Answer (Score 3)
Member

Join Date: Feb 2013
Posts: 8
#3
In reply to #1

Re: induce voltage in multi core cables

11/20/2013 12:57 PM

Thanks i will carry out the tests and inform you accordingly.

Further can you tell me what are the long term effects on the electrical network?

once again thanks for your support.

Regards

AA

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: induce voltage in multi core cables

11/20/2013 12:59 PM

The effects will be nil/zilch/nada/nothing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Feb 2013
Posts: 8
#5
In reply to #4

Re: induce voltage in multi core cables

11/20/2013 1:00 PM

Thanks.

Register to Reply
Member

Join Date: Feb 2013
Posts: 8
#6
In reply to #1

Re: induce voltage in multi core cables

11/20/2013 1:25 PM

what if i change the neon bulb with filament bulb should i still use a 250k ohms resistance?

Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#13
In reply to #6

Re: induce voltage in multi core cables

11/21/2013 9:02 AM

Changing to a filament could be beyond the current drain ability of the driving circuits. the Neon lamps have no direct connection across their leads, and so present no loading to the circuit until they fire. Changing the lamps to filaments would require pre-analysis to be sure the system would not be corrupted by the new loading.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: induce voltage in multi core cables

11/20/2013 12:36 PM

...and it's also called High Impedance Digital Voltmeter Syndrome.

Change to a cheap-and-nasty moving coil analog meter and see if the voltages are still there. There's GBP£1 resting on the outcome.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: Induce Voltage in Multi Core Cables

11/20/2013 1:51 PM

Depending on your circuit layout and loading this could be due to capacitive coupling or magnetic (transformer) coupling. In both cases a lower impedance on the non-energized cables will reduce the effect. Without knowing the details of the details of the system I cannot recommend a method to eliminate this coupling.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#8
In reply to #7

Re: Induce Voltage in Multi Core Cables

11/20/2013 6:32 PM

Or it could be a big, metal hoop-a-joop left there by the aliens, children.

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Register to Reply Off Topic (Score 6)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#9

Re: Induce Voltage in Multi Core Cables

11/20/2013 8:21 PM

Follow Slack's good advise. Or cut the cable in 1 inch pieces?

__________________
Plenty of room here
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#10

Re: Induce Voltage in Multi Core Cables

11/20/2013 10:46 PM

Yup... I agree with the other postings.

If this happens when you energize one conductor only, it is no doubt capacitive coupling.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11

Re: Induce Voltage in Multi Core Cables

11/20/2013 10:48 PM

If you are introducing 220VAC(L) to one core where is the reference for the other end of your meter? Ground perhaps or a common neutral in another cable?

These measurements of induced voltage in the other cores are these also relative to the same reference?

....and you are using neon lamps?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#12

Re: Induce Voltage in Multi Core Cables

11/20/2013 11:03 PM

Terminate all free / unused cable cores with 100k Ohms 2W resistor to earth / ground.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#14

Re: Induce Voltage in Multi Core Cables

11/21/2013 9:03 AM

This is a common issue with low voltage control cables that have been pulled/installed in the same cable tray and/or conduit with medium voltage or high-current LV load wiring.

If adding the capacitors and resistors do not clear up the "glowing" issue you will have to replace the control cables with shielded cables and earth/ground one end of the drain conductor.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Induce Voltage in Multi Core Cables

11/21/2013 2:11 PM

Disconnect all unused cores, especially if they are connected to high impedance inputs in control units in the MCC. The forum cannot see what these are.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aijaz Ahmed (3); dvmdsc (1); LongintheTooth (1); North of 60 (1); PWSlack (3); redfred (1); SHOCKHISCAN (1); Shyam (1); tcmtech (1); vermin (1); Wal (1)

Previous in Forum: Inovatec 30kVA UPS   Next in Forum: Capacitor Panel Design

Advertisement