Discolered Breaker Terminals

12/06/2013 6:11 PM

Hi everyone, I am really wondering what to do with this 100A circuit breaker. It is loaded with two 25 A motors. During start-up of each motor, this breaker sparks like a spot welding and heats up abnormally. I checked the bolts but they are well tightened. The terminals to the load side have particles already like salts on its surface and the wire is discolored to black. Do I need to change this circuit breaker? How dangerous it is to the building? Please help. Thank you. Roelexile

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Discolered Breaker Terminals

12/06/2013 6:25 PM

I hope this is a joke.

CALL SOMEONE WHO KNOWS SOMETHING ABOUT ELECTRICITY!!!!!!!!!!

DO NOT OPERATE THE MOTORS!!!!!!!!!!!!!!!

YOU COULD KILL PEOPLE, EVEN YOURSELF!!!!!!!!!!!!!!!! If the other people are lucky.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#2

Re: Discolered Breaker Terminals

12/06/2013 6:27 PM

Really?

Um...change the breaker. Get an electrician to change the breaker.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Discolered Breaker Terminals

12/06/2013 6:31 PM

It's a shame we can't send dope slaps through the internet.

Or, better yet, electric shocks!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#7
In reply to #3

Re: Discolered Breaker Terminals

12/07/2013 8:23 AM

Or buy policy's on them. $$$$

Register to Reply
Anonymous Poster #1
#8
In reply to #7

Re: Discolered Breaker Terminals

12/07/2013 11:29 PM

policy's policies

--Ed. C.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: Discolered Breaker Terminals

12/06/2013 7:21 PM

tell me you're joking??? you must be pulling my leg!!

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5

Re: Discolered Breaker Terminals

12/06/2013 8:58 PM

Pretty SCARY!! Let's hope they have a enough sense to stop and call someone qualified to make the required repairs.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
6
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#6

Re: Discolered Breaker Terminals

12/06/2013 11:58 PM

Roelexile-

It sounds like one or more of the conductors are aluminum

Solution A:

Ask your electrician:

  1. Why do aluminum junctions have to be prepared in a special way.
  2. What is the proper way to preparing them.
  3. What happens when you have Aluminum junctions that are not prepared correctly?
  4. Tell him you are not going to use those motors or the circuit breaker until HE fixes the problem.
  5. Ask him when he can start the job and how much it will cost.
  6. Forget the cost and get the electrician started on it.
  7. Remind yourself that if you don't have him do it, you could very easily kill yourself. It certainly sounds like you would. Also your investment will be given to your family and they won't have much since the buildings will probably burn down also.

Solution B:

  1. Forget solution "A" and contract with the electrician to fix it before you do anything else.
  2. When he is done with this one have him check all the rest of them. They're probably more with this deadly problem.

Solution C:

  1. Have a headstone carved with "R.I.P. Here lies a man who had a shocking demise." "The circuit breaker won, he lost"
  2. Get your good suit cleaned and pressed.
  3. Arrange for some flowers, a hearse, family car, and all the other necessary things
  4. Go ahead and try to fix it.
  5. Have others arrange for the ambulance. You might get lucky and have an "out of body experience" on the way out.
  6. Enjoy!

Take my example; I don't do my dental work. I have a dentist that does that for me. If I attempted to do it, I would probably bleed to death. Electricity works that way too.

Also, if you even think about fixing this I cannot be held liable for your mistakes. You asked the question, I gave you a good answer just like everyone else did. We all agree that this is beyond your capabilities. Deathly beyond your capabilities!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 6)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#9

Re: Discolered Breaker Terminals

12/08/2013 12:50 AM

Hi Roelexile, Yes, there is a problem. It may not be just the breaker. It wold also be helpful to know the voltage, single or 3 Phase. It may be the wiring or type of to the motors that could also be an issue. The "salts" as you describe are not a good sign. What is the environment this is located in? I have only seen this type of thing in a salt water fish farm that was so humid everything was covered in moisture. As for the breaker spitting sparks, this again is an issue. Is it being used as a switch? No motor(s) should be directly connected to a circuit breaker that is used as the switch to energize any motor. This is where a switch and contactor with an overload relay with the correct setting or heater elements comes into play. If this is a bit over your ability to handle, it is best to contact a qualified electrician to take a look at the situation and find out what the deal is.

Let us know what the final answer was.

__________________
"Real Bass Players" do not use picks
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2006
Location: Ibadan, South Western Nigeria
Posts: 13
#10

Re: Discolered Breaker Terminals

12/08/2013 1:57 AM

Need I say anything again? The wise have spoken!

__________________
"Be cautious of a naked man who is offering to give you a shirt" olusojihercules53
Register to Reply
Power-User
Australia - Member - New Member

Join Date: Aug 2010
Location: Brisbane, Australia
Posts: 136
Good Answers: 2
#11

Re: Discolered Breaker Terminals

12/08/2013 2:37 AM

Reading thru my colleagues views..I agree. I also add one - when you contact an electrician, and they check your equipment etc, I'd suggest a 'soft start' for the motors..

Register to Reply
Participant

Join Date: Dec 2013
Posts: 3
#12

Re: Discolered Breaker Terminals

12/08/2013 3:53 AM

Can we know the type of voltage source?. 3 phase or single phase, what type of motor, connect one motor at a time and test for short circuit in the motor coil, also test for earth leakage, check motor cables one after the other, check circuit breaker, if possible replace with a more sensitive type. Feed me back after doing all this.

Register to Reply
Participant

Join Date: Dec 2013
Posts: 3
#19
In reply to #12

Re: Discolered Breaker Terminals

12/08/2013 8:06 AM

This are the motor ratings: 230volts 25 amperes three phase induction type motor. There are contactors and OL rlys. The circuit breaker is intalled in a pannel board of the electrical room.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#20
In reply to #19

Re: Discolered Breaker Terminals

12/08/2013 8:10 AM

that still doesn't alter the collective view, this really doesn't sound like your specialty. let me repeat what others have expressed.......call in a professional with strong electrical experience.

Register to Reply
Participant

Join Date: Dec 2013
Posts: 3
#21
In reply to #20

Re: Discolered Breaker Terminals

12/08/2013 8:23 AM

Thank you Mr. Fredski, Your advise is good. I know how to replace the breaker. I know how to do wiring but I just want an additional info to examine my decision to replace the breaker.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#22
In reply to #21

Re: Discolered Breaker Terminals

12/08/2013 8:35 AM

Go back and re-read your original post, carefully.

If you really think anyone here, besides you, thinks you are qualified to analyze and repair an electrical circuit, you are even more delusional than I first thought you were.

<unsubscribes>

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#26
In reply to #21

Re: Discolered Breaker Terminals

12/08/2013 5:11 PM

Heres some additional information for you. Changing the breaker does not solve the problem! It will cover it for a moment, maybe! There is at least one existing problem of not multitudes of problems that have led up to the point of causing the breaker to start sparking and is the reason why people here are highly recommending call a professional electrician. Changing just the breaker could release the Magic Gennie out of the bottle!

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#32
In reply to #19

Re: Discolered Breaker Terminals

12/10/2013 9:41 AM

Please do not operate the motors before getting breaker repaired otherwise it may cause an electrical fire which may damage the complete substation. Call a qualified electrician and cable jointer to sort out the defect . It appears that your cable termination may need a rejointing and also may need complete check up of the breaker.Avoid doing experiments with such faults it may result in dangerous fire and accident.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13

Re: Discolered Breaker Terminals

12/08/2013 4:11 AM

What you do need to do is call an electrical person, or get the same one back that put two motors on one CB. Second thoughts.. don't call him back!!

Anyone who knows what they are doing would not have done this, please tell me it wasn't you!

A quick guide for you to follow, and this is by no means the solution to your problems, one motor = one CB. Call a certified electrical company, not a mate who thinks he knows something about electricity.

The damage has been done to the CB's so they do need to be changed ASAP... if not then your next call will be to the local Fire Department.

Finally... all the replies are good advice..... read well and understand them!

ps: to which address/church do we send flowers?

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Participant

Join Date: Dec 2013
Posts: 3
#14
In reply to #13

Re: Discolered Breaker Terminals

12/08/2013 5:01 AM

You might need two starter panels also that consist of contactors 20 - 30Amps overload relays, phase failure relays, voltage monitor relays and circuit breakers to start the motors. Do not connect directly to the circuit breaker.

Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16
In reply to #14

Re: Discolered Breaker Terminals

12/08/2013 6:58 AM

Not sure why you replied to my post, however, if you note the theme of the replies, no-one has offered any suggestions as to HOW to sort his problem out as, if I am not mistaken, the general consensus of opinion regarding what the Op has described is FUBAR... and requires a complete electrical makeover by a trained professional. Nothing less will suffice!

I'm sure you have heard the saying, "A little knowledge is dangerous"

This saying fits perfectly with the OP.... he has without a shadow of a doubt got more than enough rope to hang himself with and the whole of the building in which he resides/works. Giving him ideas or solutions such as yours, while you might think I've missed it out.... (trust me I haven't) will only send this guy off on a tangent to the real corrective course of action... GET A PROFESSIONAL IN!!

While I'm sure you meant well, and were not trying to call me out.. as a newbie to the site you have to be careful what you write!

ps: Question.. how do you know he hasn't got two separate DOL starters?

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#15

Re: Discolered Breaker Terminals

12/08/2013 6:53 AM

co0054, first, welcome to CR4

you are 100% right, motor starter with disconnects in the best solution.

thank you!

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#17
In reply to #15

Re: Discolered Breaker Terminals

12/08/2013 6:59 AM

and the same question to you.. how do you know he hasn't got two DOL starters?

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Dec 2013
Posts: 3
#18
In reply to #15

Re: Discolered Breaker Terminals

12/08/2013 7:53 AM

Thanks pal.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#24
In reply to #18

Re: Discolered Breaker Terminals

12/08/2013 12:10 PM

You are welcome.... and welcome to the mad house!! Oh sorry CR4!

WE can get a little cranky sometimes, as you will find out, intolerant a lot, and some can get quite rude....

However it's a fun place....

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#23

Re: Discolered Breaker Terminals

12/08/2013 11:56 AM

Hi Roelexile,

Welcome to CR4. You have received good advice. I will add that the blackened wire will probably need replacing too. What guage is it? You need to realize that 25A motors draw more current when they are starting. A breaker should never spark. Does it trip? Is it the main breaker in the panel? If the sparks get out of the panel, your building could burn down. Same thing if the wires are too small or if you have aluminum wires with breakers made for copper. Shut everything off until a qualified electrician looks it over.

-S

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#25

Re: Discolered Breaker Terminals

12/08/2013 4:42 PM

Roelexile-

Are you a betting man? If not you should study some odds, especially these-

In reference to your posting dated 12-6-13, you originally made one question.

Within the past 46 hours you have received the following answers:

Total = 24;

18 ea - No, don't even attempt to repair this, it takes a professional to do this, to the other extreme of your going to kill yourself!

4 ea - Yes, go ahead and do it. (Who even knows their electrical knowledge or skills?)

2 ea - Posts from yourself, either thanking someone or stating you have some electrical skills. These skills you state to have are far from those required for this problem.

Analyzing these statistics you can come to the conclusion that the odds of you failing are 18 out of 22. These mean that according to the 22 people who answered your question, besides yourself, 18 think the range of results is going to be you can't fix it to your going to die trying to do it and 4 think you might be able to do it.

Eighteen people have given you their answers, all good. The first ten answers were "Don't do it!" You asked a question, we all gave you the same answer------ "You can't diagnose the problem, you can't fix the problem and you likely will kill yourself trying. You are about to commit suicide if you even try". We are here to help you, not antagonize or berate you. Please listen to us.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#27

Re: Discolered Breaker Terminals

12/09/2013 6:41 AM

Already, lots of good advice here that you should be reading and understanding better.....

A 25 amp AC motor generally takes, provided no form of reduced current starter is used, between 5 and 8 times the running current at start up. This usually the "blocked rotor" current which may, or may not be not be noted on the motor spec..

Some starters start a motor up on reduced voltage to reduce the starting current, but the motor takes longer to run up, also depending upon mechanical load of the motor....

I generally use 6 x as a starting current value (could be right, less or even more!), so expect your motors, each one of them, to take around 150 amps at start up. Your electrician would probably, if he knows his job, plan for something like this, which suggests that no proper electrician was either consulted or used......

If you start both motors together, the instant current would/could be around double that.....no small wonder that the breaker sparks with either one or both motors!!!!!

There are breakers designed to accept the starting current for a short time, but to drop off if say double running current is seen for any reason. These values can be adjusted one way or another at purchase/install time.....I am sadly, out of touch with up to date modern versions....but there are plenty of good Guys here that are fully up to date as we have already seen.

Also, do not forget that "Good looks fade, but dumb is forever!" Unless of course, you blow yourself up somewhere before "forever".....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#28

Re: Discolered Breaker Terminals

12/09/2013 8:50 AM

Like almost all other replies, yes you need to change the breaker, after all, they do not last forever and will "wear out" over time, depending on how many cycles they are put through. Might want to get an electrician to check out the rest of the circuits elements as well, see if there are possible weaknesses in the insulation of the wiring which may cause excessive draw.

__________________
Never stop learning
Register to Reply Score 1 for Off Topic
Member

Join Date: Oct 2012
Posts: 8
#29

Re: Discolered Breaker Terminals

12/09/2013 9:02 AM

check the instantanous setting on the breaker

Register to Reply Off Topic (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#30

Re: Discolered Breaker Terminals

12/09/2013 1:01 PM

The root cause of the problem is that there is no-one at the facility who knows anything about electricity.

The solution is to hire someone locally who is qualified to help.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#31
In reply to #30

Re: Discolered Breaker Terminals

12/09/2013 1:10 PM

what makes you say that?

Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); Andy Germany (1); Anonymous Poster (1); brich (4); co00054 (3); dj95401 (2); fidhahusain (1); fixitorelse (1); Fredski (3); Hrecules53 (1); Jimh77 (1); Kevin LaPaire (1); kramarat (1); lyn (3); old salt (2); Phil D. (1); PWSlack (1); Roelexile (2); StandardsGuy (1); V.I.Abraham (1)

Previous in Forum: Rotor Current (Induction Motor)   Next in Forum: Data Center VTs Failure

Advertisement