Selection of Relative Humidity at Constant Pressure & Temp

01/10/2014 12:02 AM

Recently I have encountered with a problem on selection of Relative humidity at constant Temp & Pressure for design of Shell & tube heat exchanger.

The parameter are given as under Design DBT= 41 C and humidity levels are mentioned as 93% & 27%.the exchanger has fluid of air on shell side ( 135/50 c)and cooling water on tubes side (32/40 c).

I have selected higher humidity which has given more heat duty but when I Checke the calculation with lower RH the duty has reduced but area has increased and net Overdesign margin will go on negative sides.

My question is there what is the safe rule for selection of RH at constant Pressure & Temp ,because higher RH selection gives Higher duty and low area, while lower RH selection provide Low Duty and higher area.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Selection of Relative humidity at constant pressure & Temp

01/10/2014 2:53 AM

The heat conductivity factor (K or U) would be higher when more water vapor condensation is involved, resulting in less surface area for a given duty.

To be safe, check both conditions, and use the larger of the resulting areas.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#5
In reply to #1

Re: Selection of Relative humidity at constant pressure & Temp

01/11/2014 3:24 AM

Tornado:

Is the calculation CODE takes into account the rate of condensation or you go by some rule of thumb with experimental data? Interesting one.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Selection of Relative humidity at constant pressure & Temp

01/11/2014 3:40 AM

I don't have the type of software now used by heat exchanger mfrs, but I suspect the OP does. My comments are really "old school". In the U.S., Crane Valves used to have a catalog with quite a bit of "rule of thumb" information such as steam tables, K factors for various shell-and-tube situations, Williams-Hazen pipe flow calcs, etc.; it was affectionately known as the "orange Bible."

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#7
In reply to #6

Re: Selection of Relative humidity at constant pressure & Temp

01/11/2014 5:19 AM

Thanks.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Power-User

Join Date: Oct 2009
Posts: 176
Good Answers: 4
#10
In reply to #6

Re: Selection of Relative humidity at constant pressure & Temp

01/13/2014 7:29 PM
Register to Reply
Member

Join Date: Dec 2013
Posts: 6
#8
In reply to #1

Re: Selection of Relative humidity at constant pressure & Temp

01/12/2014 11:52 PM

you have mentioned to check both the condition and use Larger of the resulting area it means we should ignore heat duty and focus on larger area only because in higher RH we get higher Heat duty and low Area while on Lower RH we get lower Heat duty & Higher surface area .

Register to Reply
Power-User

Join Date: Aug 2013
Location: OHIO, tri-State design and installation, and travel nationally and consults also are international
Posts: 274
#2

Shell around COIL Re: Selection of Relative Humidity at Constant Pressure & Temp

01/10/2014 7:01 PM

www.AquaSystemsInc.com

Ernie has an idea

__________________
Simply choose your utility supplier contracting WITHOUT BROKERS and opt-out of community aggregations for free choices.
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #2

Re: Shell around COIL Re: Selection of Relative Humidity at Constant Pressure & Temp

01/11/2014 1:45 AM

Irrelevant. The OP is talking about air to water exchangers, not liquid to liquid.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3

Re: Selection of Relative Humidity at Constant Pressure & Temp

01/11/2014 1:33 AM

Dear Mr.smathur 72.

A RH of 60% is CONSIDERED as Standard for Design Purpose.

DHAYANANDHAN.S

Register to Reply
Member

Join Date: Dec 2013
Posts: 6
#9
In reply to #3

Re: Selection of Relative Humidity at Constant Pressure & Temp

01/12/2014 11:55 PM

Thanks ,but please let me know is there any basis or guide line to use 60% RH as standard for Design.?

Register to Reply
Register to Reply 10 comments