Since the Last Week in December, we were getting a high
level alarm on our Balance Tank that supplies our Cooling Water Supply pumps. See
sketch, We never had this, before, but we did upgrade our system. With higher
flow rates, we are also adding a new process that is not online yet. Basic Sketch at the bottom
On our old system, we may have been doing 1500 to 1700 GPM, I
do not have temperature of the cooling water, but the upgrade we are doing 3100
GPM with the feed temperature at 60°F with the return temperature at 67°F to
the cooling cells, (Cooling cells current capacity is of 4850 GPM, I can give
more detail on it if it helps, but I had spec.'ed it using our worse conditions
which is in the summer). I have the make-up water usage, but basically we been had to shut it off manually, and the only time we turn it on is when the level gets within an expectable range.
Now we have a number of pumps on the systems, and the seal
water for these supply pumps are coming from the city water supply, and returned
as make-up water to the cooling towers. We also have main make-up water on the
main pump supply balance tank that is controlled by the high/low level controls
(Which are about 8" apart, tank diameter is approx. 150").
When low level is reached pump make-up water is added and is
not shut off when high level alarm is reached. (There is a third sensor below
the low level alarm if for some reason water level gets too low)
This high level alarm started around Christmas Break, the
outside temperatures did drop well below 0°F to especially last week, weather
temps from last week shown below (hope you can read it, but it was below -20°F).

With all the pumps in the process system, we are adding approx..
85 GPH of the seal water to the systems as make-up water.
There are other possibilities of why we are getting high
alarms,
- An unknown supply in the system, (I checked for this)
- A failure on any of the heat exchangers that will be putting product in the cooling water. (No, I checked for contamination, (color, brix etc….)
- Failure on the make-up water valve. (unlikely, we basically manually shut it off, till it gets to an acceptable level, and when we bring it on line, he shuts off at high level, wether it sticks on/open..... possible, but unlikely)
What, I am thinking is that this water supply for the pump
seals that we then use as a partial make-up water is more than what is evaporating and is what is giving me the high
alarms. We never had this before because of the lower flow rates and the higher
temperature return, and a possible higher ΔT through the cooling cells.
The question I have is this possible, or if anyone else
experience this.